RE: Hazardous Area Designations/Certifications

2002-08-03 Thread Bill Lawrence
The areas Zone 1 and 2 are defined by EN 60079-14

EEx d is type of protection flameproof, defined by EN 50014, and is
suitable in Zone 1.

EEx n includes type of protection nA, nC, and nR, defined by EN 50021 and
are suitable for Zone 2.

Take a look at

http://www.fmglobal.com/research_standard_testing/product_certification/s296
.html

for an explanatory poster comparing US, EN, and IEC standards in this area.

Bill Lawrence
Senior Engineering Specialist, Hazardous Locations
FM Approvals, an FMGlobal Enterprise
1151 Bos-Prov Tpke
Norwood, MA 02062
781-255-4822
william.lawre...@fmglobal.com

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Chris Maxwell
Sent: Monday, July 29, 2002 10:52 AM
To: EMC-PSTC Internet Forum
Subject: Hazardous Area Designations/Certifications



Hi all,

I have been asked a question regarding the following:

use in a Zone 1 and Zone 2 classified area. This equipment shall be
certified EEX d and EEx n by a relevant authority (e.g. BASEEFA, CENELEC
etc.) and shall be suitable for Gas Group IIB and Temperature Class T3.

Can anyone elaborate on the above information?  What standard defines Zone
1 or Zone 2?  What standard defines EEX d and EEX n?  What about Gas
Group IIB and Temperature Class T3?

Any clarification, elaboration, elucidation and/or explanation that the
group members could provide would certainly be appreciated.

Thanks,

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 |





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list
attachment: winmail.dat

RE: Hazardous Area Designations/Certifications

2002-07-29 Thread Massey, Doug C.

Hi Chris,

Classified area = hazardous location = an area where the atmosphere may be
easily ignitable

Class = type of hazard; Class 1 = gas vapours; 2 = combustible dust, 3 =
ignitable fibers

Zone = Frequency of the hazard; Zone 1 means hazard present frequently or
for long periods; Zone 2 means hazard present only during maintenance or
mishap (leaky valve); Zone 0 means hazard present continuously in normal use
(the headspace above the flammable liquid in the holding tank, and the lid
of the tank)

EEx = Approved to the European version of the Ex standards

d = a protection method = 'flameproof enclosure' - contain the explosion
n = a protection method = 'non-incendive' - no hot surfaces

Gas Group IIB = Ethylene family of gases

T3 = maximum product surface temperature of 200 C, under fault conditions

Relevant authority for Europe = Notified Body (Notified to the ATEX
Directive 94/9/EC)

You scratched the surface on a really big topic; here are some links for
your education:

http://europa.eu.int/comm/enterprise/atex/index.htm - ATEX (94/9/EC) home
page, with links to harmonized standards and notified bodies
http://europa.eu.int/comm/enterprise/atex/guide/guide_en.pdf - ATEX
guideline
http://www.iecex.com/home.htm - IEC-EX home (like the CB Scheme for Ex)
http://www.ul.com/hazloc/ - UL's hazloc page
http://www.epsilon-ltd.com/ - Epsilon Ltd., home page - lots of hazloc info
http://www.extronics.com/Ex_Info/protection_concepts.html - EXTronics has a
good protection concepts table here.

You could impress the questioner by pointing out that 'EEx n' devices are
not allowed in Zone 1 areas... 

I'm guessing you have a European customer who needs a Zone 2 rating - I
don't really see network diagnostic equipment being needed in a Zone 1 or 0
location.

The full product rating would then likely be: ATEX Group 2 Category IIB, EEx
n IIB T3.

By the way, the ATEX Directive, mandatory July 1, 2003,requires notification
(certification by an ATEX Notified Body) of your quality system per
prEN13890, which is essentially ISO9000:2000 + specific ATEX requirements.
Periodic factory surviellence is mandated by the Directive (is this a
first?).

Also note that the Class/Division system of defining HAZLOCS is widely used
in North America; although the Class/Zone system has been allowed since 1999
(re 1999NEC Articles 505-510), only one facility has adopted the Class/Zone
system to date. There are three, largely separate, approvals efforts for
HAZLOC equipment; the USA, Europe, and ROW. The USA requires listing by an
OSHA-approved NRTL. Europe requires an ATEX Notification. ROW - Australia,
Brazil, Japan, among others - issue a national cert based on IEC standards.

Have fun.

Doug Massey
Lead Regulatory Engineer
LXE, Inc.

-Original Message-
From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
Sent: Monday, July 29, 2002 10:52 AM
To: EMC-PSTC Internet Forum
Subject: Hazardous Area Designations/Certifications



Hi all,

I have been asked a question regarding the following:

use in a Zone 1 and Zone 2 classified area. This equipment shall be
certified EEX d and EEx n by a relevant authority (e.g. BASEEFA, CENELEC
etc.) and shall be suitable for Gas Group IIB and Temperature Class T3.

