[RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread Hilton Dier III
I have an off-grid client who is having trouble with his aging Xantrex SW4024 inverter and is considering an upgrade. I need some advice. One of his problems with his present system is that he can't run his 3 HP 240VAC table saw on the 4024. He'd be content to run his generator for any long

Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread jay peltz
HI Hilton, Before you go anywhere you need to know what the draw on this motor is. I've seen 3 hp motors not be able to start on a 15kw genny. Why? Just horrible motors thats all. jay peltz power On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote: I have an off-grid client who is having

Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread bob ellison
-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz Sent: Saturday, October 13, 2012 5:28 PM To: RE-wrenches Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP HI Hilton, Before you go anywhere you need to know what the draw on this motor

Re: [RE-wrenches] Off-Grid Generac EcoGen 6 kW

2012-05-07 Thread Jeff Yago
I have not been a fan of any Generac brand generators, especially their low-cost, highly marketed residential stand-by generators. Although things may have changed, these were very hard to use with a typical inverter's 2-wire remote start relay, most warranties were voided if used in off-grid

Re: [RE-wrenches] Off-Grid Generac EcoGen 6 kW

2012-05-07 Thread Jason Szumlanski
I can't answer your questions directly, but for the record, if you need help with the two wire start issue, call Generac and ask for Bob Cramer. He will send you a conversion kit and instructions for residential propane standby generators. If you want his email address, contact me off list.

Re: [RE-wrenches] Off-Grid Generac EcoGen 6 kW

2012-05-07 Thread Allan Sindelar
Jeff, I have had one at my off grid home for a little over a year now. I just went out to check: 85.3 hours on this unit, so no chance to wear anything out yet. The unit has performed very well. I had two issues come up, both quite minor: at first the cold

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-06 Thread William Miller
Colleagues: I might caution against using the HBX mode for two reasons: 1. The batteries will wear out in proportion to the number of cycles. If you don't need to cycle then I recommend you don't. 2. HBX can be a very inefficient mode. If you HBX cycle frequently then you are

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-06 Thread Phil Undercuffler
Benn, If the client prefers the independence and thought of remaining primarily offgrid, has sufficient PV and battery for his loads, but wants to use the grid as his generator then HBX can really be a great solution. I'll take exception to William's comments -- with the FX you can set grid

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-05 Thread benn kilburn
Subject: Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads IMHO, the batteries are the real skeleton in the closet here. Sooner or later they're gonna poop. at 2400 Ah you're likely running a multi string set up, so it's likely someone's number is already on the board. Even if you set

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-05 Thread toddcory
i am not sure what the advantage is of running in HBX mode? why not simply grid-tie this where any surplus power (over local use) gets sold to the grid? also the vfx's can be sent into ob for upgrading to gvfxs. no need to buy new inverters. todd On Saturday, May 5, 2012

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-05 Thread da...@wind-sun.com
- Reply message - From: toddc...@finestplanet.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads Date: Sat, May 5, 2012 1:28 pm i am not sure what the advantage is of running in HBX mode? why not simply grid-tie

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-05 Thread da...@wind-sun.com
From: dan@foxfire-energy.comTo: re-wrenc...@lists.re-wrenches.orgDate: Fri, 4 May 2012 18:23:33 -0700Subject: Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads IMHO, the batteries are the real skeleton in the closet here. Sooner or later they're gonna poop. at 2400 Ah you're

[RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-04 Thread benn kilburn
Wrenches,I have an off-grid client who is going to be connecting to the grid. Since the system (~9 kW of PV and ~2400 Ah battery) is already well suited for the loads, I am wondering about the necessity of an essential loads panelboard. I'm not sure if I see the need since the battery is

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-04 Thread dan
Original Message Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads From: benn kilburn b...@daystarsolar.ca Date: Fri, May 04, 2012 5:08 pm To: Wrenches re-wrenches@lists.re-wrenches.org Wrenches,I have an off-grid client who is going to be connecting to the grid. Since

Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads

2012-05-04 Thread da...@wind-sun.com
program them for HBX mode. David Lauzon Northern Arizona Wind and Sun Phone-928-526-8017 / 800-383-0195 Fax-928-527-0729 Website-http://www.solar-electric.com - Reply message - From: d...@foxfire-energy.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Off-Grid

Re: [RE-wrenches] Off-grid ground mount

2012-03-26 Thread Larry Crutcher, Starlight Solar Power Systems
Ray, This is exactly how we installed many 10 and 12' fiberglass C-band satellite antennas back in the 80's in Tulsa. None ever came down in tornado alley. I recommend this method of pole mounting in Mexico due to frequent theft. Larry Crutcher Starlight Solar Power Systems (928) 342-9103

Re: [RE-wrenches] Off-grid ground mount

2012-03-24 Thread Drake
-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Friday, March 23, 2012 2:21 AM To: RE-wrenches Subject: [RE-wrenches] Off-grid ground mount Friends: I am curious about what the rest

Re: [RE-wrenches] Off-grid ground mount: Can it be done cheaper

2012-03-24 Thread Jason Szumlanski
Oh, to have 85 mph winds. Code changes just brought us up to 180 mph design wind speeds in Southwest Florida. Yay. Jason Szumlanski Fafco Solar On Mar 24, 2012, at 5:05 PM, Kent Osterberg k...@coveoregon.com wrote: William, There are auger mounted systems that don't require any concrete. For

[RE-wrenches] Off-grid ground mount

2012-03-23 Thread William Miller
Friends: I am curious about what the rest of you are using for off-grid ground mount racks. We need a tilt angle of 45 degrees. Thanks in advance. William Miller Miller Solar Voice :805-438-5600 email: will...@millersolar.com http://millersolar.com License No. C-10-773985

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread Jason Szumlanski
Been using Unirac U-LA for years with HD Solarmount rails. Not the cheapest, but I'm very happy with the product support and quality. 10-25 degrees is my range of experience, though. Jason Szumlanski Fafco Solar On Mar 23, 2012, at 3:21 AM, William Miller will...@millersolar.com wrote:

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread Solarguy
:21 AM To: RE-wrenches Subject: [RE-wrenches] Off-grid ground mount Friends: I am curious about what the rest of you are using for off-grid ground mount racks. We need a tilt angle of 45 degrees. Thanks in advance. William Miller Miller Solar Voice :805-438-5600 email

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread Larry Crutcher, Starlight Solar Power Systems
We use Unirac ULA. Good quality. We have winter use only systems in Mexico so we set the arrays high for best production in January. You should have no problem with 45°. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Mar 23, 2012, at 12:21 AM, William Miller wrote: Friends:

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread penobscotsolar
We use Direct Power and Water racking for ground mounts. They're engineered for 90/120 mph winds, depending on where you're installing. The two tier mounting is especially nice. Friends: I am curious about what the rest of you are using for off-grid ground mount racks. We need a tilt

[RE-wrenches] Off-grid, on grid ground mount

2012-03-23 Thread frenergy
I've been using Direct Power and Water racks for ground mounting for some 14 years. Jeff offers a lot of support for custom needs/situations, easy to assemble, can be adjustable (or fixed for a lower price). Never had any issues, except very infrequently they'll forget to send some fasteners.

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread Allan Sindelar
-wrenches Subject: [RE-wrenches] Off-grid ground mount Friends: I am curious about what the rest of you are using for off-grid ground mount racks. We need a tilt angle of 45 degrees. Thanks in advance

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread William Miller
What do you do for a foundation? thanks, William At 04:05 AM 3/23/2012, penobscotso...@midmaine.com wrote: We use Direct Power and Water racking for ground mounts. They're engineered for 90/120 mph winds, depending on where you're installing. The two tier mounting is especially nice.

