Re: [RE-wrenches] Bootstrapping and AC Coupled Sunny Island

2024-05-08 Thread Howie Michaelson via RE-wrenches
William, We have had this same SOC calibration issue with a dual stack of XW Pro (AC couple with Solaredge) and 2 eVault Max as well (other issues as well). Schneider's solution was to use voltage (open loop), not SOC, for the XW's programming. We weren't very happy about that since trying to do

Re: [RE-wrenches] PWM Controllers in parallel

2024-05-07 Thread Howie Michaelson via RE-wrenches
Yes, output not input. Thanks for clarifying that William... Howie *Sun Catcher* *Solar Electric Systems Sales & Service802-272-0004* On Tue, May 7, 2024 at 2:55 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Andrew: > > > > I see no problem paralleling the

Re: [RE-wrenches] PWM Controllers in parallel

2024-05-07 Thread Howie Michaelson via RE-wrenches
Andrew, As long as you have proper over current and wire sizing, there shouldn't be a problem with paralleling C60s. Of course, keeping the batteries at 12v for a 2kw array makes everything else bigger and more expensive. And they won't get the MPPT advantages of even 20 year old charge

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-24 Thread Howie Michaelson via RE-wrenches
Jason, My vote would be for using a 120 to 12vDC power supply large enough to handle the remaining 12 vDC loads and skip the second battery bank. In my mind, this is simpler, cleaner, and if the power supply fails at some point, it is an easy replacement, if they still want to keep the DC loads

Re: [RE-wrenches] speaking of batteries

2024-04-23 Thread Howie Michaelson via RE-wrenches
I had the same experience as Jay as far as being marketed three idea that managed lithium batteries can jane several year age differences and still play well together, only to be told, after telling my clients the same, that most manufacturers don't recommend more than a year age differential

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread Howie Michaelson via RE-wrenches
I've had several MX and FM failures (at least 5) over the years, often with the output at zero. I don't know what actually fails, but they just stop producing. I must admit, I don't remember if in all cases I tried resetting them to factory default, but my memory is when talking to Outback

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread Howie Michaelson via RE-wrenches
John, If you are thinking of pairing the Envy with lead-acid batteries, I would strongly suggest not doing it. Even though Fortress sales advertises the Envy to be compatible with lead-acid, after trying it in my off-grid home, I would emphatically say that it is not. The programming is

Re: [RE-wrenches] midnite new inverter

2024-04-09 Thread Howie Michaelson via RE-wrenches
The last I heard, they are shipping this month or early next month. The pricing is supposed to be comparable to the other all in ones (Envy, Sol-Ark, EG4, etc.) deportment on your distributor. Howie On Tue, Apr 9, 2024, 6:55 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: >

Re: [RE-wrenches] Good tech support

2024-03-27 Thread Howie Michaelson via RE-wrenches
William, I am sure that I am not the only one on the list that appreciates your willingness to share your experience, well thought out analysis, and solutions. As always, thank you for your insights and ideas. And thanks for taking the time to highlight your positive interactions with Fortress.

[RE-wrenches] Reroofing grandfathering

2024-03-20 Thread Howie Michaelson via RE-wrenches
Hi all, I have a potential job reinstalling an 11 year old 4.4kW roof mounted net metered array, feeding a PVI 4kW inverter. The array was pulled down by a reputable company last fall, with the intention of remounting it after the asphalt shingle roof was reroofed. From a distance, it appears

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-11 Thread Howie Michaelson via RE-wrenches
William, et al, As always, a thorough explanation of your considered opinion. Thanks. Food for thought and a question to others who have more insight to the world of insurance and liability than I: My understanding of General Liability insurance, is that it is intended to cover mistakes in the

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-10 Thread Howie Michaelson via RE-wrenches
According to my agent, general liability does not cover design problems, whether we wrench it or not. That is what an Errors and Omissions policy would cover, and what a previous agent mentioned to me in passing after selling me general liability for 10 years! They could offer me an E policy for

