Hi William,
I don't see the sequence below that you are referencing.
Thanks
On Thu, Feb 12, 2015 at 10:47 AM, will...@millersolar.com wrote:
Friends:
I understood the generator had to be started and stopped manually. I have
a client who was using the sequence below to stop the generator
Hi All,
It’s my understanding that that yes the EQ on the inverter/charger needs to be
started manually, but if the gen is running for an EQ cycle and it turns off
(say runs out of fuel) before the EQ cycle is complete, the Outback charge
controllers can still be in EQ mode. This happened
Sounds like a perfect use for an Arduino driven speaker.
There are thousands of publicly posted circuits that will probably net a simple
solution, or the name of a local person who would love to help/ adapt one for
this purpose.
Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse
The alarm system is already set up. It involves and Idec ice cube relay
with a 240 V coil connected between L-1 AND L-2 of the AC in bus bars.
When the grid drops out, the relay reverts to the N/C position, allowing a
120 V contact to send power to a box in the dining room (that has the
indicator
Ive had clients do it for years with no problems that I know of.
jay
peltz power
On Feb 12, 2015, at 9:47 AM, will...@millersolar.com wrote:
Friends:
I understood the generator had to be started and stopped manually. I have a
client who was using the sequence below to stop the
Might this work?
http://www.galco.com/buy/Edwards-Signaling/1064-N5?source=googleshopping
http://www.galco.com/buy/Edwards-Signaling/1064-N5?source=googleshoppingkpid=1064-N5-EDWDgclid=Cj0KEQiAu_GmBRDhtK-kzqKcuJwBEiQAJvB8n49GEUrgP8Uur3FaS47lpinWK8HaY1q0l_Eq9p6pPqoaAiMd8P8HAQ
We've found the M250 to be just as stable as the M215. Usually when we have an
issue it's right out of the box.
Thanks,
Will
Will White
Director of Construction - East Coast
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
Mac:
I meant the sequence that Jay had listed:
Gen to manual on
Initiate EQ
Gen to auto
Done
William
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Mac Lewis
Sent: Thursday, February 12, 2015 10:54 AM
To: RE-wrenches
Subject: Re:
HI All,
Ive had someone ask me about the following magnum and I know there are many
more experienced folks that maybe can chime in.
MS4448
V1-00138
2007
The problem is that for the life of the inverter it hasn't worked well for
things like digital/electronic washer/dryers, even glow bar
Mac:
Apparently so, but this operation is not supported. It supposedly works.
William
On Feb 12, 2015, at 3:18 PM, Mac Lewis maclew...@gmail.com wrote:
Hi Jay William,
Just so I understand, you can put the mate into auto right after the eq is
enabled (not after eq has finished),
Jay,
I can't answer your question, but only relate that I had a similar
experience.
An early Magnum MS4448AE would not reliably start and run a modern
hydronic boiler in an off grid home. I had opened a case with
Magnum tech support, but the
Hi Jay William,
Just so I understand, you can put the mate into auto right after the eq is
enabled (not after eq has finished), and it will manage the generator? Is
that right?
Thanks
On Thu, Feb 12, 2015 at 10:45 AM, jay peltz j...@asis.com wrote:
Ive had clients do it for years with no
Seems I was once told that (Depending on software revision), successful Switching from Manual to Auto depended on whether or not the system itself called for a start to begin with i.e. whether the start criteria was met in either AGS or a charge mode when the genny was started in manual. My
Hey guys,
For me this was a long, long time ago….But I figured that I’d chime in on the
subject.
Yes Technically if you do as Jay says it’ll work… There was one firmware
version of the mate that this was changed (One of the early 4.?? versions) or
fixed, then it was “re-fixed” shortly
The old Trace SW series had a similar issue with Rogers-White(?) boiler
controls. It had to do with how the sine (pseudo) wave crossed the X axis.
It was too long a space and the controllers just sat there definitely on but
doing nothing. I was shown this on an oscilloscope and it was very
Hi William,
I want to talk directly to your problem at hand. I think installing the
shunt and properly calibrating it, will fix this system . In a DC coupled
system with a Sunny Island, it is imperative that you use a shunt, unless
you are using the Midnite charge controllers with the
Hello wrenches,
I have a question about how the global equalization function works with the
Auto Gen Start on the Mate-2.
Is there a way to set up a global equalization that will ensure that the
generator will shutdown after the equalization has occurred? If so, how do
you set it up?
Thanks in
We looked into this recently as well, and didn't find any good options
that didn't involve us making a custom gizmo of some type. The closest
off the shelf product I found was just an AC smoke alarm that chirps
when it loses AC. I think some of the little UPS boxes also have an
alarm when
Hi William,
Yes the Outback shunt should be fine for this application. See page 72
here for the calibration:
http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-20.pdf
As far as verifying with your clamp meter, I'd say if you can verify within
15% (remember to check polarity) then it is properly
Hi William,
One other thing. Remember to specify the 50mV shunt. 225.01
BatCurSnsTyp. I believe that means it will drop 50 mV across the shunt
with 500A current throughput. It's this proportion that determines the
value for 225.03 BatCurGain. In your case, that should be 50, but I think
it
Mac
On Feb 12, 2015, at 4:45 AM, Mac Lewis maclew...@gmail.com wrote:
Hi William,
I want to talk directly to your problem at hand. I think installing the
shunt and properly calibrating it, will fix this system . In a DC coupled
system with a Sunny Island, it is imperative that you
We are looking for an audible alarm that will not drive the pets crazy if
it stays on for hours when no one is home. At present, only a red indicator
light goes on when the grid is down.
It would need to run off 120 VAC. Does anyone have any suggestions?
Thanks,
Drake
Try your local alarm company?
Dana Orzel
Great Solar Works, Inc - NABCEP # 051112-136
E - d...@solarwork.com - Web - solarwork.com
O - 970.626.5253 C - 208.721.7003 - No FAX Line
Responsible Technologies for
Hi Mac
I don't think there is a global eq function.
Eq continues to be manual on inverters.
Gen to manual on
Initiate EQ
Gen to auto
Done
Jay
Peltz power.
On Feb 12, 2015, at 4:52 AM, Mac Lewis maclew...@gmail.com wrote:
Hello wrenches,
I have a question about how the global
Friends:
I understood the generator had to be started and stopped manually. I have a
client who was using the sequence below to stop the generator automatically.
To have the generator stop automatically has a convenience factor, but I do
like my clients to verify the cycle has
There are monitoring systems that will send text or email alerts Max
Balchowsky
Design Engineer
Golden Bridge Development
1048 Irvine Ave Suite 217
Newport Beach, Ca. 92660
760-403-6810Building a Better Future For The Next Generation
From: drake.chamber...@redwoodalliance.org