2014-05-27 Thread Nick Soleil
Hi Jay, It is not acceptable to wire the AFCI breaker with the utility power on the output of the AFCI breaker. That does not meet the specifications for the AFCI breakers. These breakers are sensitive to having voltage on their output when the breaker is opened, which can damage the AFCI

Re: [RE-wrenches] 2014 NEC

2014-05-27 Thread Jay Peltz
Hi nick Good to know, I was told this by bill brooks at a training a few months ago. Jay Sent from my iPhone On May 27, 2014, at 9:00 AM, Nick Soleil nsol...@enphaseenergy.com wrote: Hi Jay, It is not acceptable to wire the AFCI breaker with the utility power on the output of the

Re: [RE-wrenches] 2014 NEC

2014-05-27 Thread Bill Brooks
Nick and Jay, There is a basic problem that products are not currently available to specifically address this application. I know Enphase has done a lot of research lately about this issue, so they may have uncovered problems that were previously not known. My information is that the

Re: [RE-wrenches] 2014 NEC

2014-05-27 Thread Will White
We’ve run into the problem in MA where the electrical board suggested we cut apart Enphase trunk cable to put it in a raceway. We all know that isn’t possible. From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Tuesday, May 27, 2014 3:18 PM To:

Re: [RE-wrenches] 2014 NEC

2014-05-27 Thread William Korthof
Code insanity. There is never voltage on the load side of an open AC switch, arc fault, or circuit breaker device supplying a solar inverter that meets UL1741. Solar inverters are current sources only, and only while utility voltage is present. /wk William Korthof 714.875.3576 Sustainable