HI All,
I’m wondering if anyone has a good source for battery buss bar stock.
Either pre made ones or stock I can use to make myself.
It would be for larger Rolls GEL 2v in this case but other battery sizes/types
as well.
thanks
jay
peltz power
Does anyone know how they actually operate?
I”m thinking they are using a variable AC voltage output from the micros to
operate at MPP matching the resistance of the heating element?
IE more PV watts, higher AC voltage, more load. Lower PV watts, lower AC
voltage, less load?
Thanks,
jay
Has anyone used the Franklin pump Fhoton solarpak, Fhoton HR Solarpak, or the
sub drive solarpak?
thanks
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address
the main inverter breakers.
thanks
jay
Peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches
Hi All,
I’m having trouble finding adjustable slide style back legs for a client who
wants to adjust his low profile array.
I can’t find them from Iron Ridge, Unirack, DPW,
Where/who can I get them from?
thanks
jay
peltz power
___
List sponsored
To follow along with the lithium questions,
I’m wondering what thoughts/information people have on prismatic vs cylindrical
lithium family batteries?
My questions are quality,cycle life, pros/cons,recycling?
Thanks
jay
___
List sponsored
I would imagine that if the breaker and enclosure had the correct AIC ratings
it should work.
But its PG, enough said.
jay
peltz power
> On Oct 3, 2017, at 10:21 AM, Jerry Caldwell <solarcow...@yahoo.com> wrote:
>
> Dear Wrenches with experience in PG territory:
> I'm i
Hi All,
I’m looking for a lithium battery for a street light lead replacement.
Size is approximately 30 - 40 amp hrs, 12v and BMS included is preferred.
Any recommendations out there?
thanks
jay
peltz power
___
List sponsored by Redwood
Can you be more specific about the fndc interface issues.
What wasn't working and the fix is new M3s firmware yet to be released?
Thx
Jay
> On Sep 20, 2017, at 4:10 AM, <d...@foxfire-energy.com>
> <d...@foxfire-energy.com> wrote:
>
> Seems earlier versions of the 3s
I”m looking for a video of how to use the SCP that I can forward to a client.
thx
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://list
for dust.
The fan doesn't blow across the power electrics, but behind it over the
transformer and FET heat sink.
Jay
Peltz power.
> On Sep 1, 2017, at 11:41 AM, William Miller <will...@millersolar.com> wrote:
>
> Friends:
>
> I am designing an off-grid system that will
Hi Dan
You can use the shunt MV reading via say fluke 87 to double check the amps that
your clamp on is reading.
Jay
> On Aug 28, 2017, at 2:47 PM, Dave Angelini Offgrid Solar
> <offgridso...@sti.net> wrote:
>
> Looks like you need a 2nd meter to test the sushi... -
Does anyone know anything about Elithion BMS systems?
Or had experience with them?
Would be used for control on tesla salvage batteries, to control upper/lower
voltage safety relays.
thanks in advance,
jay
peltz power
___
List sponsored
Hi Ray
I believe it's been replaced by the scala 2
And seems like a much better pump too.
Jay
> On Aug 11, 2017, at 1:17 PM, Ray <r...@solarray.com> wrote:
>
> We've used the Grundfos MQ series for years for exactly that purpose.
>
> Chief Technical Officer, Remo
example)
The BMS turns off the loads, but what turns off the BMS and how do you turn it
back on when it happens?
Thx
Jay
Peltz power
> On Aug 9, 2017, at 6:21 PM, Dave Angelini Offgrid Solar
> <offgridso...@sti.net> wrote:
>
> FYI, the LG Chem RESU10 consumes about 40 watts o
one of the questions no one seems to
have an answer for is energy consumption for the BMS, any BMS.
On a different note, how does the LG or PW deal with dark start? If it shuts
down due to low voltage, how do you get it started again?
Jay
> On Aug 4, 2017, at 4:26 PM, Dave Angel
what updates, reviews can you give us on those power walls?
jay
> On Aug 4, 2017, at 12:51 PM, Marco Mangelsdorf <ma...@pvthawaii.com> wrote:
>
> Tesla has been shipping the AC PWs to its dealers and we have been installing
> them.
>
> marco
>
> On Friday
.
A very easy set up compared to all the other ones I’ve seen.
No fans/computers so can be installed in a non clean environment.