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread William Miller
Larry: Are you sure they go up to 45 degrees? I looked at the web site this morning and it indicated a maximum of 30 degrees. Thanks, William At 08:36 AM 3/23/2012, you wrote: We use Unirac ULA. Good quality. We have winter use only systems in Mexico so we set the arrays high for best

Re: [RE-wrenches] Off-grid ground mount

2012-03-23 Thread Larry Crutcher, Starlight Solar Power Systems
I am sure they have their reason but I have used them at that angle. The jobs in Mexico don't ever get inspected but I've not had any failure. BTW, I also build my own structure using KEE products (like this: http://www.simplifiedbuilding.com/store/components/kee-klamp.html) and galvanized

Re: [RE-wrenches] Off Grid Alarm Communicator

2011-11-26 Thread Jeff Yago
Carl, We designed and built a custom solar power system for an alarm company about 4 years ago. They were installing the system on an un-occupied warehouse that had no electricity. The two things we had to address was make sure we had correct voltage/current battery charging arrangement as we

Re: [RE-wrenches] Off-grid system monitoring

2011-02-15 Thread Dan Fink
William; Bogart engineering, hands down. Trimetric for most customers, and Pentametric for high-information customers, if you need to measure multiple shunts, or if you want to log and monitor on a computer or via internet. Great customer service, owner and engineer Ralph will get you going

Re: [RE-wrenches] Off-grid system monitoring

2011-02-15 Thread jay peltz
HI William, I second the 2025. It has much better history than the 2020 but much more usable than the Pentametric. jay peltz power On Feb 15, 2011, at 8:35 AM, Maverick Brown [Maverick Solar] wrote: A good replacement is the Bogart TM-2025-A. It is a refreshed version of the TM-2020. It

[RE-wrenches] Off-grid system monitoring

2011-02-14 Thread William Miller
Wrenches: An off grid client has a system monitor that has not been very a satisfactory. I belive it is a Trace Meter 500. It is not calibrateable and the results are not reliable. Is there a newer monitor that will show battery voltage and charging and discharging amps and amp/hours that

[RE-wrenches] Off grid Trace 4024 off grid w/ Sunny Boy

2011-01-31 Thread lars Ortegren
Hi Wrenches: A few years ago our company set up an A/C coupled micro grid using a quad stack of Outback 3648, with 2 SB6000 inverters tied to the output side of the Outbacks. It worked marvelously, using the grid tied inverters to push the current through the output terminals until the

[RE-wrenches] Off grid generator

2011-01-25 Thread Randy Brooks
Wrenches, Thanks for the responses, on and off list, to my earlier question about what off grid generator you recommend. The Cummins Onan 20 kW GGMA (LP, 1,800 rpm, liquid cooled) we're considering also has an optional coolant heater (120vAC, 1,500 watt) that the manual recommends be used any

Re: [RE-wrenches] Off grid generator

2011-01-25 Thread Dana
not ever believe anything, but seriously trust through action. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Randy Brooks Sent: Tuesday, January 25, 2011 10:04 AM To: Wrenches RE Subject: [RE-wrenches] Off grid generator Wrenches

Re: [RE-wrenches] off grid generators

2010-06-24 Thread Kurt Albershardt
I'd suggest finding out who the industrial engine dealers are in a large nearby city (Richmond, VA?) then see who is assembling gensets from which engines. I've had good relationships with a couple of small builders over the years, one Isuzu and one Kubota based (though mostly Diesels, after

Re: [RE-wrenches] off grid generators

2010-06-23 Thread Jeff Oldham
I use a lot of MQ Power, especially the WhiperWatt diesel models for o-t-g. MQ has known they are in o-t-g service and I use their Prime Power rated units, they have never mentioned any issue with my applications on denied a warranty claim. Maybe I'm slipping by but so far I'm well taken care

