Hi everybody,
Any body has template for zabbix for Cisco 7606?
I need:
- In/Out interface traffic, uptime, cpu memory utilization,
temperatures, ...
- Graph and Trigger
Thanks
--
Regards,
Shahab Vahabzadeh, Network Engineer and System Administrator
Cell Phone: +1 (415) 871 0742
PGP
Patrick:
On 3/15/14, 12:42 AM, Patrick W. Gilmore wrote:
(As if the US has control anyway)
It's all over the popular press, strange I haven't seen it here.
http://thehill.com/blogs/hillicon-valley/technology/200889-us-to-relinquish-internet-control
Alex Rubenstein a...@corp.nac.net writes:
Go look at any standard household lamp. It has a 5-15P on the end of
it, which could be plugged into an outlet rated for 20 amps (5-20R),
with 16 gauge lamp cord rated for 10 amps or less.
Mine all seem to be NEMA 1-15P, some (most?) with 18 AWG
Go look at any standard household lamp. It has a 5-15P on the end of
it, which could be plugged into an outlet rated for 20 amps (5-20R),
with 16 gauge lamp cord rated for 10 amps or less.
Mine all seem to be NEMA 1-15P, some (most?) with 18 AWG wire.
Have I been shortchanged? :)
I
On 03/18/2014 09:39 PM, William Herrin wrote:
Meh. It depends. Plug that 30 amp power strip into a 20 amp circuit.
Try to use more than 20 amps and the main breaker trips. No problem.
Plug that 20 amp power strip into a 30 amp circuit. Try to use more
than 20 amps and the strip's breaker
We have the 70S, it's pretty awesome. We paid around $15K CAD new. You might
want to look for the 12S or 19S if the price is an issue. I believe you can
also find them refurbished.
Eric
-Original Message-
From: Pui Edylie [mailto:em...@edylie.net]
Sent: March 18, 2014 10:43 PM
To:
Alex Rubenstein a...@corp.nac.net writes:
But my point remains. Appliance/load wire size is often, and many
times smaller than the ampacity of the circuit.
Heck, how many times have you plugged in a 14 gauge extension cord
to a 5-20R?
I do this all the time. In (all our) defense, lamp
On Tue, Mar 18, 2014 at 07:09:49PM -0400, David Hubbard wrote:
I've had to do that before; provider gave me a 208v/30a circuit and I
already had a power strip I wanted to re-use that had a corded L6-20P
connector on it. I purchased a L6-30P plug / L6-20R receptacle adapter
from
On Wed, Mar 19, 2014 at 9:07 AM, Lamar Owen lo...@pari.edu wrote:
2011 NEC article 210.23(A) permits 15A receptacles on 20A branch circuits;
30A branch circuits must use 30A receptacles. If the OP's 30A branch
circuit has an L6-20R on it then this would be a violation; see NEC Table
210.24
Hey folks….
We need a new customer ticketing system and I’m looking for input. I am
still working on a scope document on everything we want to do with the new
system.
The most common problem I run across is that a system is either built for
enterprise internal IT helpdesk or it is built like a
Kayako is the way to go. IIRC they have a trial up on their website, may be
worth checking out.
Tim
- Original Message -
From: Paul Stewart p...@paulstewart.org
To: nanog@nanog.org
Sent: Wednesday, March 19, 2014 9:01:11 AM
Subject: Customer Support Ticketing
Hey folks….
We need a new
Kayako is what we use. We're happy with it.
--
Joe Hamelin, W7COM, Tulalip, WA, 360-474-7474
On Wed, Mar 19, 2014 at 7:35 AM, Tim Burke t...@tburke.us wrote:
Kayako is the way to go. IIRC they have a trial up on their website, may
be worth checking out.
Tim
- Original Message -
The advice I will share with you is as follows:-
Take your wish list and divide it into Core Functions (need to have),
Functions (want to have) and Functions (nice to have).
Be prepared to compromise, the most troublesome area is going to be the
Functions (want to have).. Many of us want to
Hi Paul,
I formerly worked at Topdesk http://www.topdesk.co.uk/. I use it at my current
employer. It has a nice webbased GUI. It is not a simplistic IT helpdesk type
of software (and therefore not ultra cheap). I don't know much about
integration options (used to be fairly ok). If you get
Kayako is pretty reasonable with a few caveats. If you self host it,
which I recommend from a security/supportability/customization
standpoint, then you are also taking the trade off of dealing with
upgrading it yourself, which is not always easy. Make use of their
LoginShare functionality to
On 03/19/2014 09:51 AM, William Herrin wrote:
Nobody is talking about putting an L6-20R on a 30 amp circuit. OP was
talking about putting an L6-30P on a 20 amp appliance: a PDU that has
its own 20 amp breaker. Big difference.
