On 03/19/2014 06:33 PM, Rob Seastrom wrote: It's not the conductor that you're derating; it's the breaker. Per NEC Table 310.16, ampacity of #12 copper THHN/THWN2 (which is almost certainly what you're pulling) with 3 conductors in a conduit is 30 amps. Refer to Table 310.15(B)(2)(a) for

Re: L6-20P - L6-30R

2014-03-20 Thread Rob Seastrom
Lamar Owen lo...@pari.edu writes: Actually, there is no NEC 384.16 any more, at least in the 2011 code. Guilty. I reflexively reached for my 2008 copy since that's the code of record here where I live. Glad we're not on 2011, wish we were still on 2005; a lot of stupidity has crept in since

Re: L6-20P - L6-30R

2014-03-20 Thread Gary Buhrmaster
On Thu, Mar 20, 2014 at 4:00 PM, Rob Seastrom r...@seastrom.com wrote: Lamar Owen lo...@pari.edu writes: Actually, there is no NEC 384.16 any more, at least in the 2011 code. Guilty. I reflexively reached for my 2008 copy since that's the code of record here where I live. Glad we're not

Re: L6-20P - L6-30R

2014-03-20 Thread Brandon Galbraith
Is it too late to demand code be in open Github repos with changes tracked at no cost? On Thu, Mar 20, 2014 at 12:12 PM, Gary Buhrmaster gary.buhrmas...@gmail.com wrote: On Thu, Mar 20, 2014 at 3:05 PM, Lamar Owen lo...@pari.edu wrote: . Tracking code changes fuels an entire industry, and

Re: L6-20P - L6-30R

2014-03-20 Thread Lamar Owen
On 03/20/2014 12:27 PM, Gary Buhrmaster wrote: Think of the children! I hear the 2017 edition of NFPA 70 (aka NEC) may require one to turn off the power to the entire household in order to plug in a coffee maker to minimize potential arc flash hazard (just kidding). Gary ROTFL. No,

Re: L6-20P - L6-30R

2014-03-20 Thread Jay Hennigan
On 3/18/14 3:54 PM, George Herbert wrote: This sort of thing is usually an adapter, a little cylinder with a L6-20R on one end and a L6-30P on the other, since the loads are safe. Either that, or a short jumper cable wired the same way. The loads aren't safe. You will have a 30-amp circuit

Re: L6-20P - L6-30R

2014-03-20 Thread Owen DeLong
On Mar 20, 2014, at 4:52 PM, Jay Hennigan j...@west.net wrote: On 3/18/14 3:54 PM, George Herbert wrote: This sort of thing is usually an adapter, a little cylinder with a L6-20R on one end and a L6-30P on the other, since the loads are safe. Either that, or a short jumper cable wired the

Re: L6-20P - L6-30R

2014-03-19 Thread Rob Seastrom
Alex Rubenstein a...@corp.nac.net writes: Go look at any standard household lamp. It has a 5-15P on the end of it, which could be plugged into an outlet rated for 20 amps (5-20R), with 16 gauge lamp cord rated for 10 amps or less. Mine all seem to be NEMA 1-15P, some (most?) with 18 AWG

RE: L6-20P - L6-30R

2014-03-19 Thread Alex Rubenstein
Go look at any standard household lamp. It has a 5-15P on the end of it, which could be plugged into an outlet rated for 20 amps (5-20R), with 16 gauge lamp cord rated for 10 amps or less. Mine all seem to be NEMA 1-15P, some (most?) with 18 AWG wire. Have I been shortchanged? :) I

Re: L6-20P - L6-30R

2014-03-19 Thread Lamar Owen
On 03/18/2014 09:39 PM, William Herrin wrote: Meh. It depends. Plug that 30 amp power strip into a 20 amp circuit. Try to use more than 20 amps and the main breaker trips. No problem. Plug that 20 amp power strip into a 30 amp circuit. Try to use more than 20 amps and the strip's breaker

Re: L6-20P - L6-30R

2014-03-19 Thread Rob Seastrom
Alex Rubenstein a...@corp.nac.net writes: But my point remains. Appliance/load wire size is often, and many times smaller than the ampacity of the circuit. Heck, how many times have you plugged in a 14 gauge extension cord to a 5-20R? I do this all the time. In (all our) defense, lamp

