Drake, I believe that is for a single phase 2 wire output only. I am assuming one hot and one neutral for the inverter output in this case. I would think most *grid tied* inverters fall under 705.95B, where the neutral is only a voltage sense and can be sized as small as the equipment ground.

Re: [RE-wrenches] neutral sizing for sense

2022-01-25 Thread drake . chamberlin
"the maximum load connected between the neutral and any one ungrounded [10] conductor plus the inverter [9] output rating shall not exceed the ampacity [5] of the neutral conductor [6]." So the neutral conductor is supposed to be sized for the connected load plus the entire maximum output of

Re: [RE-wrenches] neutral sizing for sense

2022-01-24 Thread Kirk Herander
705.95 Ampacity of Neutral Conductor National Electrical Code 2017 of New York State > 7 Special Conditions > 705 Interconnected Electric Power Production Sources

Re: [RE-wrenches] neutral sizing for sense

2022-01-24 Thread Foxfire Energy
I’d start with the manufacturers recommendations Sent from my iPhone > On Jan 24, 2022, at 11:52 AM, jay wrote: > > HI All, > > Where do I find in the code how to size a sense only neutral wire for GT > inverter. > > thanks > > jay > > peltz power > > >

[RE-wrenches] neutral sizing for sense

2022-01-24 Thread jay
HI All, Where do I find in the code how to size a sense only neutral wire for GT inverter. thanks jay peltz power ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address:

Re: [RE-wrenches] Neutral sizing

2018-09-24 Thread Bradley Bassett
I have a long triplex wire run with a smaller neutral to my place from the utility entrance, and I do end up with a large load on one leg often. When another large load is on the other leg to balance the legs, it reduces the voltage drop dramatically. The voltage on the one leg rises when I

Re: [RE-wrenches] Neutral sizing

2018-09-23 Thread jay
HI Drake and all, Thanks for this. As I understand this better now, maybe. Neutral sizing changes between supply side and load side of main service panel. Others have chimed in with an argument that can be made that if the neutral wire is sized for a 200 amp service then it should be OK even

Re: [RE-wrenches] Neutral sizing

2018-09-23 Thread glenn.b...@glbcc.com
...@glbcc.com;RE-wrenches;Cc: Subject:Re: [RE-wrenches] Neutral sizing Hi Jay, Is this for an inverted output circuit? If so then I think the NEC reference you’re looking for is 705.95(B). That says you can size the neutral to the same size as the EGC if the neutral is used only for instrumentation

Re: [RE-wrenches] Neutral sizing

2018-09-22 Thread Garrison
RE-wrenches On Behalf Of > Dana > Sent: Saturday, September 22, 2018 10:32 AM > To: 'RE-wrenches' > Subject: Re: [RE-wrenches] Neutral sizing > > What about 4/04/02/0 aluminum, service feed? Or is that utility excepted? > > -

Re: [RE-wrenches] Neutral sizing

2018-09-22 Thread Glenn Burt
al Message- From: RE-wrenches On Behalf Of Dana Sent: Saturday, September 22, 2018 10:32 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Neutral sizing What about 4/04/02/0 aluminum, service feed? Or is that utilit

Re: [RE-wrenches] Neutral sizing

2018-09-22 Thread Dana
sdorf Sent: Friday, September 21, 2018 10:39 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Neutral sizing At the risk of sounding like a grandpa Wrench...I've never had or seen a neutral conductor be smaller than current carrying. marco -Original Message- From: RE-wrenches [mailto:r

Re: [RE-wrenches] Neutral sizing

2018-09-22 Thread Marco Mangelsdorf
-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Neutral sizing Hi all, I’m wondering if there is code reference to size of neutral vs power conductors. County is requiring neutral same size as mains 240vac. As it’s 500 mcm due to VD (200 amp service) it’s a non trivial expense. I know

Re: [RE-wrenches] Neutral sizing

2018-09-21 Thread Ray
220.61, 310.15(B)(7)(4), 215.2(2), 230.42(C) Can't say exactly how to apply all that to your case, but that should be a start. Ray Walters Remote Solar 303 505-8760 On 9/21/18 7:47 PM, Jay wrote: Hi all, I’m wondering if there is code reference to size of neutral vs power conductors.

[RE-wrenches] Neutral sizing

2018-09-21 Thread Jay
Hi all, I’m wondering if there is code reference to size of neutral vs power conductors. County is requiring neutral same size as mains 240vac. As it’s 500 mcm due to VD (200 amp service) it’s a non trivial expense. I know that where I live, the utility brings in a smaller neutral than