If the PDU isn't listed for 30A then it's the essentially the same
On 03/19/2014 09:20 AM, Eric Dugas wrote:
We have the 70S, it's pretty awesome. We paid around $15K CAD new. You might
want to look for the 12S or 19S if the price is an issue. I believe you can
also find them refurbished.
We have a 17S, and are very happy with it. We paid a little more
On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen lo...@pari.edu wrote:
Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe
and (IMO) unwise, since the breaker in the input of the PDU does not protect
the flexible cord's conductors from internal overcurrent faults.
Yet an 18
On Wed, Mar 19, 2014 at 12:24:38PM -0400, William Herrin wrote:
On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen lo...@pari.edu wrote:
Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe
and (IMO) unwise, since the breaker in the input of the PDU does not protect
the
I recently bought a UPS with a 30R plug on it, and sat and tried for about 20
minutes to plug it into what I thought was a 30 socket. It was, in fact, a 20.
They're similar enough that if you're looking at the ends you might be
convinced that someone has bent a one of the ends of the plug
Original Message -
From: William Herrin b...@herrin.us
On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen lo...@pari.edu wrote:
Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe
and (IMO) unwise, since the breaker in the input of the PDU does not protect
the
You probably should ask your facility operator or electrician what the
requirements are (who, unlike most network engineers, is qualified to
decide what to do), but it sounds like replacing the PDU is simple and
easy, and unquestionably not a bad thing to do.
Alternatively, you can replace the
On Wed, Mar 19, 2014 at 1:06 PM, Chuck Anderson c...@wpi.edu wrote:
Yet an 18 awg PC power cable is perfectly safe when plugged in to a
5-20R on a circuit with a 20 amp breaker. Get real man.
Not really, that is just a compromise in safety standards for
convenience. It was deemed to be safe
- Original Message -
From: Joel Maslak jmas...@antelope.net
Alternatively, you can replace the 30A circuit with a 20A one. I'm not an
electrician, but I'll bet it's not much more complex or expensive than
replacing a breaker and a receptacle,
It is exactly that: no one says you
On Wed, Mar 19, 2014 at 1:18 PM, Jay Ashworth j...@baylink.com wrote:
From: William Herrin b...@herrin.us
Yet an 18 awg PC power cable is perfectly safe when plugged in to a
5-20R on a circuit with a 20 amp breaker. Get real man.
A PC isn't a power distribution device.
There are no power
Just because you say the debate should be ended doesn't mean it's true, or that
you are even correct.
To end the debate, my staff master electrician says just replace the breaker.
Your staff electrician missed half the answer, which would be to replace the
breaker AND the receptacle. But you
To end the debate, my staff master electrician says just replace the
breaker. You can leave the outlet if you want or replace it too.
Doesn't matter. The 30A circuit should be 10 gauge which is fine for 20amp.
And to Jay: Network cables most certainly do carry power.
On 3/19/2014 12:18 PM,
Fair point.
PoE is 48V and current limited, though, precisely to keep it what the Code
calls Low Voltage.
On March 19, 2014 1:26:54 PM EDT, William Herrin b...@herrin.us wrote:
On Wed, Mar 19, 2014 at 1:18 PM, Jay Ashworth j...@baylink.com wrote:
From: William Herrin b...@herrin.us
Yet an 18
On Wed, Mar 19, 2014 at 1:55 PM, Jay Ashworth j...@baylink.com wrote:
PoE is 48V and current limited, though, precisely to keep it what the Code
calls Low Voltage.
Hi Jay,
50 watts DC. It won't electrocute you (that's AC) but it's the same
power that makes a 40 watt bulb burning hot.
Regards,
[Whee. This discussion is good for me, as I need to refresh my memory
on the relevant code sections for some new data center
clients.thanks, Bill, you're a great help!]
