...@glbcc.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org,
Date:
07/25/2015 12:46 PM
Subject:
Re: [RE-wrenches] DC conductor line loss numbers
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org
You would want to confirm hot temp PV circuit values with chosen Vdrop to
ensure the irrelevant
From: jarmo.venalai...@schneider-electric.com
Date: 07/27/2015 5:34 AM (GMT-10:00)
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] DC conductor line loss numbers
Hi:
When deciding on voltage drops and otherwise
working out the design of a solar system, one
I have worked out the area under the daily bell curve. A 2% loss at max current
equals 1% loss average. Maybe this logic could allow some flexibility.
William
On Jul 25, 2015, at 5:52 AM, Jerry Shafer jerrysgarag...@gmail.com wrote:
Wrenches
I have 3 engineering firms and one in-house
It should be noted that the NEC recommendations for feeder circuits are to
do with acceptable voltages at the load, i.e., you do not want your 208V
equipment running on 200V. PV circuits are not feeder circuits, voltage
drop is irrelevant. Power loss may be relevant, but only in terms of
economic
Mason cometenergysyst...@gmail.com
Sent: 7/25/2015 15:20
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] DC conductor line loss numbers
It should be noted that the NEC recommendations for feeder circuits are to
do with acceptable voltages at the load, i.e., you do
Wrenches
I have 3 engineering firms and one in-house engineer that only use 1%
because in the NEC it is stated as a suggestion and not a requirement but
they take this as a must not exceed instead,
I cant change CC as it will be remotely monitored via the Outback
connection, the Engineers refuse
Wrenches
Some time back there was discussion on the conductor size and efficiency
rating requirement for long DC runs.
What I am looking at is this, 400 feet of MCM 400 to keep the line loss at
or below 1% per NEC code for an off grid application, cost vs return is not
acceptable. 2/0 is less than
Maybe 600vdc charge controller?
Roy Rakobitsch
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
Certified Advanced Tower Climbing, Safety Rescue
Wind/PV Design Engineer
Windsine LLC
631-514-4166
www.windsine.org
On Jul 22, 2015 1:52 PM, Jerry Shafer
Of *Jerry Shafer
*Sent:* Wednesday, July 22, 2015 10:38 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] DC conductor line loss numbers
Wrenches
Some time back there was discussion on the conductor size and efficiency
rating requirement for long DC runs.
What I am looking at is this, 400 feet of MCM
Jerry,
A long distance wire run is practical now days using a high voltage controller.
Have a look at Schneider and Morningstar 600Vdc controllers. Not sure what you
mean by nothing can be changed but wire size” but you will have to rewire the
strings into series and protect the wire run.
@lists.re-wrenches.org,
Date:
07/22/2015 11:52 AM
Subject:
[RE-wrenches] DC conductor line loss numbers
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org
Wrenches
Some time back there was discussion on the conductor size and efficiency
rating requirement for long DC runs.
What I am
11 matches
Mail list logo