I would use them again.
jay
peltz power
> On Aug 4, 2017, at 12:04 PM, Tom Lane <t...@ecs-solar.com> wrote:
>
> Does anyone know about or
it was during morning
battery fill up before sell mode and the client has a backed up loads panel
connected to it?
jay
peltz power
> On Jul 17, 2017, at 8:19 AM, Drake <drake.chamber...@redwoodalliance.org>
> wrote:
>
> Hi Dan and Dave,
>
> The system did not cras
HI All,
DPW used to have pole depth/concrete base size “ recommendations” but I can
longer find them.
Does anyone have any advice on this?
thanks
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re
same
day or next day drop ship from OB.
Hope this helps.
jay
peltz power
> On Jun 28, 2017, at 5:19 PM, frenergy <frene...@psln.com> wrote:
>
> Jay,
>
>I just had an FM80 fail in a FP1, less than a year old. Called
> 6:30 AM and waited 20-30 minutes
HI Tump,
Yep that part has been true for a while.
I find most distributers don’t have them.
But I have gotten them from “thesolarbiz.com”
Also they sell brand new ones with full warranty vs refurbished ones with 90
day warranty.
jay
peltz power
> On Jun 28, 2017, at 9:01 AM, Tump
tuesday ( yesterday) and
still nothing as to tracking/email etc.
Anyone else having these kinds of issues.
I do have to say that usually they are normal and timely.
But not this time.
jay
peltz power
___
List sponsored by Redwood Alliance
List
HI Dana,
Can you tell us about this 10 year working life. Is there a website having
such info or??
thanks
jay
peltz power
> On Jun 27, 2017, at 12:52 PM, Dana <d...@solarwork.com> wrote:
>
> I use & recommend an Energy Star Refers & do the math: A 512 Kwhr per year
make sense to remove/reroof in that area. And the roof can
handle the weight without removing the tiles.
thanks in advance,
Jay
Peltz Power.
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver
Hi dave
How about a buck transformer
Jay
Peltz power.
> On Jun 22, 2017, at 5:38 AM, Dave Tedeyan <dtede...@taitem.com> wrote:
>
> Hi All,
>
> Is anyone out there familiar with PV Powered inverters?
> If so, is it possible to adjust the voltage setpoints? The
You can fit a 2 wire start with aftermarket kits for Honda generators.
Jay
Peltz power.
> On Jun 16, 2017, at 7:36 AM, Kevin Pegg <kp...@energyalternatives.ca> wrote:
>
> You could use a 2 -> 3 wire converter such as the Atkinson GSCM module that
> will take the 2 wi
Solar World Sun Clips are what I would use.
Jay
Peltz power.
> On May 24, 2017, at 6:28 AM, AE Solar <autonomousenerg...@gmail.com> wrote:
>
> With Solarworld/SnapNRack we run wires in the rail and use clips on the long
> edge of the frame when needed. SnapNRack ha
What connectors are they, and are you using same brand when you connect to
comber/junction box?
I have seen issues with non same connectors.
jay
peltz power
> On May 8, 2017, at 7:44 AM, Howard Arey <scot.a...@solarcentex.com> wrote:
>
> Sunpreme GxB-360.. Datasheet at
if an inverter engineer might talk with the utility engineer.
And I’ve actually got one on my house. Its one of the first installs in
northern California, and not only is the a lockable disco, its locked ON.
jay
peltz power
> On May 2, 2017, at 9:50 AM, Mac Lewis <maclew...@gma
HI Dave
Every one I’ve ever seen is replaceable.
The sealed units come with a short 1/2” temp sensor, and the vented units come
with a temp sensor mounted to the transformer.
But its the same attachment, small 2 pin polarized connector.
jay
peltz power
> On Apr 30, 2017, at 1:45 PM, D
Hi Dave,
Did you replace the temp sensor?
Jay
Peltz power.
> On Apr 30, 2017, at 6:30 AM, Dave Palumbo <palumbo1...@gmail.com> wrote:
>
> Wrenches,
>
> We recently swapped in a new internal fan on a OB FX 2524T after the original
> fan stopped working on the 6 yr
Grundfos SCALA2
its the new version of the MQ pump.
jay
peltz power
> On Apr 27, 2017, at 7:39 AM, Dave Angelini Offgrid Solar
> <offgridso...@sti.net> wrote:
>
> What has been the reliability issue with Grundfos? I have not had any
> problems with them other
just haven’t been able to figure out how this aspect of the design.
Wondering if anyone out there has any info?
thanks in advance,
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change
ding the 3rd.
