Brian,
I appreciate for your purposes the SPC component of 
choice is the MOV. Quite right too, if you are considering 
cost and device safety standards like UL 1449. SPC 
standards, which tend to be for component electrical and 
environmental performance, can only overlap the requirements 
of an Equipment/Device safety standard.


Your perception of other protection technologies needs 
revision.


True, PN junction zener breakdown diodes have a very soft 
clamping characteristic. NB The zener breakdown effect only 
occurs below about 7 V.
To counter the poor zener clamping characteristic a 
multi-junction silicon semiconductor component using the 
punch-through effect can be used. This type of technology 
provides a sharp clamping characteristic from a few volts 
upwards. Punch-through voltage limiters can be found in 
Ethernet ports. These SPCs protect the Ethernet PHY chip 
against damaging overvoltages (even though 5-volts may not 
sound like an overvoltage)


Above 7 V a different breakdown effect comes in -- the 
avalanche effect.
Avalanche breakdown diodes have a good sharp clamping 
characteristic. You may see them referred to as SADs, 
Silicon Avalanche Diodes. The three-letter acronym powers 
that be in the IEC said they didn't want a sad component and 
so the ABD, Avalanche Breakdown Diode, acronym came into 
being. Unfortunately, many people, who don't know the 
difference between zener and avalanche breakdown, call ABDs 
zeners, which is totally wrong.
All PN junction semiconductors have relatively low thermal 
capacity and energy absorption capability. These 
deficiencies can be countered by using series and parallel 
combinations of ABDs. There are several companies in the US 
making AC Power SPDs using this approach -- costly, but 
these have a better clamping performance than an MOV.


The GDT uses gaseous discharge and the switching time from 
sparkover to the low-voltage arc can be in the tens of 
nanoseconds. The problem is that the sparkover voltage is 
dependent on the rate of voltage rise. This overshoot of 
surge sparkover to AC sparkover can be something like 2:1. 
This is not a firm ratio but dependent on the AC/DC 
sparkover voltage. An 80 V GDT will have a higher surge 
sparkover voltage than the sweet spot 250 V GDT.
An interesting trend I've noticed is for GDT MOV series 
combinations where PLC is being used. Put MOV protection 
(read capacitance) on the AC supply and PLC reach and 
environmental pollution are reduced. Protect using a low 
capacitance GDT MOV series combination and PLC reach and 
environmental pollution are maximised.


Regards
Mick


On 14/11/2011 21:04, Brian Oconnell wrote:

o further abuse a meme - moar standards! [insert troll-face here]

Another member has previously commented that there a several type of
components used to arrest a surge. For the purpose of my OP, was focused on
a MOV-type SPD as defined under UL CCNs VZCA2 and VZCA8, where the effective
standards are UL1449 and CSA C233.1, and various CSA TILs. And of course,
the wondrous IEC61051-2. This is another case where EMC requirements
(61000-4-5,6) can affect product safety. Last year's update to the 2d ed of
60950-1 for my component power supplies was, for some models, quite an
adventure.

A problem NOT ADDRESSED by TC108 is the increased energy AFTER a surge, or
during a SFC, due to the 120% rating requirement. Perhaps this was a
principal intent of UL1449 3d ed - verify that the high E and I do not make
the MOV puke it guts and start a fire. There are many sources of increased
energy - my two problem children are the effects of an inductive kick to the
circuit being 'protected' by the SPD*after*  the current interrupt device
has opened; and the higher voltage (CV^2), during a surge, at which the SPD
will start conducting.

As for GDTs - they take longer to get to low Z. And zener-type arrestors do
not have a sharp knee at the conduction level. The ZnO MOV seems to be the
best chance of survival, assuming the other  circuit components can handle
much higher coulombs running around before clamping.


Moar standards! Moar unintended effects! Moarrr

Brian

-Original Message-
From:emc-p...@ieee.org  [mailto:emc-p...@ieee.org]On Behalf Of
ralph.mcdiar...@schneider-electric.com
Sent: Monday, November 14, 2011 11:31 AM
To:EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] MOV requirements

Does the industry really need another standard, I wonder?

