Hi Chris, As usual, Rich is correct that removing more then one ground connection would be an improper single fault test. However, Rich's comment... A single-fault test is with one ground open (a meaningless test when there is a second ground in place)... Is not quite accurate, the test is

Re: Secondary Grounding

2001-06-01 Thread Rich Nute
Hi Chris: Consider a product with two, independent protective grounding/earthing connections. This may be by means of two power cords (as is done for uptime reliablity by employing parallel power supplies) or by means of one power cord and a separate ground connection (as, for example, by

X ray safety interlocks.

2001-06-01 Thread Chaplis, Bob
All, Paragraph C4 in cfr 1020.40 States: Each door of a cabinet X-Ray system shall have a minimum of two safety interlocks. One, but not both of the required interlocks shall be such that the door opening results in physical disconnection of the energy supply circuit to the high

RE: Secondary Grounding

2001-06-01 Thread Chris Maxwell
Hmm, This question centers around whether two separate ground cables equals double protection. Safety standards call for single fault testing. For Class I equipment, one of the single fault test conditions is removal of the ground connection. I'm curious how most test labs would

Re: UL Mark

2001-06-01 Thread Rich Nute
Hi Dave: Can anybody tell me where it is defined at what point in production it is permissible to apply the UL mark? Can it only be done after the hi-pot has passed? Or is it OK to have the label applied before the test as long as the units are clearly marked as having failed

[Fwd: RE: ESD Question]

2001-06-01 Thread David Heald
Forwarded for Mike Hopkins. Original Message Subject: RE: ESD Question List-Post: emc-pstc@listserv.ieee.org Date: Wed, 30 May 2001 16:06:48 -0400 From: Mike Hopkins mhopk...@thermokeytek.com To: 'Chris Maxwell' chris.maxw...@nettest.com,'Sandy Mazzola'mazzo...@symbol.com,

Re: Surge Test Question

2001-06-01 Thread Patrick Lawler
I've also seen this effect when testing component power supplies (off-line switch-mode converters, 50-500W). The problem became apparent when a customer added another EMI filter ahead of our power supply, creating a system we didn't anticipate. The power supply alone passed the test, but the

RE: EMC/RFI Gaskets

2001-06-01 Thread Dick Grobner
I would have to state that the polymeric material would be listed under the manufacture of that material (not necessarily the EMI gasket manufacturer) and the shield effectiveness data would be from the manufacturer of the EMI gasket. You should be able to contact the EMI gasket manufacture for

RE: EMC/RFI Gaskets

2001-06-01 Thread Robert Tims (EMX)
Hi Peter, Gaket material are covered as Recognized Plastics material. They are in the yellow books, just like regular plastics material (QMFZ2). Some gasket material were Recognized under that QMFZ2 category, but there is also a special category (Q) that covers gaskets in particular. I

EMC/RFI Gaskets

2001-06-01 Thread Peter Merguerian
Dear All, While UL does its' own research, under what UL category one can find polymeric insulated RFI/EMI gaskets that have been previously evaluated for flammability and shielding effectiveness? PETER S. MERGUERIAN Technical Director I.T.L. (Product Testing) Ltd. 26 Hacharoshet St., POB

[Fwd: JISC to U.S. Code equivalency]

2001-06-01 Thread Dave Heald
Forwarded for Leslie Wood. Please CC Leslie (lesliew...@aol.com) on replies. Dave Heald Original Message Subject: JISC to U.S. Code equivalency List-Post: emc-pstc@listserv.ieee.org Date: Thu, 31 May 2001 20:49:00 EDT From: lesliew...@aol.com To: emc-p...@majordomo.ieee.org