Re: L6-20P - L6-30R

2014-03-19 Thread Chuck Anderson
On Tue, Mar 18, 2014 at 07:09:49PM -0400, David Hubbard wrote: I've had to do that before; provider gave me a 208v/30a circuit and I already had a power strip I wanted to re-use that had a corded L6-20P connector on it. I purchased a L6-30P plug / L6-20R receptacle adapter from

Re: L6-20P - L6-30R

2014-03-19 Thread William Herrin
On Wed, Mar 19, 2014 at 9:07 AM, Lamar Owen lo...@pari.edu wrote: 2011 NEC article 210.23(A) permits 15A receptacles on 20A branch circuits; 30A branch circuits must use 30A receptacles. If the OP's 30A branch circuit has an L6-20R on it then this would be a violation; see NEC Table 210.24

Re: L6-20P - L6-30R

2014-03-19 Thread Lamar Owen
On 03/19/2014 09:51 AM, William Herrin wrote: Nobody is talking about putting an L6-20R on a 30 amp circuit. OP was talking about putting an L6-30P on a 20 amp appliance: a PDU that has its own 20 amp breaker. Big difference. If the PDU isn't listed for 30A then it's the essentially the same

Re: L6-20P - L6-30R

2014-03-19 Thread William Herrin
On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen lo...@pari.edu wrote: Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe and (IMO) unwise, since the breaker in the input of the PDU does not protect the flexible cord's conductors from internal overcurrent faults. Yet an 18

Re: L6-20P - L6-30R

2014-03-19 Thread Chuck Anderson
On Wed, Mar 19, 2014 at 12:24:38PM -0400, William Herrin wrote: On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen lo...@pari.edu wrote: Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe and (IMO) unwise, since the breaker in the input of the PDU does not protect the

RE: L6-20P - L6-30R

2014-03-19 Thread Staudinger, Malcolm
, but no amount of trying will make them fit. Malcolm -Original Message- From: Jay Ashworth [mailto:j...@baylink.com] Sent: Tuesday, March 18, 2014 4:12 PM To: NANOG Subject: Re: L6-20P - L6-30R - Original Message - From: Randy a...@djlab.com I have a situation where a 208v

Re: L6-20P - L6-30R

2014-03-19 Thread Jay Ashworth
Original Message - From: William Herrin b...@herrin.us On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen lo...@pari.edu wrote: Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe and (IMO) unwise, since the breaker in the input of the PDU does not protect the

Re: L6-20P - L6-30R

2014-03-19 Thread Joel Maslak
You probably should ask your facility operator or electrician what the requirements are (who, unlike most network engineers, is qualified to decide what to do), but it sounds like replacing the PDU is simple and easy, and unquestionably not a bad thing to do. Alternatively, you can replace the

Re: L6-20P - L6-30R

2014-03-19 Thread William Herrin
On Wed, Mar 19, 2014 at 1:06 PM, Chuck Anderson c...@wpi.edu wrote: Yet an 18 awg PC power cable is perfectly safe when plugged in to a 5-20R on a circuit with a 20 amp breaker. Get real man. Not really, that is just a compromise in safety standards for convenience. It was deemed to be safe

Re: L6-20P - L6-30R

2014-03-19 Thread Jay Ashworth
- Original Message - From: Joel Maslak jmas...@antelope.net Alternatively, you can replace the 30A circuit with a 20A one. I'm not an electrician, but I'll bet it's not much more complex or expensive than replacing a breaker and a receptacle, It is exactly that: no one says you

Re: L6-20P - L6-30R

2014-03-19 Thread William Herrin
On Wed, Mar 19, 2014 at 1:18 PM, Jay Ashworth j...@baylink.com wrote: From: William Herrin b...@herrin.us Yet an 18 awg PC power cable is perfectly safe when plugged in to a 5-20R on a circuit with a 20 amp breaker. Get real man. A PC isn't a power distribution device. There are no power