Ralph McDiarmid  |   Schneider Electric   |  Renewable Energies Business  |
CANADA  |   Regulatory Compliance Engineering


From: John Woodgatej...@jmwa.demon.co.uk
To:EMC-PSTC@LISTSERV.IEEE.ORG
Date: 11/11/2011 06:48 AM
Subject: Re: [PSES] MOV requirements

In message4ebd2d05.5050...@ieee.org, dated Fri, 11 Nov 2011, Mick
Maytumm.j.may...@ieee.org  writes:


MOV, Varistor, VDR; Metal-Oxide Varistor are all names for a
voltage-limiting component using a particular technology.

I think this 'particular technology' is an 

[PSES] Northeast Product Safety Society Vendor’s Night Tomorrow, November 16th

2011-11-15 Thread Matthew Campanella


All,




 

The
Northeast Product Safety Society invites you to the 17th annual Vendor’s Night
to be held at the Marlborough Holiday Inn next week tomorrow, November 16th
from 5:00 to 9:30 PM.  Vendor's Night is
opportunity to get answers to all your product safety/EMC questions in one
evening.  There will be up to 50
companies exhibiting.  Exhibitors are
from certification agencies, qualified testing laboratories, independent
consultants and suppliers of services, test equipment and components.  If you 
will be in the area, feel free
to join us.  Walk-in registration is
welcomed.  There is no fee to attend.

 

The
Vendor’s Night registration opens at 4:30 PM and the Exhibition will be open
from 5:00 PM to 9:30 PM.  A free, 2
entrée, buffet style dinner will be served during the exhibition from 7:30 PM
to 9:00 PM.  A Vendor’s Night
announcement flyer is available at http://www.nepss.net/17thNPSSFlyer.doc and a 
Vendor’s
Night exhibitor registration form is available at 
http://www.nepss.net/17thNPSSRegForm.doc on the NPSS web
site but we ask you to complete your reservations before Nov 14th.  There are 
still a few tables available for any
vendor that would like to participate in the 17th Annual Vendor’s Night.  
Please feel free to contact Bill Graham at b...@grahamweb.com, Dave Wheeler at 
inter...@aol.com or myself for
more information about Vendor’s Night.

 

There
is no charge for admission to the exhibits with complimentary buffet dinner.  
So that we may plan the dinner, we ask you to
make a dinner notice reservation with Donna Kearney
at 978-870-5563 (email to dkearn...@hotmail.com) or Matthew Campanella at 
508-786-7629 (email to matthew.campane...@motorola.com).

 

In addition to the
world class products and varied local services on display this year there will
be a prize drawing for those attending. 
This Prize drawing is restricted to visitors to the show.  In addition various 
companies will have
handouts.   Please join us at the Holiday Inn on the 16th
and network with your many friends and colleagues in the Product Safety and EMC
communities in New England, enjoy an evening of good food and perhaps not only
come away with a little more product or service information but maybe a little
more cash in your pocket.

 

Further
information about the Northeast Product Safety Society is available at 
http://www.nepss.net.  An NPSS membership application form with brief
NPSS brochure is also available on the NPSS site at 
http://www.nepss.net/page18.html. 

 

The 17th Annual Vendor’s Night location is:

 

Marlborough Holiday Inn

265 Lakeside
  Avenue

Marlborough, MA 01752

(508) 481-3000

 

Web directions are available at 
http://www.ichotelsgroup.com/h/d/hi/1/en/hotel/boxma/transportation

 

Directions: 

From Route 495 North or South, take Exit 24, Route 20
East

Turn left into Holiday Inn entrance (approximately 100
feet from Route 495 North)

 

Matt
Campanella

    NPSS Secretary

 

(508) 786-7629 

matthew.campane...@motorola.com  email



 

 



-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

Re: [PSES] SPC component properties

2011-11-15 Thread Brian Oconnell
Mick,

Good points, most of which are within the realization of my employer's
designs. For example, for the automotive stuff, we tend to not use MOVs, but
as you suggested, an avalanche diode(where our big concern is not surge, but
ESD). But for component conversion devices, where the rated input will be up
1kV, we do the MOV and/or GDT dance.