On 03/19/2014 12:24 PM, William Herrin wrote:
Yet an 18 awg PC power cable is perfectly safe when plugged in to a
5-20R
On Wed, Mar 19, 2014 at 02:05:42PM -0400, William Herrin wrote:
On Wed, Mar 19, 2014 at 1:55 PM, Jay Ashworth j...@baylink.com wrote:
PoE is 48V and current limited, though, precisely to keep it what the Code
calls Low Voltage.
Hi Jay,
50 watts DC. It won't electrocute you (that's AC)
On 03/19/2014 02:05 PM, William Herrin wrote:
50 watts DC. It won't electrocute you (that's AC) but it's the same
power that makes a 40 watt bulb burning hot.
802.3af is limited to 15.4W, and 802.3at to 25.5W. The limits for Class
2 and 3 circuits are found in Chapter 9, Table 11 (A and B), of
On Wed, Mar 19, 2014 at 2:19 PM, Chuck Anderson c...@wpi.edu wrote:
On Wed, Mar 19, 2014 at 02:05:42PM -0400, William Herrin wrote:
50 watts DC. It won't electrocute you (that's AC) but it's the same
power that makes a 40 watt bulb burning hot.
I don't know where you are getting your facts,
L3 escalates on Peering/CDN/Neutrality.
http://arstechnica.com/information-technology/2014/03/level-3-blames-internet-slowdowns-on-isps-refusal-to-upgrade-networks/
--
Sent from my Android phone with K-9 Mail. Please excuse my brevity.
Hey paul
We use Netsuite with OpenNms ~ as an ISP i think you will always be stuck
with alot of customization ~ unless you build your own
Good luck
Chris
On Wed, Mar 19, 2014 at 10:01 AM, Paul Stewart p...@paulstewart.org wrote:
Hey folks
We need a new customer ticketing system and I'm
Paul,
My past two job, I used Kayako. I like it so much I bought a copy for my
side project. I feel work flow with kayako is will thought out for tech
minded people. Having easy access to staff notes while still able to see
the ticket is a big deal for me. Its someway easy to customize
On 3/19/14, 10:21, Jay Ashworth wrote:
It is exactly that: no one says you*can't* wire a 20A branch circuit with
#10.
It is even*possible*, though unlikely, that if you did so, you wouldn't
have to derate it to 80%. I would have to reread the Code to be sure.
Well, I'd say it's pretty
For what it's worth, I've actually heard the Intuit guys that sell Quickbase
will build and customize your ticketing system for you. I haven't looked that
heavily into other options since I've run a few RT instances I'm most
comfortable there but I'm sure you know it doesn't integrate with
Another +1/like/upvote for Kayako.
RAY SANDERS
Senior Systems Engineer
ray.sand...@sheknows.com
From: Nolan Rollo nro...@kw-corp.com
Sent: Wednesday, March 19, 2014 3:14 PM
To: Paul Stewart; nanog@nanog.org
Subject: RE: Customer Support Ticketing
For
Jay Ashworth j...@baylink.com writes:
It is exactly that: no one says you *can't* wire a 20A branch circuit with
#10.
It is even *possible*, though unlikely, that if you did so, you wouldn't
have to derate it to 80%. I would have to reread the Code to be sure.
It's not the conductor that
I saw mention of Quckbase and wanted to chime in…I spent some time consulting
inside Intuit a few years ago, and my oh my they sure eat their dog food on
QuickBase. It’s crazy flexible - easy learning curve for basic use, and the
scripting language allows for some crazy creative tricks to
On 3/19/2014 7:00 AM, Alex Rubenstein wrote:
Go look at any standard household lamp. It has a 5-15P on the end of
it, which could be plugged into an outlet rated for 20 amps (5-20R),
with 16 gauge lamp cord rated for 10 amps or less.
Mine all seem to be NEMA 1-15P, some (most?) with 18 AWG
- Original Message -
From: Alex Rubenstein a...@corp.nac.net
And to Jay: Network cables most certainly do carry power.
No, they carry signal, which is considerably different - unless of
course it is 802.1af.
That's what he meant, yes, and a couple other people made the point as
- Original Message -
From: Seth Mattinen se...@rollernet.us
On 3/19/14, 10:21, Jay Ashworth wrote:
It is exactly that: no one says you*can't* wire a 20A branch circuit
with #10.
It is even*possible*, though unlikely, that if you did so, you wouldn't
have to derate it to 80%. I
44 matches