RE: L6-20P - L6-30R

2014-03-19 Thread Alex Rubenstein
Just because you say the debate should be ended doesn't mean it's true, or that you are even correct. To end the debate, my staff master electrician says just replace the breaker. Your staff electrician missed half the answer, which would be to replace the breaker AND the receptacle. But you

Re: L6-20P - L6-30R

2014-03-19 Thread Aaron
To end the debate, my staff master electrician says just replace the breaker. You can leave the outlet if you want or replace it too. Doesn't matter. The 30A circuit should be 10 gauge which is fine for 20amp. And to Jay: Network cables most certainly do carry power. On 3/19/2014 12:18 PM,

Re: L6-20P - L6-30R

2014-03-19 Thread Jay Ashworth
Fair point. PoE is 48V and current limited, though, precisely to keep it what the Code calls Low Voltage. On March 19, 2014 1:26:54 PM EDT, William Herrin b...@herrin.us wrote: On Wed, Mar 19, 2014 at 1:18 PM, Jay Ashworth j...@baylink.com wrote: From: William Herrin b...@herrin.us Yet an 18

Re: L6-20P - L6-30R

2014-03-19 Thread William Herrin
On Wed, Mar 19, 2014 at 1:55 PM, Jay Ashworth j...@baylink.com wrote: PoE is 48V and current limited, though, precisely to keep it what the Code calls Low Voltage. Hi Jay, 50 watts DC. It won't electrocute you (that's AC) but it's the same power that makes a 40 watt bulb burning hot. Regards,

Re: L6-20P - L6-30R

2014-03-19 Thread Lamar Owen
[Whee. This discussion is good for me, as I need to refresh my memory on the relevant code sections for some new data center clients.thanks, Bill, you're a great help!] On 03/19/2014 12:24 PM, William Herrin wrote: Yet an 18 awg PC power cable is perfectly safe when plugged in to a 5-20R

Re: L6-20P - L6-30R

2014-03-19 Thread Chuck Anderson
On Wed, Mar 19, 2014 at 02:05:42PM -0400, William Herrin wrote: On Wed, Mar 19, 2014 at 1:55 PM, Jay Ashworth j...@baylink.com wrote: PoE is 48V and current limited, though, precisely to keep it what the Code calls Low Voltage. Hi Jay, 50 watts DC. It won't electrocute you (that's AC)

Re: L6-20P - L6-30R

2014-03-19 Thread Lamar Owen
On 03/19/2014 02:05 PM, William Herrin wrote: 50 watts DC. It won't electrocute you (that's AC) but it's the same power that makes a 40 watt bulb burning hot. 802.3af is limited to 15.4W, and 802.3at to 25.5W. The limits for Class 2 and 3 circuits are found in Chapter 9, Table 11 (A and B), of

Re: L6-20P - L6-30R

2014-03-19 Thread William Herrin
On Wed, Mar 19, 2014 at 2:19 PM, Chuck Anderson c...@wpi.edu wrote: On Wed, Mar 19, 2014 at 02:05:42PM -0400, William Herrin wrote: 50 watts DC. It won't electrocute you (that's AC) but it's the same power that makes a 40 watt bulb burning hot. I don't know where you are getting your facts,

Re: L6-20P - L6-30R

2014-03-19 Thread Seth Mattinen
On 3/19/14, 10:21, Jay Ashworth wrote: It is exactly that: no one says you*can't* wire a 20A branch circuit with #10. It is even*possible*, though unlikely, that if you did so, you wouldn't have to derate it to 80%. I would have to reread the Code to be sure. Well, I'd say it's pretty

Re: L6-20P - L6-30R

2014-03-19 Thread Rob Seastrom
Jay Ashworth j...@baylink.com writes: It is exactly that: no one says you *can't* wire a 20A branch circuit with #10. It is even *possible*, though unlikely, that if you did so, you wouldn't have to derate it to 80%. I would have to reread the Code to be sure. It's not the conductor that

Re: L6-20P - L6-30R

2014-03-19 Thread Larry Sheldon
On 3/19/2014 7:00 AM, Alex Rubenstein wrote: Go look at any standard household lamp. It has a 5-15P on the end of it, which could be plugged into an outlet rated for 20 amps (5-20R), with 16 gauge lamp cord rated for 10 amps or less. Mine all seem to be NEMA 1-15P, some (most?) with 18 AWG

