[RE-wrenches] Large transformer losses

2024-05-06 Thread Steven Lawrence via RE-wrenches
> > > Hi Jay, A 75kVA low voltage transformer will have roughly 0.3% iron core losses and have an efficiency loss of roughly 2%. It depends on when the transformer was made and what efficiency standard it was adhered to. the manufacturer should be able to provide you with the testing results

Re: [RE-wrenches] Monitoring large PV systems

2021-04-12 Thread Steven Lawrence
William, I've used a lot of services from Fat Spaniel, SolarMagic, Draker, Noveda, AlsoEnergy, Locus, Qantum, Powerfactors, and Green Power Monitoring. Which one is the best is highly dependent upon your preferences and what services you require. I prefer AlsoEnergy for numerous reasons, one

Re: [RE-wrenches] NEC 690.8(A) - Bifacial Modules

2021-03-17 Thread Steven Lawrence
that. It is, however, less than the traditional BSTC nameplate x 1.25 method. Regards Steven Lawrence, PE ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://list

[RE-wrenches] Bad Diodes in QCells?

2020-11-09 Thread Steven Lawrence
Hi Adam, I have a 3.3MW site using Hanwha 400s where IV curve tracing and other voltage checks found roughly 1% of the modules are experiencing some type of voltage issues. We all suspect bad diodes. We just got the site up and running and we will be doing an aerial thermal imaging flyover to

[RE-wrenches] Rooftop Conduit

2020-07-27 Thread Steven Lawrence
I design a lot of grid tied projects, but I still do a rooftop about once or twice a year. All of them going back 7 years or so always used covered/vented cable tray. This includes homeruns, DC feeders, and all AC wiring. There still is some metallic conduit used (usually EMT) - a small jumper

Re: [RE-wrenches] connector mismatch

2019-09-04 Thread Steven Lawrence
We've averaged maybe 1 or 2 on 6MW projects over a year with this hard requirement versus 100+ we had on a 1MW rooftop project that mixed multiple manufacturers. Steven Lawrence ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.

Re: [RE-wrenches] wireless relays for load shedding?

2018-05-23 Thread Steven Lawrence
Phoenix contact makes a bunch of wireless radios and relays that can communicate discrete signals as well as standard communications. I've used it for a minimum export relay with SCE and telemetry for SCE. It's simple to install and use. If you're going wireless, make sure you have line of

Re: [RE-wrenches] AFCI Faults, SMA Inverters, Solectria RSB's, & RF Signals

2018-01-25 Thread Steven Lawrence
Hi James, Is the solectria combiner actually combining strings so you have one input into the SMA inverter? If so, did SMA approve arc fault detection at that high current? From what I understand, arc fault detection doesn't work on strings greater than 20A. In the solectria box, I'm assuming

Re: [RE-wrenches] Tariff

2017-11-09 Thread Steven Lawrence
) of modules to store to ride out the tariff. I imagine utility scale projects will be hit the hardest. When you have a $0.10/W tariff being added to a $1.00/W project, that's a 10% increase, which means a lot of projects won't go forward. -Steven Lawrence

Re: [RE-wrenches] Solar World Wind Damage

2017-01-11 Thread Steven Lawrence
Hi Ray, Have you checked the torquing on all the other bolts? My company's had a few projects where some modules blew off - it's always been due to over-torquing of the bolts. Steven Lawrence ___ List sponsored by Redwood Alliance List Address: RE

[RE-wrenches] NRTL certification question

2016-08-29 Thread Steven Lawrence
Just to expand on this, the NRTL has to test to the specific UL standard. However, if you look at the definition of "listed" in the NEC, it states "equipment, materials, or services included in a list published by an organization that is acceptable to the AHJ...). I have heard of some

Re: [RE-wrenches] Canadian Solar / MC4 connectors in a marine environment

2016-06-07 Thread Steven Lawrence
Kirk, Double check those connectors very closely. On our other projects, Canadian solar doesn't use MC4 connectors - they use PV2 which we found does not mate well with MC4. Steven Lawrence ___ List sponsored by Redwood Alliance List Address: RE

Re: [RE-wrenches] traveling with digital meters

2015-11-10 Thread Steven Lawrence
I've had no issues traveling with a DMM and its associated probes. However, I did travel one time with the Seaward analyzer and that set off the bomb detection machine. Not a very fun 30 minutes. ___ List sponsored by Redwood Alliance List Address:

Re: [RE-wrenches] Serviceable equipment on a roof

2015-08-14 Thread Steven Lawrence
Hi Dan, I don't know which state you're in, but the state of NJ put out a notice stating that solar panels do not require servicing. This came from the top electrical inspector back in 2010. The link can be found at