Utility was fine with the other two which were added one at a time. ( 1 per
year, this being year 3)
Jay
Peltz power
> On Mar 24, 2017, at 5:09 PM, Glenn Burt <glenn.b...@glbcc.com> wrote:
>
> HI Jay,
>
> Are they saying that adding the 3rd inverter wi
Hi Glenn
I had it correct in the subject, but got it wrong below, here is the correct
number
2014NEC, 705-100 (a)
> On Mar 21, 2017, at 8:09 PM, Glenn Burt <glenn.b...@glbcc.com> wrote:
>
> Hi Jay,
> I must not understand.
> I don't see a 705.11 in the 2014 NEC.
>
, using SMA 3kw for phases 1 and 2)
Now they are being stopped on adding the 3rd.
Anyone ever run into this before?
Any answers?
thanks
jay
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email
nothing
from Tesla directly, but some from other folks by google search.
Does anyone on the list here know anything solid?
For example.
what inverter is being used?
how do they stack?
battery chemistry?
actual size ( depending on which info it changes)
are they actually shipping?
Thanks
jay
there are some issues with battery life
The 375/376 FC look solid
The Seaward clamp meter
And there are a few others.
All thoughts are welcome,
thanks
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Hi Lou,
I”ve had a few customers doing this exact operation with no issues.
It has been very consistent.
jay
peltz power
> On Feb 12, 2017, at 8:12 PM, Lou Russo <l...@spreesolarsystems.com> wrote:
>
> Aloha Wrenches,
>
> I have steered clear of the Mate 3 for as lon
. Max watts around 300.
Yours might be different however.
jay
peltz power
> On Feb 9, 2017, at 10:29 AM, solar1onl...@charter.net wrote:
>
> Lou,
> You are getting great advice from the list. Yesterday's sinewave inverter is
> not today's sinewave inverter. The washers ar
reports etc on
this.
I should have been more specific and clear on my original email.
jay
> On Feb 5, 2017, at 3:23 AM, Dana <d...@solarwork.com> wrote:
>
> It is at the polar opposite end of the scale from Organic. I have worn quite
> a bit in fire training and the smell
HI All,
I am wondering if anyone has any information or knows of studies etc that
discuss any toxic nature of FR cotton clothing.?
Thanks in advance,
jay
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
, so I just want to make sure I’ve got the right tips.
thanks
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cg
Hi John,
If you are looking for something similar to the 9325 but better then.
Check out Sunpumps.
Much better pump because of the superior case, cheaper, more reliable and
easier to repair
Also Sunpumps make some really nice LCB controls.
jay
peltz power
> On Jan 15, 2017, at 2:04
Its not just the weight but the size, i.e. so small!
jay
peltz power
> On Jan 12, 2017, at 5:01 PM, Dana <d...@solarwork.com> wrote:
>
> Bottom side bolt up. But they were 1995 Solarex remember the weight of
fixes you guys come
up with or if the OEM’s change things or if the rack folks offer some added
parts to address this issue.
Jay
Peltz Power
> On Jan 11, 2017, at 10:26 AM, Ray Walters <r...@solarray.com> wrote:
>
> Bill;
>
> Great point, I have had the exact same t
I can't find the link to Jeff randles new rack company?
Can someone help me out
Thx
Jay
Peltz power.
Sent from my iPhone
> On Jan 10, 2017, at 8:31 PM, Ray Walters <r...@solarray.com> wrote:
>
> Hi William;
>
> Your link had a glitch, I think this
, by the time its told to shut down its not
running all that hard, which shouldn’t be a problem.
But again, I’ll defer to the genny experts here.
Happy new year
jay
> On Dec 30, 2016, at 1:13 AM, Hugh Piggott <h...@scoraigwind.co.uk> wrote:
>
> hi Lou,
>
> I don’t wish to co
Hi Lou,
I might suggest a relay that switches with the signal for ags start/stop.
It'll disconnect the AC from the genset with a lot shorter delay.
Jay
Peltz power.
Sent from my iPhone
> On Dec 29, 2016, at 11:27 AM, Lou Russo <l...@spreesolarsystems.com> wrote:
>
> W
Hi john
Thanks for that tip
Interesting quandary.
New revs seem to work better, more stable for RE.
But yea they screwed up on the internal memory clear.
Can you clear that via RE?
Jay
Peltz power.
> On Dec 19, 2016, at 7:57 AM, Chris Schaefer <ch...@solarandwindfx.com> wrote:
, I'd suspect a weak battery in the 48v.
