Jay,
The Exeltechs can be routinely ordered with the Low Idle option,
which I think brings the idle draw down to 10W. In some small
applications, a remote on/off switch allows the user to manually (or
otherwise with additional external control, I suppose) turn the unit
Bill,
I have always used the CU200 ("Sorry, sir, that's what it costs to
give you what you want...") when a float switch is called for (which
is nine times out of ten) so I haven't done this, but:
The only alternative to their proprietary product would be a means
to
That doesn't make sense, the inverter's charger determines the max
charge rate and the max draw from the generator.
The 8.5 kW Kohler should have no problem running the 4.4 kW Magnum.
What is the altitude?
Is it wired for 240 vac ? If the generator is running at 120 vac, then
you are only
Hi Chris,
The problem summary is a bit light on details to be too specific. What,
precisely, does a generator running "rough" mean? Overheating? Smoking? Breaker
tripping?
THE MS4448 has about 3 kW charging capability (63A @ 50 VDC). So the 8.5 kW
Kohler should be able to handle that
William,
I agree about the subpanel in the house situation. The customer is a bit
eccentric, and I have tried to bring him around. And I have explained to him
that his approach will be more expensive. He doesn’t care. In the end, there is
no safety risk. So I’ll plan for 4 branch circuits
Dear people:
I have an off-grid customer who has, in his system, a Magnum MS4448 and 16
of the Rolls S550 batteries, a Kohler generator (and Trimetric meter and
other components). He upgraded his batteries this past March, and since
he's installed his new batteries, the generator is running
Peter:
I think it is a mistake to not locate a sub-panel in the house. Running
branch circuits 45 feet to a separate building is not efficient or
practical.
Voltage drop: 1% VD is a choice, not a requirement. Code requires 3% on
feeders and 5% cumulative on AC branch circuits. I like to
Also look at the notes to the tables in Chapter 9. For conduit fill,
all wires are counted. 310.15 covers ampacity derating for more than 3
current carrying conductors in the raceway. The key is "current carrying
conductors". The neutral definitely carries current. You don't have to
count
You should find your answers in 310.15
Patrick A. Shortell
Licensed Master Electrician
Certified Solar Installer
71 Oregon Street
Long Beach N.Y. 11561
Www.thesolarstorehouse.com
> On Apr 21, 2016, at 11:56 AM, Peter Parrish
> wrote:
>
> I am working with a
I am working with a customer who is doing a complete remodel and addition to
his house: stripped to the open studs and floor joists, and rafters. Not a
wire in the house. We have designed a 14.4 kWp PV system with 16 kW of
storage for backup and load shifting. The main panel, inverters, critical
10 matches