If only an SMA would work here. But DC volts too low. We are using Solectria
PVI5200TLS.
We do not use PV wire. We transition to THWN-2 in conduit immediately.
William
Miller Solar
> On Oct 6, 2014, at 8:30 PM, Chris Mason wrote:
>
> I presumed SMA TL series.
>
>> On Mon, Oct 6
William,
Just about a week ago I asked Greg Smith at SMA to confirm that it
would be appropriate to use THWN-2 in the buried PVC conduit for the DC run
from a pole mount array with it's DC disco to the SMA DC disco below their
inverter..Just to be sure you're not thinking you have t
I presumed SMA TL series.
On Mon, Oct 6, 2014 at 10:02 PM, Jerry Shafer
wrote:
> As i read the thread you say TL which TL SMA, AE ect. They have defferent
> dc input designs
> On Oct 6, 2014 12:21 PM, "jay peltz" wrote:
>
>> I do believe the outback and midnite combiners have a lock hole to
>>
As i read the thread you say TL which TL SMA, AE ect. They have defferent
dc input designs
On Oct 6, 2014 12:21 PM, "jay peltz" wrote:
> I do believe the outback and midnite combiners have a lock hole to prevent
> exactly your concern.
> unauthorized access.
>
> jay
>
> peltz power
> On Oct 6, 20
After re-reading it looks like you’re not wanting the RC remotes but rather the
remote option for the PS series. So, as Roseanne Roseannadanna would
say…..never mind.
On Oct 6, 2014, at 5:20 PM, Starlight Solar Power Systems
wrote:
Hi Chris,
We still have stock on the RC6, RC7 and RC7GS tha
I don't understand the reference to Arc-Flash. Arc-flash ratings are
dependent on high current potential, typically above 700 amp short circuit
current. I don't think you can get an arc flash from a solar system as
solar is inherently current limited.
On Mon, Oct 6, 2014 at 2:40 PM, William Miller
If it is a TL, there is a combiner input, and yes, you can use no fuses for
two strings.
On Mon, Oct 6, 2014 at 6:27 PM, William Miller
wrote:
> Mike:
>
>
>
> If I have just two strings of Solarworld SW275 modules per inverter, can I
> use one input to the built-in combiner to feed in a combined
Hi Chris,
We still have stock on the RC6, RC7 and RC7GS that came before the RC/GS. These
all work with the old RV and Legend series inverters. I will be back in Az in
about 1 week if you still need one.
Larry
On Oct 6, 2014, at 9:37 AM, Chris Daum wrote:
Dear people:
Does anyone have the
I've always been a fan of Petzl stuff, super comfortable. Here is a quick link
I found.
http://www.patrollersupply.com/equipment/item_4446.asp
jay
peltz power
On Oct 6, 2014, at 3:31 PM, David Brearley wrote:
> Hi Bill,
>
> Joey Krys not only sells a lot of fall protection equipment, but al
Hi Bill,
Joey Krys not only sells a lot of fall protection equipment, but also
understands some of the unique requirements of PV contractors:
> Joey Krys
> ToolUp Professional Contractor Supplies
> Sales / Fall Protection Specialist
>
> Mobile: 858-864-2821
>
Mike:
If I have just two strings of Solarworld SW275 modules per inverter, can I
use one input to the built-in combiner to feed in a combined string? My
calculations indicate that I might be able to feed the two strings into one
25 amp KLKD fuse. The Isc is 8.94. times 1.25 = 11.715. Times
I do believe the outback and midnite combiners have a lock hole to prevent
exactly your concern.
unauthorized access.
jay
peltz power
On Oct 6, 2014, at 11:40 AM, William Miller wrote:
> Wrenches:
>
> We are getting up to speed on using transformer-less inverters. I have
> advocated long fo
Any time we do a ground array, at the array location we combine the strings
and have a disconnect and it has come in handy to
On Oct 6, 2014 10:41 AM, "Mark Westbrock"
wrote:
> If you don't want to combine strings at the array, then I would use a
> Square D HU361 for each string. It is a lot of
Hi William,
I wanted to let you know that currently, there is no bypass terminal to allow
for combining at the array in this series of inverters. We have gotten a lot of
feedback from customers that this is a required feature. Working toward that,
in the next few months, we will phase into prod
If you don't want to combine strings at the array, then I would use a
Square D HU361 for each string. It is a lot of hardware, but not too
expensive and very straightforward for a lay person to shut off without
risk.
Cheers,
Mark
*Mark Westbrock*
Field Manager & Employee-Owner
NM EE98J Jou
How about the Midnite Solar four pole disconnect?
Can't remember the model number but recently installed one on a two string TL
input circuit. They are made for disconnecting both positive and negative.
Jeremy Rodriguez,
President
All Solar, Inc.
1463 M
Penrose Colorado 81240
719-372-3808 offi
William,
No suggestions for what might work, but how would you be sure that the
gardener (or other) would not attempt to open the fuseholders under load?
Perhaps the box could have a padlock on it and the key could be located at
the inverters where they could be shutdown prior to opening the
fuseho
Wrenches:
We are getting up to speed on using transformer-less inverters. I have
advocated long for the additional safety offered by these inverters but I am
realizing the trade-offs with the new technology: The implementation gets
more complicated with the requirement for PV wire, OCPD and d
Chris and all,
In case you don't know:
- it was called the "Power Station", with the initials PS ( which some Wrenches
agreed stood for "P. of S."
- it was marketed as a lower cost, stripped-down SW.
- the standard SW remote is used to program it; there was no remote specific to
this model.
- i
Hi mick,
The more current classic firmware has a VMX mode which is adjustable for absorb
time based on how quickly it got there, plus you can set it to skip days etc.
Also. The new wiz bang jr allows better return amp monitoring
So if you are running old firmware, good time to upgrade.
Jay
P
Dear people:
Does anyone have the RC option for the old Trace power series inverter? I
have a customer looking for one; you can't change any of the settings
without it.
Feel free to contact me off list.
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax
www.oasismontana.com
___
I'm just wondering if anyone could tell me if I have programmed this right
on my own off-grid cabin system with an Outback FX80 -
If I set the re-bulk fairly low (like 24.5 volts for a 24 volt system) I
should avoid bulk/absorb charging on days when the batteries are not being
cycled? There are no
Mick,
You are in luck!
The Classic controller can be programmed to skip up to 32 days of
bulk charging.
Look for this in the Main menu under Charge/ Advanced/ Skipand
select the # of days you want to skip.
Not sure what firmwar
Greetings, Mechanics~
My client's (flooded lead acid) battery is in Float almost all the time,
courtesy of an XW inverter stack plus public utility power while the system
waits in standby. "Selling to grid" is not enabled for complicated reasons,
so here's the problem.
Each day at sunup, the Midn
I certainly do. We use DBI-Sala safety equipment despite the POOR sales rep and
my local supplier, the equipment is first rate. When one is selecting devices
for LIFE SAVING WORK safety at the cost of ~2K for 2 persons, I would have
thought their rep would have been more attentive. We even calle
25 matches
Mail list logo