I have found this Electricenter accessory part # ECSBPK01. to be very useful
with locally available load centers. labelled for Siemens and Murray. Fits
well on Eaton tho not listed for that brand.
Available locally for $32 or so lately.
Does the same thing the Generac sub panel does for the
You can also build them with the interlock kits for (almost) whatever load
center you like. https://interlockkit.com/shop/
Some of these are UL listed, some are not.
The disadvantage of this route is that they are typically made for a high
ampacity main circuit breaker, probably overkill for
Wrenches
It might be easier to use the wire cabinet for the radian, but hey thats
just me
On Thu, Mar 2, 2023, 9:47 AM Kristopher Schmid via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi All,
>
> I have a stand alone system that was upgraded from an FX inverter to a
> Radian
Here's a 100 amp version of the Reliance box. Cheap, lots of room, easy
to wire up, but NEMA 1.
https://www.electricgeneratorsdirect.com/Reliance-Controls-TCA1006D/p1102.html
On 3/2/2023 6:10 PM, Howie Michaelson via RE-wrenches wrote:
Does anyone know of any bypass switch/breaker setup for
Thanks for the help and suggestions!
Shine On!
Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE
On Thu, Mar 2, 2023, 7:40 PM John Blittersdorf via
Howie,
I use the QO612 small breaker box with two double pole breakers and the
QO2DTI toggle.
John Blittersdorf
On Thu, Mar 2, 2023 at 8:11 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Does anyone know of any bypass switch/breaker setup for anything
Does anyone know of any bypass switch/breaker setup for anything greater
than 60 amps for 2 poles, other than large DPDT switches which get pricey
and hard to source especially for 200 amps?
Howie
On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
I probably still have one of the old QO boxes on the shelf, but I never
liked them. Single pole, very tight, and you had to double lug or use a
weird split bolt arrangement with exposed copper out past the breaker.
I started using these 60A T switches from Northern:
Kris, It was SqD QO403, and it was a 3-pole load center/disconnect, not
4-pole. You may recall that the dual-inverter Trace Power Panels of long
ago used two of these, each one serving as an inverter bypass switch to
one 120V AC leg.
On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches
,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting
Get Outlook for iOS<https://aka.ms/o0ukef>
From: RE-wrenches on behalf of
Kristopher Schmid via RE-wrenches
Sent: Thursday, March 2, 2023 12:46:43 PM
To: RE-wrenches
Cc: Kristopher Schmid
Subject: [RE-wrenches] In
Hi All,
I have a stand alone system that was upgraded from an FX inverter to a
Radian WITHOUT the companion load center. I would like to add an inverter
bypass circuit to operate the house on generator power. There used to be a
4 slot breaker panel (SqD?) with the rocker switch preventing both
Hello wrenches,
I am interested in input about an inverter bypass assembly for a dual Sunny
Island 5048-US system with a 30 kW generator. SMA does not offer anything
for this, but I think its an important part of the design. Any input would
be appreciated.
Thanks
--
Mac Lewis
*
Yo solo
Mac,
This is the unformatted, cut-n-pasted content from a pdf file, from
which you may extract the info you need. This was offered by Greg
Smith of SMA to those who attended the Sunny Island seminar at the
recent NABCEP Continuing Education Conference. The Nottagutter is