In my opinion, board-mounted AC inlets are inadvisable at best. The problems
extend to more than the risk of an open circuit during a ground fault. The AC
in
it used to be
From: Ted Eckert <07cf6ebeab9d-dmarc-requ...@ieee.org>
Sent: Tuesday, September 24, 2019 6:55 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding of metal cabinet
The rationale I remember learning is that the main grounding/earthing
connection must be made
September 2019 14:55
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding of metal cabinet
The rationale I remember learning is that the main grounding/earthing
connection must be made in a way such that any repairs would not need to
disconnect that main grounding connection. Let me
Microsoft Corporation
The opinions experessed are my own and do not necessarily reflect those of my
employer.
From: Pete Perkins
Sent: Tuesday, September 24, 2019 10:30 AM
To: Ted Eckert ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] Grounding of metal cabinet
Ted et al. Since we’re
;
Sent: Monday, September 23, 2019 9:45 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding of metal cabinet
Our safety regulators have insisted that power cord safety ground/earth go
first to the metal chassis, with rare exceptions. Exception, the majority of
chassis is plastic
ay, September 23, 2019 4:19 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding of metal cabinet
The question is how the cabinet is earthed if the PE wire goes to a terminal
block. If a wire comes out of the terminal block to a stud on the cabinet,
that is less reliable
tember 23, 2019 4:19 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding of metal cabinet
The question is how the cabinet is earthed if the PE wire goes to a terminal
block. If a wire comes out of the terminal block to a stud on the cabinet,
that is less reliable than a solid con
The question is how the cabinet is earthed if the PE wire goes to a
terminal block. If a wire comes out of the terminal block to a stud on
the cabinet, that is less reliable than a solid connection. I suggest
you take the advice. It doesn't apply if the 'terminal block' is not an
insulating
A flexible 1-phase AC cable is entering a metal cabinet and the PE-wire is
directly connected to an Earth terminal block (green/yellow).
Some years ago, a safety engineer told me that the earth wire should first
be connected to a ground stud inside the cabinet via a lug terminal climp
and fastened
IEEE Life Fellow
>
> p.perk...@ieee.org mailto:p.perk...@ieee.org
>
>
>
> Entropy ain’t what it used to be
>
>
>
> From: Nyffenegger, Dave
> Sent: Tuesday, June 18, 2019 12:21 PM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Sub
9 12:21 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding
Steve, I don’t recall EN 60204-1 requiring a central earthing point,
disallowing daisy chaining of the protective bonding circuit. My copy is with
2009 amendments. Is there a newer version with this requirement? NFP
...@comcast.net]
Sent: Tuesday, June 18, 2019 2:39 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Grounding
HI all,
I have a client with whom I am having a discussion about grounding for an EN
60204-1 product. The product consists of 3 sub-modules all of which use mains
power derived from
18, 2019 11:39 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Grounding
HI all,
I have a client with whom I am having a discussion about grounding for an EN
60204-1 product. The product consists of 3 sub-modules all of which use mains
power derived from the first module where the
:00 PM (GMT-05:00) To: Steve Brody Cc: IEEE
EMC PSTC Subject: Re: [PSES] Grounding Steve,I
agree, you need a positive bonding connection back tot he PE point.The WAGO
terminal are excellent. They have some spectacular test videos on their web
site showing the effects of overcurrent on their
Steve,
I agree, you need a positive bonding connection back tot he PE point.
The WAGO terminal are excellent. They have some spectacular test videos on
their web site showing the effects of overcurrent on their terminal blocks, and
I have personally found them to be highly reliable in some dema
Sulis Consultants Ltd
Tel: +44 (0)7946 624317
Web: https://sulisconsultants.com/
Registered in England and Wales, number 05466247
From: Grasso, Charles
Sent: 18 June 2019 19:49
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Grounding
My 2c – You are correct (MOO).
Thanks!
Charles Grasso
W: 303
First, you have done the right thing by showing the requirement in the
standard that supports your assertion. It's really difficult to argue
against that. Second, I suggest you ask the manufacturers of the
terminal block how they claim it meets the requirements of 60204-1. You
may find that it
My 2c – You are correct (MOO).
Thanks!
Charles Grasso
W: 303-706-5467
From: Steve Brody [mailto:sgbr...@comcast.net]
Sent: Tuesday, June 18, 2019 12:39 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Grounding
This message originated outside of DISH and was sent by:
owner-emc-p
HI all,
I have a client with whom I am having a discussion about grounding for an EN
60204-1 product. The product consists of 3 sub-modules all of which use mains
power derived from the first module where the external mains comes into the
unit.
In the first module the ground from the branch
solution. Look
outside the box. Colorado Brian
-- Original Message --
From: "Brian O'Connell"
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] grounding of output of solar inverter
Date: Tue, 16 Feb 2016 17:27:37 +
Reference articles 250 and 690 of
O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Tuesday, February 16, 2016 6:59 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] grounding of output of solar inverter
Also, should have noted to reference the NDs in UL62109-1, which further
addresses below requirements, as stuff in North Am
-PDFs/SAV4704.pdf
Brian
-Original Message-
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Tuesday, February 16, 2016 9:28 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] grounding of output of solar inverter
Reference articles 250 and 690 of the NEC (NFPA70). Canad
Reference articles 250 and 690 of the NEC (NFPA70). Canada and Mexico code
similar.
Brian
From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
Sent: Monday, February 15, 2016 9:05 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] grounding of output of solar inverter
Dear experts,
Is anyone
Dear experts,
Is anyone familiar with UL 1741? I am dealing with solar inverter for US
market. Solar inverter can operate in utility interactive mode (feeding the
grid) or in a standalone mode where only homeloads are supplied by inverter
(anti-islanding relays are open, due to problems with t