Jay
Peltz power.
> On Dec 18, 2016, at 5:41 PM, John Blittersdorf <john.blittersd...@gmail.com>
> wrote:
>
> I have had several instances of the Mate 3 locking up where I cannot program
> anything and the main screen is abbrevia
Hi Roy and others,
A very worrisome situation.
I’m wondering if anyone who’s had this problem has not been using OpticsRE.
IE is the problem somehow related to RE?
Thanks
jay
peltz power
> On Dec 14, 2016, at 2:19 PM, Roy Rakobitsch <winds...@gmail.com> wrote:
>
> Hello Wi
HI Matt,
How does UL deal with fixing this? I seem to remember that on AC modules ( not
sure what you call a SE/integrated module) that you had to replace the
inverter/module as a unit.
Hopefully thats no longer the case.
jay
peltz power
> On Dec 14, 2016, at 7:51 AM, Matt Partymiller
&
Hi all
I've got a buddy who has the following problem.
Every parameter has been triple checked.
He has been in contact with highers up at tech support.
AC grid voltage is 122/123v
Anybody have any suggestions or similar problems or answers.
Thanks
Jay
>
> Post the qu
Hi William and others who have had this kind of issue,
Is it yet confirmed if all of these systems are connected via OPticsRE ?
Thx
Jay
Sent from my iPhone
> On Nov 17, 2016, at 11:44 AM, Brian Teitelbaum <bteitelb...@aeesolar.com>
> wrote:
>
> William,
>
> This
Call OB for a new one.
I’ve had a few go back for this reason.
Once the start that, they don’t get better.
Jay
Peltz power
> On Nov 4, 2016, at 4:24 AM, Solar <dahlso...@gmail.com> wrote:
>
> All,
>
> We have a MATE3 on campus that resets each time you press a button to lea
regulate watts to stay
at that voltage or shut off like a normal GT inverter?
Or could there be another reason/s?
Thanks
Jay
Peltz power.
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver
Hi Mac
No don't recommend replacing internal fans
But I have installed external 120v muffin fans on the ends.
Seal up the vents around the ends so it pulls air through.
Hook the fans to the genny input.
Quick and works well
Jay
> On Nov 3, 2016, at 7:09 AM, Mac Lewis <maclew...@gma
You could look at the rotary vane pump ( dankoff for example). They come in
24v, quiet, require extremely good filtration, much smaller than the MQ but
you’ll need a small pressure tank.
jay
peltz power
> On Oct 28, 2016, at 1:13 PM, Ray Walters <r...@solarray.com> wrote:
>
Hi All,
I”ve got some spare fans that are OB inverter replacements.
I’m looking for the correct connector.
I think its the Molex Mini-fit Jr. 4.20mm.
Can anyone confirm this?
thanks
jay
___
List sponsored by Redwood Alliance
List Address: RE
Hi Bill
Indeed. Thanks for correcting that.
It's the h4 version that uses the MC3 crimper dies. I can't seem to keep that
one straight.
The h4 is a heck of a pin though. Real weight to it.
Jay
Peltz power.
> On Oct 15, 2016, at 7:17 PM, frenergy <frene...@psln.com> wrote:
Hi Bob
Both UL and the NEC say you have to follow OEM instructions.
MC says no to any connection except to another MC.
Amphenol H4 uses same crimper as MC4.
Contact Bryan at PV CABLES
707-923-3000
Jay
Peltz power.
> On Oct 14, 2016, at 5:26 PM, RE Ellison <reelli...@gmail.com&
while we are on the subject of recombining caps has anyone used the following.
http://www.sbsbattery.com/PDFs/Battery-Recombination-Plug.pdf
<http://www.sbsbattery.com/PDFs/Battery-Recombination-Plug.pdf>
Jay
peltz power
> On Oct 13, 2016, at 9:38 AM, penobscotso...@midmaine.com wrote
trays?
No one else does that?
Thanks
jay
peltz power
> On Oct 12, 2016, at 5:28 PM, Kevin Pegg <kp...@energyalternatives.ca> wrote:
>
> I am a big fan of the Schneider XW system, and the XW Power Distribution
> Panel. Full disclosure - I helped design it. The original desig
HI William,
The SI does indeed have a BOS. Made by midnite solar which worked with SMA to
produce it.
Jay
Peltz Power
> On Oct 12, 2016, at 10:36 AM, William Miller <will...@millersolar.com> wrote:
>
> Kevin:
>
> I am curious, what brand would you prefer over the R
They are not compatible nor UL listed.