[RE-wrenches] Monitor Display

2014-10-02 Thread Steven Lawrence
Hi Bill, For a Solaron, I've used a plastic stair tread, some velcro and some super glue to cover the display. Only a few bucks from Home Depot. It's worked out pretty well provided it's not very windy. Steven Lawrence Date: Thu, 2 Oct 2014 07:45:01 -0700 From: frenergy frene...@psln.com

[RE-wrenches] PID

2013-12-27 Thread Steven Lawrence
. The SMA CP-US inverters are transformless and can use a solidly grounded conductor. -Steven Lawrence Hello Wrenches, Attached is an article from Home Power that came in my email. It says module degradation is increased by PID (Potential Induced Degradation) by the use of transformerless

[RE-wrenches] Breaker Testing

2013-11-08 Thread Steven Lawrence
Hi Max, Try http://epsii.com/users/awp.php?ln=121219 I just used them for some relay testing and they were outstanding. Thanks Steven Lawrence ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email

[RE-wrenches] Burned Inverter Technician

2013-10-17 Thread Steven Lawrence
) with the full mask on, especially when it's hot outside, but it is something everyone should be doing when troubleshooting anything energized. Stay safe. Steven Lawrence ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re

[RE-wrenches] double insulated wire

2013-06-28 Thread Steven Lawrence
Hi Marco, It goes back to 690.35(D). Transformerless inverters are usually ungrounded PV systems, so the wire must bein raceways, or it must be PV wire. There are a few exceptions, the SMA CP-US inverters can have a grounded conductor, but you must have a floating AC neutral. And the Solarons

[RE-wrenches] IV Curve Tracer

2013-06-13 Thread Steven Lawrence
Esteemed wrenches, Does anyone know of an IV Curve Tracer that's rated for 1000VDC and 30A? I can find some 1000V tracers but they're only at 10A. Thanks ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Old Modules for GIT system?

2013-06-04 Thread Steven Lawrence
Dana, Maybe wire 3 in series to a single Enphase? It'll depend on what the voltages are. Date: Tue, 4 Jun 2013 14:01:42 -0600 From: Dana d...@solarwork.com To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Old Modules for GIT system? Message-ID:

[RE-wrenches] PV-direct electric water heating

2013-05-14 Thread Steven Lawrence
Luke, Most tankless hot water heaters can't accept pre-heated water. Some of them can, but even still these have a minimum heat input into the water. You may run into a situation where you have 105F water into the tankless and the thing won't fire up due to safety reasons (can't put out 130F or

Re: [RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread Steven Lawrence
Hi Robert, Get a mega Ohm meter, isolate the home runs and perform a test. You should get 550 MOhms. If not, there's something likely wrong with that string that's causing the intermittent ground fault. Or, have someone stand on the ground with a hose pointing it at the roof and try to find it

Re: [RE-wrenches] 15 kV redundant relay

2012-11-21 Thread Steven Lawrence
Hi Conrad, Without any specs on what the redundant relay is trying to accomplish, I'm guessing you'll need the SEL 547. It's a microprocessor relay that takes voltage and current and will trip a circuit breaker provided you have a set of PTs and CTs. Steven Lawrence Date: Tue, 20 Nov 2012

[RE-wrenches] MC4 Y Connectors

2012-03-08 Thread Steven Lawrence
Allen, I use to use them on the old Sanyo modules. As long as the combined short circuit rating is less than the series fuse rating, you'll be ok. They're really only good for modules with high voltage/low current. -Steven From: Allen Frishman amfr...@aeonsolar.com To: RE-wrenches

Re: [RE-wrenches] big combiner box

2011-06-07 Thread Steven Lawrence
Hi Marco, Check out Bentek, Shoals, and SolarBOS. If you're doing thin film, I suggest looking into the in-line fusing from Shoals. -Steven Date: Mon, 6 Jun 2011 13:04:35 -1000 From: Marco Mangelsdorf ma...@pvthawaii.com To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org Subject:

[RE-wrenches] Whats with Kyocera

2010-05-18 Thread Steven Lawrence
It's the same thing here. They aren't taking any large orders from us. Steven Lawrence NABCEP Certified Solar PV Installer(tm) -- Date: Mon, 17 May 2010 18:22:27 -0700 From: i2p i...@aol.com To: List for complaining about anything RE. re-bitch...@lists.re

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
service panel that can be fed from the backup load panel. Steven Lawrence __ Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT) From: Nick Soleil nicksoleilso...@yahoo.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
loads aren't over 60A, and what's left in the main service panel wouldn't be over 60A. But yeah, it always depends on the AHJ. Here in NJ I try to stay away from panel upgrades whenever possible. They can run from $2k-$3k, and that's not an adder I want to put on a client. Steven Lawrence