Re: [RE-wrenches] off grid generators

2010-06-22 Thread Jeff Yago
I know this topic has come up before, but am hoping there are some new products out there. Although we are doing more grid tie these days, we still get more than our share of off grid systems due to the fact that e have been doing this for son long that there was a time when all systems were

Re: [RE-wrenches] Off-Grid Diesel Generators

2010-04-13 Thread benn kilburn
attachments. Date: Mon, 12 Apr 2010 17:38:47 -0400 From: penobscotso...@midmaine.com To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Off-Grid Diesel Generators Ben, Here in Maine we don't install diesel gennies in off grid applications. Typically, diesel gennies require

Re: [RE-wrenches] Off-Grid Diesel Generators

2010-04-13 Thread bob
is good. Just another opinion, Bob From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of benn kilburn Sent: Monday, April 12, 2010 3:36 PM To: Wrenches Subject: [RE-wrenches] Off-Grid Diesel Generators Wrenches, Can anyone

[RE-wrenches] Off-Grid Diesel Generators

2010-04-12 Thread benn kilburn
Wrenches, Can anyone in the off-grid market, in colder climate regions (i'm at latitude 53) suggest or recommend a reliable diesel generator for off-gird home back-up. It will likely be coupled with two Outback VFX3648's and a 1500 to 2500 amp/hr battery. Any experiences with pairing Lister

Re: [RE-wrenches] Off-Grid Diesel Generators

2010-04-12 Thread Steve Higgins
Ave Ne Arlington Wa 98223 360-618-4313 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of benn kilburn Sent: Monday, April 12, 2010 12:36 PM To: Wrenches Subject: [RE-wrenches] Off-Grid Diesel Generators Wrenches, Can

Re: [RE-wrenches] Off-Grid Diesel Generators

2010-04-12 Thread penobscotsolar
Ben, Here in Maine we don't install diesel gennies in off grid applications. Typically, diesel gennies require a block heater which can use as much as 1000 watts. Unless this is a tremendously large off grid system it won't be a good idea to go that way. Why not just use a propane gennie.

Re: [RE-wrenches] Off-Grid Diesel Generators

2010-04-12 Thread benn kilburn
of the communication, including attachments. Date: Mon, 12 Apr 2010 13:02:05 -0700 From: shigg...@outbackpower.com To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Off-Grid Diesel Generators Benn, The only thing I have heard about NL generators was about 5 years ago

Re: [RE-wrenches] Off-Grid Diesel Generators

2010-04-12 Thread Darryl Thayer
wrote: From: benn kilburn b...@daystarsolar.ca Subject: Re: [RE-wrenches] Off-Grid Diesel Generators To: Wrenches re-wrenches@lists.re-wrenches.org Date: Monday, April 12, 2010, 9:22 PM Steve,Thanks for the feedback.  A Northern Lights dealer i spoke with is selling Outback equipment as well

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-10 Thread Darryl Thayer
. --- On Thu, 12/3/09, wind...@wind-sun.com wind...@wind-sun.com wrote: From: wind...@wind-sun.com wind...@wind-sun.com Subject: Re: [RE-wrenches] Off-Grid Sizing Case To: RE-wrenches re-wrenches@lists.re-wrenches.org Date: Thursday, December 3, 2009, 12:18 PM Off-Grid Sizing Case

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-10 Thread robert ellison
: Thursday, December 03, 2009 10:56 AM Subject: Re: [RE-wrenches] Off-Grid Sizing Case So being able to achieve C10 charging from the PV is not so important? Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-10 Thread Roy Butler
efficency of a Honda inverter gen is hard to beat. --- On Thu, 12/3/09, wind...@wind-sun.com wind...@wind-sun.com wrote: From: wind...@wind-sun.com wind...@wind-sun.com Subject: Re: [RE-wrenches] Off-Grid Sizing Case To: "RE-wrenches" re-wrenches@lists.re-wrenches