I can dig up the official MC paper if you need
Jay
Peltz power.
Sent from my iPhone
> On Oct 11, 2016, at 11:35 AM, Abe Powell <a...@solforce.com> wrote:
>
> Hello Wrenches,
>
> It has come to our attention that enphase is shi
and removal of
wire without removal of the breaker or the plate/breakers. With thimbles of
course. And I can’t find them but I know they make them, shields that fit
between each breaker so the lay in lugs are insulated.
jay
peltz power
> On Oct 10, 2016, at 4:40 PM, William Mil
and if there is such a tip, where to get one?
thanks
jay
Peltz Power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenche
PV wire co marked USE-2 is direct burial.
jay
peltz power
> On Sep 27, 2016, at 2:50 PM, Corey Shalanski <co...@joule-energy.com> wrote:
>
> Umm, is PV Wire rated for direct burial? I have seen several manufacturer
> spec sheets that suggest this is the case, but I haven
I would suggest talking to the folks at PV cables.
They know about crimpers!
jay
peltz power
> On Sep 21, 2016, at 7:19 PM, Kevin Pegg <kp...@energyalternatives.ca> wrote:
>
> I purchased a Helios H4TC0001 crimper, as recommended by Kyocera and have to
> report it as ju
Is this a remote display or the built in one?
Jay
Peltz power
Sent from my iPhone
> On Sep 15, 2016, at 4:11 PM, RM You <solarea...@solareagle.com> wrote:
>
> Has anyone seen this kind of readout on a Trace 4024 inverter. Unit is
> functioning but access to the menu is u
Hi mike,
question.
Are you saying the corrosion has been the source of the failures?
Is this wire connection or actually inside the micro?
Jay
Peltz power
> On Sep 13, 2016, at 6:44 PM, Mike Nelson <mdelectricso...@gmail.com> wrote:
>
> I've had so many Enphase fai
Hi Drake,
You might look at the fluke connect series. Pretty interesting what they can
do.
Jay
Peltz Power
Sent from my iPhone
> On Sep 13, 2016, at 2:24 PM, Drake <drake.chamber...@redwoodalliance.org>
> wrote:
>
> Hello Wrenches,
>
> My old Fluke 337 i
Hi Kris,
yes I think you need to help us with greater information about what the reasons
are, and the specific requirements.
1. instantaneous or monthly?
2. does it have to be listed and approved?
3. is this utility requirement or customers fancy?
4. anything else?
thanks
jay
peltz power
I haven’t use the 2v, but have used many 6v L-16s
Been in 2 years at most.
so far so good.
They are about 10lbs heavier than either a Trojan or Rolls L-16/flooded.
jay
> On Sep 1, 2016, at 7:08 PM, Gary Willett <g...@icarussolarservices.com> wrote:
>
> Larry:
>
> Wh
HI Ray,
I second your opinion.
jay
peltz power
> On Sep 1, 2016, at 4:43 PM, Ray Walters <r...@solarray.com> wrote:
>
> Hi Gary;
>
> I think it would be a waste of time to load test a sealed battery that is 9
> years old. Even at only 20% discharge, that batt
HI All,
I can’t find usage for a dishwasher.
And as I don’t have one I can’t test it.
Any ideas for a newer high efficiency one?
Both kw and kwh? Worst case I guess?
thanks
jay
___
List sponsored by Redwood Alliance
List Address: RE-wrenches
and I’ll email them to you.
And it makes a big difference.
One pump was up around 80% efficient, the others at 40s% for same height.
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver
Hi Bill and Benn,
Those micros are rated nema 6, which is submersible rated.
I”m curious which element/s they are referring to?
jay
peltz power
> On Aug 28, 2016, at 6:35 PM, frenergy <frene...@psln.com> wrote:
>
> Benn,
>
> Just curious, if they are o
HI Howie,
Midnight still makes the Epanel for FXR
They did discontinued the narrow versions, but still make the wider ones.
Jay
> On Aug 27, 2016, at 2:30 PM, Howie Michaelson <ho...@suncatchervt.com> wrote:
>
> H Jeremy,
>
> It has been years since I used Outback's
Hi all
Does anybody know anything about these batteries?
I had some ask.
The data on the website is really weak.
http://www.siliconebatteries.ca/dw.html
Thanks in advance
Jay
Peltz power___
List sponsored by Redwood Alliance
List Address: RE
Hi all
I'm not looking for the SQFLEX but the SQ.