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Howie Michaelson via RE-wrenches
With the Sol-Ark (or other DC coupled inverter/charge controller combinations such as the Envy), will the system pass through solar power if the inverter has turned off on LBCO? If not, then these alternative methods for powering the RSD signal generators won't make a difference, correct? And does

Re: [RE-wrenches] EG4 Equipment

2024-02-18 Thread Howie Michaelson via RE-wrenches
ost are mounted face up in the original > insulated L16 or Surrette industrial cell battery box's, Signature solar > has said this orientation will not void the warranty or effect operation of > the battery. > > Carl Hansen > > Hansen Electric 505 470-0770 > >

Re: [RE-wrenches] EG4 Equipment

2024-02-18 Thread Howie Michaelson via RE-wrenches
> fifteen years. Our call backs with systems over the last ten years, first > with a decline in equipment quality and then the switch to Li are costing > us too much money and causing a lot of heartburn for our clients. Rant Over > > > > On Fri, Feb 16, 2024 at 12:57 PM Howie Mich

[RE-wrenches] EG4 Equipment

2024-02-16 Thread Howie Michaelson via RE-wrenches
Hi All, I've searched the archives for info pertaining to EG4 inverters and batteries. The comments have been mostly positive. I have stayed away from EG4 until now in part, for the reason the Michael Morningstar suggested last June - that is, they seemed very oriented to the DIY market and not

[RE-wrenches] Automatic load control

2023-12-14 Thread Howie Michaelson via RE-wrenches
Hi all, I am trying to figure out best options to control loads in a Sol-Ark15k battery backup residential system. It's been quite a few years since I've set up an automatic load control, and never with a Sol-Ark. The Sol-Ark will output to the main breaker panel, so no separate "backed up"

Re: [RE-wrenches] Home grid stacked battery heating

2023-11-05 Thread Howie Michaelson via RE-wrenches
Daryl, Being in Vermont and dealing with lots of off-grid, occasional use systems, I'm definitely interested in others' experience with cold weather installations. Howie Michaelson Sun Catcher On Sun, Nov 5, 2023 at 3:03 PM Darryl Thayer via RE-wrenches < re-wrenches@lists.re-wrenches.org>

Re: [RE-wrenches] Aging Batteries

2023-10-27 Thread Howie Michaelson via RE-wrenches
Hey Will, At the risk of being overly simplistic and obvious, have you kept good specific gravity records over the years? Are they showing lowered or uneven readings? I've often been able to get some more life out of flooded batteries by raising the charge and equalize voltages, particularly if

Re: [RE-wrenches] Wattnode AC Coupling Monitoring on Insight Cloud

2023-10-26 Thread Howie Michaelson via RE-wrenches
tion match device value. > • AC coupled power flow on InsightCloud & InsightMobile will be coming > soon. > > > > *Dave Angelini Offgrid Solar > "we go where powerlines don't" ><http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ &

[RE-wrenches] Wattnode AC Coupling Monitoring on Insight Cloud

2023-10-26 Thread Howie Michaelson via RE-wrenches
Hi All, Has anyone successfully implemented the new AC coupled monitoring function using a Wattnode meter (Gateway firmware V1.18) so that it shows up on Insight Cloud? I have been able to get it to display on Insight Local, but not on the Cloud. I have spent perhaps 20-30 hours on getting this

[RE-wrenches] Pytes Batteries

2023-10-11 Thread Howie Michaelson via RE-wrenches
Does anyone have any experience with using Pytes LiFePO4 batteries? They appear to be a solid option, but have little to no direct knowledge of them. TIA, Howie Michaelson Sun Catcher ___ List sponsored by Redwood Alliance Pay optional member dues here:

[RE-wrenches] Solar World 285

2023-09-25 Thread Howie Michaelson via RE-wrenches
Hi all, I have a client with (3) 15 panel TPMs with 6 completely damaged SolarWorld 285s (black) and another 4 that would be good to replace (so he's in need of ideally 10, but he could get by with 6). Does anyone know of a source for these panels (at least ones that are the same footprint and

Re: [RE-wrenches] Fronius USA available 2023 & 2024 ?