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-09 Thread CVSOLAR
Mark, I always recommend more PV. In this case, doubling the array to 8 panels is probably the least expensive addition. The added 4 panels will max out the C40. We always get many phone calls in November and December when solar is low but the calls disappear as soon as the days get

[RE-wrenches] Off-Grid Sizing Case

2009-12-03 Thread Mark Frye
Folks, I have a customer with a 3 year old system in northern CA: 8 - Deka 370AH, 6V, 2x4 banks - 740Ah @ 24V 2 - DR2424 120/240V series 4 - EC-120-GL 1 - C40 CC 1 - 5000W, old portable gas gen The problem is increased gen runtime probally due to chronic undercharging. Based on estimated

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-03 Thread wind...@wind-sun.com
, December 03, 2009 10:22 AM Subject: [RE-wrenches] Off-Grid Sizing Case Folks, I have a customer with a 3 year old system in northern CA: 8 - Deka 370AH, 6V, 2x4 banks - 740Ah @ 24V 2 - DR2424 120/240V series 4 - EC-120-GL 1 - C40 CC 1 - 5000W, old portable gas gen

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-03 Thread wind...@wind-sun.com
/ .. - Original Message - From: Mark Frye To: 'RE-wrenches' Sent: Thursday, December 03, 2009 10:56 AM Subject: Re: [RE-wrenches] Off-Grid Sizing Case So being able to achieve C10 charging from the PV is not so important? Mark Frye Berkeley Solar Electric

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-03 Thread Allan Sindelar
505 424-1112 www.PositiveEnergySolar.com http://www.positiveenergysolar.com/ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye Sent: Thursday, December 03, 2009 10:23 AM To: 'RE-wrenches' Subject: [RE-wrenches] Off-Grid

Re: [RE-wrenches] Off-Grid Sizing Case

2009-12-03 Thread jay peltz
Hi Mark, I'd install as much PV as I could afford, a MPPT controller and a battery capacity meter to keep an eye on things. And if they are still looking to throw money around then a new generator as Allan suggested. jay peltz power On Dec 3, 2009, at 9:22 AM, Mark Frye wrote: Folks, I

[RE-wrenches] Off grid outdoor lighting

2008-10-06 Thread North Texas Renewable Energy Inc
Wrenches a general contractor working on upgrades to a VA hospital has come up with the big idea to use a series of lighted directional signs and landscape lights along the driveway and walkways leading to the building complex. To come up with a design to power these standalone natural stone

[RE-wrenches] off-grid pump controls

2008-09-08 Thread Mendocino Solar Service
Hello Wrenchers, I'm sure some of you guys and gals are familiar with this one: We have a customer with an off-grid studio building that gets little use, but has a nice 1.5 kw Unisolar array going unused most days. The owner wants to use the excess capacity to pump water from a well into

[RE-wrenches] off grid in Maine coastal?

2008-09-08 Thread Geoff Greenfield
contact me if you install off grid in Maine.. For a brighter energy future, Geoff Greenfield President Third Sun Solar Wind Power Ltd. 340 West State Street, Unit 25 Athens, OH 45701 740.597.3111 Fax 740.597.1548 www.Third-Sun.com Clean Energy - Expertly Installed

Re: [RE-wrenches] off-grid pump controls

2008-09-08 Thread mick abraham
Bruce @ Medocino Solar asked about the best control strategy for making a pump run only after the battery completes its absorption phase. Mick says: The Morningstar Relay Driver might help. It seems very versatile but also a bit tricky to figure out. One must really think like a controls

Re: [RE-wrenches] off-grid pump controls

2008-09-08 Thread Richard L Ratico
Bruce, You may have already seen this on the Outback Users Forum, in the thread titled, How do I use every last electron? http://www.outbackpower.com/forum/viewtopic.php?f=29t=2865 Most of the discussion applies to the FX60 FX80, but I think there were some tips for the MX60 as well. Dick