Can anyone elaborate on the above information?  What standard defines Zone
1 or Zone 2?  What standard defines EEX d and EEX n?  What about Gas
Group IIB and Temperature Class T3?

Any clarification, elaboration, elucidation and/or explanation that the
group members could provide would certainly be appreciated.

Thanks,

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:  

RE: Hazardous Area Designations/Certifications

2002-07-29 Thread Dave Lorusso

Chris,

This brings back a lot of memories; my first job out of college
was with Factory Mutual Research Corporation (www.fmglobal.com)
doing hazardous location approvals.  Instead of reinventing the
wheel (and digging deep into memory), here's a link to an
excellent primer on explosion protection by R. Stahl, one of my
first clients.

http://www.rstahl.com/Exprotection/index.htm

Click on the pdf Basics of Explosion Protection for an in depth
look at this subject.  It's about 4.5 Mb.  The answers to your
questions are in there plus a whole lot more.

Good luck and best regards,

Dave Lorusso
Lorusso Technologies, LLC
www.lorusso.com
512.695.5871

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Chris
Maxwell
Sent: Monday, July 29, 2002 9:52 AM
To: EMC-PSTC Internet Forum
Subject: Hazardous Area Designations/Certifications


Hi all,

I have been asked a question regarding the following:

use in a Zone 1 and Zone 2 classified area. This equipment shall
be certified EEX d and EEx n by a relevant authority (e.g.
BASEEFA, CENELEC etc.) and shall be suitable for Gas Group IIB
and Temperature Class T3.

Can anyone elaborate on the above information?  What standard
defines Zone 1 or Zone 2?  What standard defines EEX d and
EEX n?  What about Gas Group IIB and Temperature Class T3?

Any clarification, elaboration, elucidation and/or explanation
that the group members could provide would certainly be
appreciated.

Thanks,

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1
315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 |





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Hazardous Area Designations/Certifications

2002-07-29 Thread LCrane
  Chris, 

Looks like you're dealing with equipment for use in explosive atmosphere's
legislation/standards. The exact details vary a bit depending on the
world-region (US, Europe, etc...). One of the basic how to determine zones
documents is IEC 60079-10 and its few clones. 

Watch out also for the two so-called ATEX directives comming down the pike
in Europe. Optional now, mandatory in May 2003. There is one for the
workplace and one for the equipment that goes into the workplace. 

Cheers, 

Lauren Crane
TUV America


-Original Message-
From: Chris Maxwell
To: EMC-PSTC Internet Forum
Sent: 7/29/2002 10:51 AM
Subject: Hazardous Area Designations/Certifications


Hi all,

I have been asked a question regarding the following:

use in a Zone 1 and Zone 2 classified area. This equipment shall be
certified EEX d and EEx n by a relevant authority (e.g. BASEEFA, CENELEC
etc.) and shall be suitable for Gas Group IIB and Temperature Class T3.

Can anyone elaborate on the above information?  What standard defines
Zone 1 or Zone 2?  What standard defines EEX d and EEX n?  What
about Gas Group IIB and Temperature Class T3?

Any clarification, elaboration, elucidation and/or explanation that the
group members could provide would certainly be appreciated.

Thanks,

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797
8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Hazardous Area Designations/Certifications

2002-07-29 Thread Art Michael

Hello Chris,

While I can't supply specifics, I expect you can find what you need on
Links available on the Safety Link www.safetylink.com

Once you arrive therein, using your browser's FIND function (Control-F in
most browsers), search on the following terms:

ATEX
Ex Scheme
HAZLOC
Intrinsic Safety

You will be delivered to links to sites with a plethora of info on these
subjects.

Best regards, Art Michael, Webmaster - the Safety Link


On Mon, 29 Jul 2002, Chris Maxwell wrote:

 
 Hi all,
 
 I have been asked a question regarding the following: 
 
 use in a Zone 1 and Zone 2 classified area. This equipment shall be
 certified EEX d and EEx n by a relevant authority (e.g. BASEEFA, CENELEC
 etc.) and shall be suitable for Gas Group IIB and Temperature Class T3. 
 

 Can anyone elaborate on the above information?  What standard defines
 Zone 1 or Zone 2?  What standard defines EEX d and EEX n?  What
 about Gas Group IIB and Temperature Class T3? 
 

 Any clarification, elaboration, elucidation and/or explanation that the
 group members could provide would certainly be appreciated. 


 Thanks,
 
 Chris Maxwell | Design Engineer - Optical Division
 email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024
 
 NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
 web www.nettest.com | tel +1 315 797 4449 | 
 
 
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list