2023-08-24 Thread Howie Michaelson via RE-wrenches
Hi Mick, Unlike others in the list, I am still mostly happily using SolarEdge for my straight grid tied roof mounted arrays. There have been significant hiccups with service, although not so much recently, and the failure rate is higher than I like, but it hasn't been dramatic for me. For systems

[RE-wrenches] Silfab

2023-08-21 Thread Howie Michaelson via RE-wrenches
Hi All, I have heard mixed comments about Silfab modules. If anyone has experience with these panels, I would appreciate any feedback available. Thanks, *Howie Michaelson**Sun Catcher* ___ List sponsored by Redwood Alliance Pay optional member dues

[RE-wrenches] SolarEdge Car Charger

2023-07-25 Thread Howie Michaelson via RE-wrenches
Hi All, I have never installed the SolarEdge car charger, and even though it seems to have some capacity advantages over a standalone charger, for some reason I've stayed away from them. I'd be interested to hear others' takes on the advantages/disadvantages of going that route. Thanks, Howie

Re: [RE-wrenches] Inverter output fluctuations

2023-07-24 Thread Howie Michaelson via RE-wrenches
offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > > On 2023-07-23 9:37 pm, Howie Michaelson via RE-wrenches wrote: > > Don, > Thanks, but this is not the issue here. The fluctuations happen anytime &g

Re: [RE-wrenches] Inverter output fluctuations

2023-07-23 Thread Howie Michaelson via RE-wrenches
Don, Thanks, but this is not the issue here. The fluctuations happen anytime the AC coupled inverter connects to the XW+'s "grid", not just when the batteries are full. The frequency only changes about 1/10 of a herz when it connects, but it doesn't matter what the voltage is of the batteries,

Re: [RE-wrenches] Inverter output fluctuations

2023-07-23 Thread Howie Michaelson via RE-wrenches
rked fine for years it would appear that the XW+ has an > issue. > > I don’t see how the SE could cause this. > > Is it still under warranty? What does Schneider say about the issue. > > Jay > > > > On Jul 22, 2023, at 10:33 PM, Howie Michaelson via RE-wrenches &l

Re: [RE-wrenches] Inverter output fluctuations

2023-07-22 Thread Howie Michaelson via RE-wrenches
rom Support many years ago and combined >>> with my findings over the years. Really rare for this kind of weirdness and >>> why it would be getting worse without visual evidence. >>> >>> Good Luck Howie! >>> >>> >>> >>> >&g

Re: [RE-wrenches] Inverter output fluctuations

2023-07-22 Thread Howie Michaelson via RE-wrenches
k Howie! > > > > > *Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > > > > On 2023-07-03 12:42 pm, How

[RE-wrenches] SolarEdge and Schneider Conext

2023-07-05 Thread Howie Michaelson via RE-wrenches
Hi all, Had anyone successfully established communications between a SolarEdge single phase inverter and a Schneider Gateway? I have a client with a battery backup system which included a dual stack of XW pros and 2 AC coupled SolarEdge inverters. He would really like to be able to use one

[RE-wrenches] Inverter output fluctuations

2023-07-03 Thread Howie Michaelson via RE-wrenches
Hi All, I upgraded an old clients' off-grid system about five years ago to a Schneider XW6848+ and 2 Blue Ion 2.0 cabinets (32kWh). When the batteries were moving toward full, if the charge rate was on the higher side via generator or solar (AC coupled w/SolarEdge 6kW and DC coupled with an FM

Re: [RE-wrenches] Need detailed help with Pytee battery

2023-06-04 Thread Howie Michaelson via RE-wrenches
Daryl, I purchased some Pytes batteries for my brother-in-law this spring, as I had some contact with them, and he wanted to try their batteries. I've had no contact with their support team at all, and the only real contact I have is the sales person I dealt with, Austin Li