Re: L6-20P - L6-30R

2014-03-19 Thread Jay Ashworth
- Original Message - From: Alex Rubenstein a...@corp.nac.net And to Jay: Network cables most certainly do carry power. No, they carry signal, which is considerably different - unless of course it is 802.1af. That's what he meant, yes, and a couple other people made the point as

Re: L6-20P - L6-30R

2014-03-19 Thread Jay Ashworth
- Original Message - From: Seth Mattinen se...@rollernet.us On 3/19/14, 10:21, Jay Ashworth wrote: It is exactly that: no one says you*can't* wire a 20A branch circuit with #10. It is even*possible*, though unlikely, that if you did so, you wouldn't have to derate it to 80%. I

L6-20P - L6-30R

2014-03-18 Thread Randy
I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R). Before I order the correct PDU's and whip cords...sanity check...are connectors 'similar' enough that this is possible (with force) or am I going to find we've actually got L6-20R's on the

Re: L6-20P - L6-30R

2014-03-18 Thread Mike Hale
They're different. You can't force them. On Tue, Mar 18, 2014 at 12:24 PM, Randy a...@djlab.com wrote: I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R). Before I order the correct PDU's and whip cords...sanity check...are connectors

Re: L6-20P - L6-30R

2014-03-18 Thread Wayne E Bouchard
The whole point behind the locking connectors (like the IEC connectors) is to prevent you from plugging the wrong connectors together. Not only are the different dimensions, but the prongs are keyed differently as well. If you put a L6-20P device into a L6-30R, then it was done by physically

Re: L6-20P - L6-30R

2014-03-18 Thread Niels Bakker
* w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]: I have had to do this at times but it is not strictly allowed by codes and not at all recommended. It's an active fire hazard. The cables aren't rated (= built) for the power draw. -- Niels.

Re: L6-20P - L6-30R

2014-03-18 Thread Michael Brown
‎The connectors are definitely distinct and incompatible, you won't be able to force a 20 into a 30 or vice versa.  So yes, one of the ends has been changed. M.   Original Message   From: Randy Sent: Tuesday, March 18, 2014 18:42 To: nanog@nanog.org Reply To: a...@djlab.com Subject: L6-20P

Re: L6-20P - L6-30R

2014-03-18 Thread George Herbert
https://www.21cii.com/ITStudio/Content/Resources/Images/Appendix/Plug%20%20Power/SB%202P-3W_505x447.png I think the 250 v 15 amp plugs fit in the 20 amp sockets, but the 20s don't fit in the 30 sockets. This sort of thing is usually an adapter, a little cylinder with a L6-20R on one end and a

Re: L6-20P - L6-30R

2014-03-18 Thread Andrei Ivanov
Randy a...@djlab.com wrote: I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R).   Before I order the correct PDU's and whip cords...sanity check...are connectors 'similar' enough that this is possible (with force) or am I going to find we've

Re: L6-20P - L6-30R

2014-03-18 Thread George Herbert
Crap, was looking at the non-locking ones. Ignore that. On Tue, Mar 18, 2014 at 3:54 PM, George Herbert george.herb...@gmail.comwrote: https://www.21cii.com/ITStudio/Content/Resources/Images/Appendix/Plug%20%20Power/SB%202P-3W_505x447.png I think the 250 v 15 amp plugs fit in the 20 amp

RE: L6-20P - L6-30R

2014-03-18 Thread David Hubbard
staff to reset the breaker. David -Original Message- From: Randy [mailto:a...@djlab.com] Sent: Tuesday, March 18, 2014 3:25 PM To: nanog@nanog.org Subject: L6-20P - L6-30R I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R). Before I order

Re: L6-20P - L6-30R

2014-03-18 Thread Justin M. Streiner
On Tue, 18 Mar 2014, Randy wrote: I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R). Before I order the correct PDU's and whip cords...sanity check...are connectors 'similar' enough that this is possible (with force) or am I going to find

Re: L6-20P - L6-30R

2014-03-18 Thread Jay Ashworth
- Original Message - From: Randy a...@djlab.com I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R). Before I order the correct PDU's and whip cords...sanity check...are connectors 'similar' enough that this is possible (with force) or

Re: L6-20P - L6-30R

2014-03-18 Thread Stephen Sprunk
On 18-Mar-14 17:54, Niels Bakker wrote: * w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]: I have had to do this at times but it is not strictly allowed by codes and not at all recommended. It's an active fire hazard. The cables aren't rated (= built) for the power draw.

