Matpower 5.1 and constant impedance loads
Hi Jarek,
I don’t think any code changes should be necessary for solving the problem you
want to solve. That is, if you put the constant impedance loads in the GS and
BS columns of the bus matrix, the calculations should be correct, including all
of t
Hi Jarek,
I don’t think any code changes should be necessary for solving the problem you
want to solve. That is, if you put the constant impedance loads in the GS and
BS columns of the bus matrix, the calculations should be correct, including all
of the resulting voltages and flows. The only
Dear Matpower authors,
I wish to use the Matpower software in my PhD research.
I need to calculate power flow for the distribution system that consists of
many constant impedance and constant power loads.
After I read in the manual that " (...) the constant impedance portions can be
modeled as