Thanks
Jay.
Sent from my iPhone
> On Aug 26, 2016, at 8:29 AM, Allan Sindelar <al...@sindelarsolar.com> wrote:
>
>
> Allan Sindelar
> al...@sindelarsolar.com
> NABCEP Certified PV Installation Professional
>
> Hi all,
I can't find Grundfos SQ power curves, any ideas of where or anybody have them
Thanks
Jay
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://l
disconnected it, all normal. I tested voc of all modules after they
were replaced,(190 watt 72 cell) customer wanted more watts, and all were
normal and the same. I didn't spent the time to do a ISC.
Replacement is my thought.
Jay
Peltz power.
> On Aug 25, 2016, at 7:04 AM, Allan Sinde
Ha that's a good one.
But still good to know if they were murdered or had defects.
While I also have had early failures on every brand, that's earlier than most
I've seen
Usually it's outside of warranty, of course.
Jay
> On Aug 24, 2016, at 7:56 AM, Ray Walters <r...@solarray.com&
Hi drake,
The early failure of other batteries brings up questions
Charge set points?
Frequent overcharge, possible but damn unusual
Frequent undercharge?
Hi heat location?
Offgrid?
Ongrid?
Battery type?
Jay
Peltz power.
> On Aug 24, 2016, at 7:36 AM, Drake <drake.c
Hi all
I was contacted by someone offsite about a 5 stack outback radian, grid
connected that is having all sorts of problems.
He's been in long contact with OB engineering but still no answers.
If anyone has experience with such a critter, please let me know.
Thanks
Jay
Peltz power
Thimbles are easy to install and make fine strand wire OK for use in standard
connections.
Jay
Peltz power.
> On Aug 8, 2016, at 5:39 PM, Glenn Burt <glenn.b...@glbcc.com> wrote:
>
> Be aware that depending upon the vintage of the Engage cable, up to recently
> t
So what is the micro of choice these days?
If enphase is no longer home?
Jay
Peltz power.
> On Aug 5, 2016, at 6:59 AM, gary easton <g...@arp-solar.com> wrote:
>
> just a worthless ticket but no action and certainly no timely reimbursement
> if at all. I would
ost sense.
Any recommendations?
Thanks
Jay
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
Spend $600 and get a front loader.
I just checked mine
150 watt max watt load
.11 kWh
VS
3000+ watt surge.
I've seen old top loaders bury a old stout trace U2512.
It will destroy the samlex
Jay
Peltz power.
Sent from my iPhone
> On Jul 28, 2016, at 9:21 AM, frenergy <
There is also the Ace clamp.
I haven’t used it or heard any reports about it.
Looks better in many regards than the S-5.
jay
peltz power
> On Jul 28, 2016, at 6:06 AM, Will White <w...@solarenergy.org> wrote:
>
> The big problem I've had with the minis is when you attach
can't seem to locate them.
Thanks in advance
Jay
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches
I've got a customer with an older pair of XW 4048 inverters and cc's.
He would like to use the new web conext box, and probably the battery meter
with them.
Anybody know if this is possible?
Thanks
Jay
Peltz power.
___
List sponsored by Redwood
I’m curious about it happening at the same time each day. I think that is a
big clue.
Could it be some other interference from some other electrical part? Motors
etc?
And what about if its heat related? IE the roof/modules heating up causing the
issue?
Curious.
jay
peltz power
> On
Oh boy.
Which BP models.
I mean those things have had lots of trouble.
jay
peltz power
> On Jul 22, 2016, at 8:23 AM, August Goers <aug...@luminalt.com> wrote:
>
> Glen,
>
> It’s interesting you mention that you’re having AFCI issues with new TL
> inverters and old
not on “smart”meter.
Can anyone help me with what this persons options are?
thanks
jay
peltz power
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches
Hi All,
Any trick methods to keep a SQflex running on AC power at a given flow rate
that is less than full power?
I’ve got a well that is just on 1 gpm, around 150’ lift.
the sqflex 3-2 will do it, but at 3gpm with full watts, an amazing 265 watts.
thx
jay
peltz power
as well as to what others think?
jay
peltz power
> On Jun 21, 2016, at 4:59 PM, Jason Andrade <ja...@westcoastsustainables.com>
> wrote:
>
> Hi Wrenches,
>
> I am looking at the new rates for PG’s time of use and was wondering what
> others in California are usi