RE: L6-20P - L6-30R

2014-03-18 Thread Alex Rubenstein
Strictly speaking, no, you cannot do this. The diameter of the pattern of the pins are different 20 to 30 amps. If no electrical inspectors are looking, yes, you can bend the pins and make it work. I've done it, others have done it, but you shouldn't do it and it is a clear electrical code

RE: L6-20P - L6-30R

2014-03-18 Thread Alex Rubenstein
Go look at any standard household lamp. It has a 5-15P on the end of it, which could be plugged into an outlet rated for 20 amps (5-20R), with 16 gauge lamp cord rated for 10 amps or less. It all depends on the connected load. * w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]:

Re: L6-20P - L6-30R

2014-03-18 Thread Randy
On 03/18/2014 7:11 pm, Jay Ashworth wrote: As it happens, the chart at http://www.stayonline.com/reference-nema-locking.aspx suggests that the L6-20 and L6-30 are less different than you'd expect. I *think* those are on different diameters, and a datacenter employee ought to friggin' know

Re: L6-20P - L6-30R

2014-03-18 Thread Randy Carpenter
- Original Message - On 18-Mar-14 17:54, Niels Bakker wrote: * w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]: I have had to do this at times but it is not strictly allowed by codes and not at all recommended. It's an active fire hazard. The cables aren't rated

Re: L6-20P - L6-30R

2014-03-18 Thread Jay Ashworth
- Original Message - From: Stephen Sprunk step...@sprunk.org On 18-Mar-14 17:54, Niels Bakker wrote: * w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]: I have had to do this at times but it is not strictly allowed by codes and not at all recommended. It's an

Re: L6-20P - L6-30R

2014-03-18 Thread Laszlo Hanyecz
It's temporary unless it works. -Laszlo On Mar 18, 2014, at 11:30 PM, Jay Ashworth j...@baylink.com wrote: - Original Message - From: Stephen Sprunk step...@sprunk.org On 18-Mar-14 17:54, Niels Bakker wrote: * w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]: I have

Re: L6-20P - L6-30R

2014-03-18 Thread William Herrin
On Tue, Mar 18, 2014 at 6:54 PM, Niels Bakker niels=na...@bakker.net wrote: * w...@typo.org (Wayne E Bouchard) [Tue 18 Mar 2014, 23:53 CET]: I have had to do this at times but it is not strictly allowed by codes and not at all recommended. It's an active fire hazard. The cables aren't rated

Re: L6-20P - L6-30R

2014-03-18 Thread Larry Sheldon
we've actually got L6-20R's on the provider side? http://www.amazon.com/L6-20P-L6-30R-Locking-Power-Adapter/dp/B004W359W0 -- Requiescas in pace o email Two identifying characteristics of System Administrators: Ex turpi causa non oritur actio

Re: L6-20P - L6-30R

2014-03-18 Thread Wayne E Bouchard
On Tue, Mar 18, 2014 at 09:39:46PM -0400, William Herrin wrote: There just aren't a whole lot of failure modes here that result in fire short of one or the other breaker failing. And that results in fire regardless of the amperage mismatch. This, by the way, is why you're allowed to plug

Re: L6-20P - L6-30R

2014-03-18 Thread Jeremy Bresley
On 3/18/2014 6:11 PM, Jay Ashworth wrote: From: Randy a...@djlab.com I have a situation where a 208v/20A PDU (L6-20P) is supposedly hooked to a 208v/30A circuit (L6-30R). Before I order the correct PDU's and whip cords...sanity check...are connectors 'similar' enough that this is possible (with