There are no normative safety requirements for the SELV/PELV input
environment for our automotive toys, but for mains-connected stuff - you
gotta dance with the component that can party until you puke.

Have I used enough crass metaphors?

Brian



-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Mick Maytum
Sent: Tuesday, November 15, 2011 6:15 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: SPC component properties

Brian,
I appreciate for your purposes the SPC component of choice is the MOV.
Quite right too, if you are considering cost and device safety standards
like UL 1449. SPC standards, which tend to be for component electrical and
environmental performance, can only overlap the requirements of an
Equipment/Device safety standard.

Your perception of other protection technologies needs revision.

True, PN junction zener breakdown diodes have a very soft clamping
characteristic. NB The zener breakdown effect only occurs below about 7 V.
To counter the poor zener clamping characteristic a multi-junction silicon
semiconductor component using the punch-through effect can be used. This
type of technology provides a sharp clamping characteristic from a few volts
upwards. Punch-through voltage limiters can be found in Ethernet ports.
These SPCs protect the Ethernet PHY chip against damaging overvoltages (even
though 5-volts may not sound like an overvoltage)

Above 7 V a different breakdown effect comes in – the avalanche effect.
Avalanche breakdown diodes have a good sharp clamping characteristic. You
may see them referred to as SADs, Silicon Avalanche Diodes. The three-letter
acronym powers that be in the IEC said they didn’t want a sad component and
so the ABD, Avalanche Breakdown Diode, acronym came into being.
Unfortunately, many people, who don’t know the difference between zener and
avalanche breakdown, call ABDs zeners, which is totally wrong.
All PN junction semiconductors have relatively low thermal capacity and
energy absorption capability. These deficiencies can be countered by using
series and parallel combinations of ABDs. There are several companies in the
US making AC Power SPDs using this approach – costly, but these have a
better clamping performance than an MOV.

The GDT uses gaseous discharge and the switching time from sparkover to the
low-voltage arc can be in the tens of nanoseconds. The problem is that the
sparkover voltage is dependent on the rate of voltage rise. This overshoot
of surge sparkover to AC sparkover can be something like 2:1. This is not a
firm ratio but dependent on the AC/DC sparkover voltage. An 80 V GDT will
have a higher surge sparkover voltage than the “sweet spot” 250 V GDT.
An interesting trend I’ve noticed is for GDT MOV series combinations
where PLC is being used. Put MOV protection (read capacitance) on the AC
supply and PLC reach and environmental pollution are reduced. Protect using
a low capacitance GDT MOV series combination and PLC reach and environmental
pollution are maximised.

Regards
Mick


On 14/11/2011 21:04, Brian Oconnell wrote:
o further abuse a meme - moar standards! [insert troll-face here]

Another member has previously commented that there a several type of
components used to arrest a surge. For the purpose of my OP, was focused on
a MOV-type SPD as defined under UL CCNs VZCA2 and VZCA8, where the effective
standards are UL1449 and CSA C233.1, and various CSA TILs. And of course,
the wondrous IEC61051-2. This is another case where EMC requirements
(61000-4-5,6) can affect product safety. Last year's update to the 2d ed of
60950-1 for my component power supplies was, for some models, quite an
adventure.

A problem NOT ADDRESSED by TC108 is the increased energy AFTER a surge, or
during a SFC, due to the 120% rating requirement. Perhaps this was a
principal intent of UL1449 3d ed - verify that the high E and I do not make
the MOV puke it guts and start a fire. There are many sources of increased
energy - my two problem children are the effects of an inductive kick to the
circuit being 'protected' by the SPD *after* the current interrupt device
has opened; and the higher voltage (CV^2), during a surge, at which the SPD
will start conducting.