Re: [RE-wrenches] Fortress LFPs & ENVY 12kw inverter

2023-06-01 Thread Howie Michaelson via RE-wrenches
Kirk, I have not tried the new Envy inverter, and at the moment am slightly reluctant to do so, mostly because I have gone all in on Sol-Ark/eVault Max setups for battery based systems and I hate having more and more different products to stay on top of. That being said, I attended an Envy

Re: [RE-wrenches] Schneider Conext SCP

2023-05-26 Thread Howie Michaelson via RE-wrenches
Thanks for the heads up, Kevin! However I seem to have missed the memo that xantrex and Schneider are separate entities? How far out of the loop am I? Howie Sun Catcher On Fri, May 26, 2023, 1:28 PM Kevin Pegg via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Not sure if it’s quite

[RE-wrenches] Solar direct water pumping

2023-05-08 Thread Howie Michaelson via RE-wrenches
Hi, I have a friend/client that is looking to keep his pond filled with water pumped from a spring downhill from the pond. He's happy to have the pond filled just when there is enough sun to pump, so no batteries are desired. I have little to no experience with water solar direct pumping, so I'm

[RE-wrenches] HomeGrid Battery Experience

2023-04-14 Thread Howie Michaelson via RE-wrenches
Hi All, I am looking to upgrade an offgrid client's battery bank from 2-volt Rolls KS17s to LiFePO4 batteries. I'm basically looking at one Fortress eVault Max cabinet vs. a HomeGrid 4 stack option. I have used the eVault Maxs before, and generally like them. The 2 options are relatively

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-03 Thread Howie Michaelson via RE-wrenches
Daniel, If it was me, I wouldn't do it. The biggest issue is that dissimilar batteries (as well as different age batteries) have different internal resistance. This will only exacerbate the problem with running multiple strings of batteries - that is they will charge and discharge at different

Re: [RE-wrenches] Intermittent

2023-03-16 Thread Howie Michaelson via RE-wrenches
Hilton, Can you give more details about the inverter? And when the DC was reading 0 volts, did you try turning off the disconnect at the array to see if isolating it from the inverter, it would show voltage? Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Howie Michaelson via RE-wrenches
Does anyone know of any bypass switch/breaker setup for anything greater than 60 amps for 2 poles, other than large DPDT switches which get pricey and hard to source especially for 200 amps? Howie On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote:

Re: [RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-09 Thread Howie Michaelson via RE-wrenches
For systems where the batteries are getting a relatively full charge every week or and cycling down below 30% at least every now and then, closed loop is certainly the safest way to go since the battery BMS is determining the SOC, not the inverter's algorithm. I've been told by a tech at Fortress

[RE-wrenches] VillaGrid Lithium Titanium Batteries

2023-01-23 Thread Howie Michaelson via RE-wrenches
Has anyone had any experience with the VillaGrid Lithium Titanium batteries? They are supposedly usable in below zero temperatures, which of course the LFP batteries are not. They also apparently have a 20 year 10,000 cycle warranty (not that I really put much stock in being able to exercise a

Re: [RE-wrenches] Sola-ark cold morning

2022-12-06 Thread Howie Michaelson via RE-wrenches
Hi All, Dana's troubles with the Sol-Ark reminded me that I wanted to write about my experience with Sol-Ark and Fortress as my troubles with that install were unfolding. I had made many calls and emails to both Sol-Ark and Fortress about the lack of charging and the odd generator behavior.

