Re: Secondary Grounding

2001-06-02 Thread Pete Perkins
Chris PSNet, This issue was discussed on this forum last January. Check the archives for more details... There is a considerable body of knowledge that shows for the usual socket outlets (NEMA 15 in North America) or less technical, but equally acceptable information for similar Euro

Re: Secondary Grounding

2001-06-01 Thread fwest
by: cc: emc-p...@majordomo.ieee.org owner-emc-pstc@majordomSubject: Re: Secondary Grounding o.ieee.org

Re: Secondary Grounding

2001-06-01 Thread Rich Nute
Hi Chris: Consider a product with two, independent protective grounding/earthing connections. This may be by means of two power cords (as is done for uptime reliablity by employing parallel power supplies) or by means of one power cord and a separate ground connection (as, for example, by

RE: Secondary Grounding

2001-06-01 Thread Chris Maxwell
Hmm, This question centers around whether two separate ground cables equals double protection. Safety standards call for single fault testing. For Class I equipment, one of the single fault test conditions is removal of the ground connection. I'm curious how most test labs would

Secondary Grounding

2001-05-31 Thread georgea
wiring or other external factor. Using Class II insulation would require a third fault, i.e. a failure of the supplemental insulation, for a shock hazard to occur. Applying the principles above, there would be no need to provide parallel or secondary grounding paths. George Alspaugh Lexmark

RE: Secondary Grounding

2001-05-31 Thread jrbarnes
Martin, I agree with Peter about designing even Class I (grounded) power supplies with Class II (double-insulated) internal construction. Our Product Safety folks require this, and have required it going back to our IBM Lexington days. The grounding of wall outlets can not be trusted in many

RE: Secondary Grounding

2001-05-31 Thread Peter Merguerian
-5339022 Fax: + 972-(0)3-5339019 Mobile: + 972-(0)54-838175 -Original Message- From: marti...@appliedbiosystems.com [mailto:marti...@appliedbiosystems.com] Sent: Thursday, May 31, 2001 12:25 AM To: emc-p...@majordomo.ieee.org Subject: Secondary Grounding Group, This is a general

Re: Secondary Grounding

2001-05-31 Thread John Woodgate
of08958f39.0dda511c-on88256a5c.007a1...@pe-c.com, marti...@appliedbiosystems.com inimitably wrote: In order to avoid test failures during a single fault condition where the primary ground is removed, what design methods can be used to add a second ground to the system so that a ground is still

Secondary Grounding

2001-05-30 Thread MartinJP
Group, This is a general product safety question: In order to avoid test failures during a single fault condition where the primary ground is removed, what design methods can be used to add a second ground to the system so that a ground is still provided even during a single fault condition of