As for GDTs - they take longer to get to low Z. And zener-type arrestors do
not have a sharp knee at the conduction level. The ZnO MOV seems to be the
best chance of survival, assuming the other  circuit components can handle
much higher coulombs running around before clamping.


Moar standards! Moar unintended effects! Moarrr

Brian

-Original Message-
From: emc-p...@ieee.org 

Re: [PSES] AC Powering or not to AC power that is the test option

2011-11-15 Thread Mick Maytum

Brian,
I find portions of our discussion has been transcribed 
to the entire IEC TC 108 group. Thus I feel I should respond 
to your TC 108 comments



A problem NOT ADDRESSED by TC108 is the increased energy AFTER a surge, or
during a SFC, due to the 120% rating requirement. Perhaps this was a
principal intent of UL1449 3d ed - verify that the high E and I do not make
the MOV puke it guts and start a fire.
I don't think TC 108 is deficient in missing out AC 
powering when surging. I'm not in love with some other stuff 
they do, but that's another discussion.


My reasoning is, if the surge damages the MOV, then all 
the applied AC does is provide a power source to cause a 
component power loss and temperature rise that might lead to 
thermal runaway and component destruction.
Without the application of AC power, there are 
measurement techniques available to tell if the component 
has been damaged. At the component level, measuring the MOV 
nominal voltage at 1 mA DC is a common approach. If this 
voltage changes by more than a given amount then the MOV has 
degraded due to surge.


I've spent a deal of time studying UL 1449 recently 
and, as I understand it, in the most stressful surge test UL 
doesn't apply AC power (like TC 108).


Type 2 SPDs have a Nominal discharge current test (As 
the MOV isn't a GDT with a gaseous filling, you can't have a 
discharge current in it, so the correct term is the more 
mundane nominal surge current).
Preferred current values are 3 kA, 5 kA, 10 kA and 
20 kA. These are currents in the SPD, not short-circuit 
ones, produced by an 8/20 current generator. No AC power is 
applied.


 Type 3 SPDs have an operating duty cycle test with AC 
power applied. The surge generator is a 1.2/50-8/20 
combination wave generator set for 6 kV open-circuit and 3 
kA short-circuit. Once you included the coupling/decoupling 
network and the component, it is only a quasi-8/20 current 
of a smaller amplitude than the short-circuit value in the MOV .


UL measure pre and post test limiting voltage - this is 
a very crude validation assessment method. A lot has gone 
wrong to cause a significant change in limiting voltage. On 
the bright side, because UL throws a lot of extra tests in, 
there is a leakage current test, which performs a similar 
appraisal as the component 1 mA nominal voltage test.


Regards
Mick

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] CE marking of deep-fat fryer

2011-11-15 Thread McInturff, Gary
Ralph, no real argument to the benefit except especially the safety folks won't 
even go into court as an expert witness on your behalf. But the benefit of the 
third party is more in how deep they get into your wallet. is the reasonable 
manufacturer doctrine in Tort law. It's just what it sounds like. Did you meet 
the minimums of what a reasonable manufacturer would do? E.g. Did you seek a  
second opinion about the safety or the product? If it is common in the industry 
to do so and you don't bother then you don't' meet the doctrine and the 
monetary damages are going to escalate dramatically because you've shown a 
disregard for you customers safety. - This is all paraphrased and cut down from 
a seminar on Tort law as it applies to safety many years ago.

So the value is a ha'  penny versus a pound sterling.

From: ralph.mcdiar...@schneider-electric.com 
[mailto:ralph.mcdiar...@schneider-electric.com]
Sent: Tuesday, November 15, 2011 8:51 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] CE marking of deep-fat fryer


I don't think UL would be sued; the manufacturer is ultimately liable.  The is 
little or no benefit of 3rd party certification of a product under Tort law.
_

Ralph McDiarmid  |   Schneider Electric   |  Renewable Energies Business  |   
CANADA  |   Regulatory Compliance Engineering


From:

John Woodgate j...@jmwa.demon.co.uk

To:

EMC-PSTC@LISTSERV.IEEE.ORG

Date:

11/14/2011 10:50 PM

Subject:

Re: [PSES] CE marking of deep-fat fryer






In message 4ec19e99.7060...@aol.com, dated Mon, 14 Nov 2011, Derek
Walton lfresea...@aol.com writes:

I guess I find this nonsense.   ANYTHING abused looks dangerous.