Re: [RE-wrenches] Sola-ark cold morning

2022-12-04 Thread Howie Michaelson via RE-wrenches
Dana, Sounds like potentially the same issue I've been dealing with in a new Sol-Ark 15 paired with Fortress eVault Maxs. Apparently, Sol-Ark did a recent firmware update that caused erratic closed loop communication between the inverter and batteries. I don't know if the Sol-Ark firmware update

[RE-wrenches] Fortress support call

2022-12-01 Thread Howie Michaelson via RE-wrenches
Jeremy, I would love to have an opportunity to talk with Fortress about their support process. I am just in the tail end of installing 2 Sol-Ark/Fortress off grid systems (one 15k with 2 eVaults and two 15ks with 5 eVaults). I've been very impressed with both pieces of equipment so far. However,

[RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-16 Thread Howie Michaelson via RE-wrenches
Good Evening, I have a frustrating charging issue involving 2 Fortress eVault Maxs connected to a Sol-Ark 15k. Commissioned the system last week, replacing a legacy off-grid Dual Stack SunnyIsland 5048s and 2-volt Rolls battery system. Initially, we connected one of the eVaults to the Sol-Ark,

Re: [RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Howie Michaelson via RE-wrenches
Hi Ray, I have been having a difficult time communicating with Fortress as well. I filed a support ticket several times and only got a response a couple of days later asking another question that was easily answered, but then do not receive any reply to that without filing another support ticket,

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
ar.com > 715-653-4295 > NABCEP Certified PV Installation Professional > Licensed Wisconsin Master Electrician > BSEE > > On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hi folks, >> I have a

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
e system size of batteries We have had several issues with resi and > 80kWhr limitations, I dont know if this is an issue for you or not just > want to through it out there. > Jerry > > On Fri, Oct 21, 2022 at 11:14 AM Howie Michaelson via RE-wrenches < > re-wrenches@lists.re-

[RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
Hi folks, I have a client that I'm doing a larger inverter and battery upgrade. We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units. The client is wanting manufacturer certification that the equipment is "qualified solar electric property". I don't know that I've ever run

[RE-wrenches] Sol-Ark phase imbalances

2022-09-10 Thread Howie Michaelson via RE-wrenches
Is there a white paper or a thorough explanation of the issue Sol-Ark had with large imbalances between phases. I am looking at a large residential off-grid system using potentially (2)15 kw Sol-Arks. What are the concerns specifically around unbalanced inductive loads. Also, I have not installed

[RE-wrenches] Do Sunny Islands and Fortress batteries play well together?

2022-09-01 Thread Howie Michaelson via RE-wrenches
Has anyone put Fortress batteries into a Sunny Island off grid system, either an E flex or an E vault? I have a client with older 2 volt Rolls batteries that need replacing. Currently about 55 kwhs. Or any experience with other LiFEPO4 batteries with Sunny Island off grid systems? Thanks Howie Sin

Re: [RE-wrenches] off-grid AC coupling feasibility

2022-07-30 Thread Howie Michaelson via RE-wrenches
Hey Kirk, This is something I've done a few times with success, although I've used an XW pro instead of the Radian, with OB charge controllers. Having the mix of DC and AC coupled is ideal, as the solaredge will do the bulk of the charging, but then charge controllers will do the finish taper

Re: [RE-wrenches] Dark Starting Simpliphi PHI3.5 batteries

2022-07-27 Thread Howie Michaelson via RE-wrenches
ccepted a charge and > have apparently functioned well for the customer. Job was installed by > others. > > I hope that helps. > Wallace Stahle > Future Electric Energy Co > PO Box 236 > Willits, CA 95490 > 707-459-0474 > Lic.#C10-762093 > fut...@pacific.net > > On Jul

[RE-wrenches] Dark Starting Simpliphi PHI3.5 batteries

2022-07-27 Thread Howie Michaelson via RE-wrenches
Hi All, I was called into a job of a previously off-grid system that new owners had an electrician bring the grid to, but the batteries ( a pair of Simpliphi 3.5, which I have no experience with) have been dead for an unknown period of time previously. I am trying to figure out the easiest way to

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-10 Thread Howie Michaelson via RE-wrenches
We typically do not require UL listing, but that is always good for insurance reasons... *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Sun, Jul 10, 2022 at 12:53 PM Tump via RE-wrenches <