More examples of Nanny state control.

Yes, but if they didn't do it, UL would be sued for $100 by
everyone who sets their fryer on fyer. That may happen anyway because
the person concerned can't read English.
--
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
Some people who are peeling the finch of the financial crisis are thinking of
biting a rook.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

__
This email has been scanned by the MessageLabs Email Security System.
__


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at 
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.netmailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.orgmailto:j.bac...@ieee.org
David Heald dhe...@gmail.commailto:dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] CE marking of deep-fat fryer

2011-11-15 Thread Peter Tarver
 From: ralph.mcdiar...@schneider-electric.com
[mailto:ralph.mcdiar...@schneider-electric.com]
 Sent: Tuesday, November 15, 2011 08:51

 I don't think UL would be sued; the manufacturer is ultimately liable.
 The is little or no
 benefit of 3rd party certification of a product under Tort law.

The precedence of tort law is to assign financial responsibility in
weighted proportion to the depth of pocket, regardless of actual
responsibility or lack thereof.

If UL (or any other NRTL) has a safety certification mark on a product
used with the offending fryer, even if not a part of the original
equipment, it can lead to naming them in a suit.


Regards,

Peter L. Tarver, PE

This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] CE marking of deep-fat fryer

2011-11-15 Thread McInturff, Gary
Yup, it's the theory of deep pockets but there still has to be proximal cost 
for them to drag anybody into the fray UL didn't design it, they didn't sell 
it, and they didn't tell anybody it was safe - only that it meets the standards 
for safety that exist at the time of review. I suppose it was a very strong 
implication though. 

I've been involved in exactly one case. A monitor in a bank caught fire, the 
insurance company came after us, and even after showing UL review, proper 
plastics (at least as far as the current state of product safety was concerned) 
and pointing out that the fire was caused by an employee who lit a candle near 
the monitor and forgot to blow it out before she left for the night and was the 
actual source of the fire our insurance company paid up. Cheaper to pay than to 
litigate I suppose. But neither then nor any time since then during product 
recalls or safety accidents, to the best of my knowledge, UL nor any other 3rd 
party evaluator was every made party to the lawsuit. (I remember a Listed 
Coffee pot that caught fire and Listed laptops with Li Batteries were bursting 
in flames and cause injuries for example) 


Not a lawyer by either trade nor inclination





-Original Message-
From: John Shinn [mailto:jmsh...@pacbell.net] 
Sent: Tuesday, November 15, 2011 12:43 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] CE marking of deep-fat fryer

Peter is correct.  The Lawyers will usually list everyone
remotely associated with the product, including the
retailer who sold it.

John Shinn

-Original Message- 
From: Peter Tarver
Sent: Tuesday, November 15, 2011 10:53 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] CE marking of deep-fat fryer

 From: ralph.mcdiar...@schneider-electric.com
[mailto:ralph.mcdiar...@schneider-electric.com]
 Sent: Tuesday, November 15, 2011 08:51

 I don't think UL would be sued; the manufacturer is ultimately liable.
The is little or no
 benefit of 3rd party certification of a product under Tort law.

The precedence of tort law is to assign financial responsibility in
weighted proportion to the depth of pocket, regardless of actual
responsibility or lack thereof.

If UL (or any other NRTL) has a safety certification mark on a product
used with the offending fryer, even if not a part of the original
equipment, it can lead to naming them in a suit.


Regards,

Peter L. Tarver, PE

This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an 
intended recipient, you may not review, use, copy, disclose or distribute 
this message. If you received this message in error, please contact the 
sender by reply email and destroy all copies of the original message.


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that 
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net