I have an off-grid client who is having trouble with his aging Xantrex
SW4024 inverter and is considering an upgrade. I need some advice.
One of his problems with his present system is that he can't run his 3
HP 240VAC table saw on the 4024. He'd be content to run his generator
for any long
HI Hilton,
Before you go anywhere you need to know what the draw on this motor is.
I've seen 3 hp motors not be able to start on a 15kw genny.
Why? Just horrible motors thats all.
jay
peltz power
On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:
I have an off-grid client who is having
-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Saturday, October 13, 2012 5:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
HI Hilton,
Before you go anywhere you need to know what the draw on this motor
I have not been a fan of any Generac brand generators, especially their
low-cost, highly marketed residential stand-by generators. Although things
may have changed, these were very hard to use with a typical inverter's
2-wire remote start relay, most warranties were voided if used in off-grid
I can't answer your questions directly, but for the record, if you need
help with the two wire start issue, call Generac and ask for Bob Cramer. He
will send you a conversion kit and instructions for residential propane
standby generators. If you want his email address, contact me off list.
Jeff,
I have had one at my off grid home for a little over a year now. I
just went out to check: 85.3 hours on this unit, so no chance to
wear anything out yet.
The unit has performed very well. I had two issues come up, both
quite minor: at first the cold
Colleagues:
I might caution against using the HBX mode for two reasons:
1. The batteries will wear out in proportion to the number of cycles. If
you don't need to cycle then I recommend you don't.
2. HBX can be a very inefficient mode. If you HBX cycle frequently then
you are
Benn,
If the client prefers the independence and thought of remaining
primarily offgrid, has sufficient PV and battery for his loads, but
wants to use the grid as his generator then HBX can really be a
great solution. I'll take exception to William's comments -- with the
FX you can set grid
Subject: Re: [RE-wrenches] Off-Grid to Grid-Connected -essential loads
IMHO, the batteries are the real skeleton in the closet here. Sooner or later
they're gonna poop. at 2400 Ah you're likely running a multi string set up, so
it's likely someone's number is already on the board. Even if you set
i am not sure what the advantage is of running in HBX mode? why not simply
grid-tie this where any surplus power (over local use) gets sold to the grid?
also the vfx's can be sent into ob for upgrading to gvfxs. no need to buy new
inverters.
todd
On Saturday, May 5, 2012
- Reply message -
From: toddc...@finestplanet.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads
Date: Sat, May 5, 2012 1:28 pm
i am not sure what the advantage is of running in HBX mode? why not simply
grid-tie
From: dan@foxfire-energy.comTo: re-wrenc...@lists.re-wrenches.orgDate: Fri, 4
May 2012 18:23:33 -0700Subject: Re: [RE-wrenches] Off-Grid to Grid-Connected
-essential loads
IMHO, the batteries are the real skeleton in the closet here. Sooner or later
they're gonna poop. at 2400 Ah you're
Wrenches,I have an off-grid client who is going to be connecting to the grid.
Since the system (~9 kW of PV and ~2400 Ah battery) is already well suited for
the loads, I am wondering about the necessity of an essential loads panelboard.
I'm not sure if I see the need since the battery is
Original Message
Subject: [RE-wrenches] Off-Grid to Grid-Connected -essential loads
From: benn kilburn b...@daystarsolar.ca
Date: Fri, May 04, 2012 5:08 pm
To: Wrenches re-wrenches@lists.re-wrenches.org
Wrenches,I have an off-grid client who is going to be connecting to the grid. Since
program them for
HBX mode.
David Lauzon
Northern Arizona Wind and Sun Phone-928-526-8017 / 800-383-0195
Fax-928-527-0729
Website-http://www.solar-electric.com
- Reply message -
From: d...@foxfire-energy.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Off-Grid
Ray,
This is exactly how we installed many 10 and 12' fiberglass C-band satellite
antennas back in the 80's in Tulsa. None ever came down in tornado alley. I
recommend this method of pole mounting in Mexico due to frequent theft.
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Friday, March 23, 2012 2:21 AM
To: RE-wrenches
Subject: [RE-wrenches] Off-grid ground mount
Friends:
I am curious about what the rest
Oh, to have 85 mph winds. Code changes just brought us up to 180 mph
design wind speeds in Southwest Florida. Yay.
Jason Szumlanski
Fafco Solar
On Mar 24, 2012, at 5:05 PM, Kent Osterberg k...@coveoregon.com wrote:
William,
There are auger mounted systems that don't require any concrete. For
Friends:
I am curious about what the rest of you are using for off-grid ground mount
racks. We need a tilt angle of 45 degrees.
Thanks in advance.
William Miller
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
Been using Unirac U-LA for years with HD Solarmount rails. Not the
cheapest, but I'm very happy with the product support and quality.
10-25 degrees is my range of experience, though.
Jason Szumlanski
Fafco Solar
On Mar 23, 2012, at 3:21 AM, William Miller will...@millersolar.com wrote:
:21 AM
To: RE-wrenches
Subject: [RE-wrenches] Off-grid ground mount
Friends:
I am curious about what the rest of you are using for off-grid ground mount
racks. We need a tilt angle of 45 degrees.
Thanks in advance.
William Miller
Miller Solar
Voice :805-438-5600
email
We use Unirac ULA. Good quality. We have winter use only systems in Mexico so
we set the arrays high for best production in January. You should have no
problem with 45°.
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Mar 23, 2012, at 12:21 AM, William Miller wrote:
Friends:
We use Direct Power and Water racking for ground mounts. They're
engineered for 90/120 mph winds, depending on where you're installing.
The two tier mounting is especially nice.
Friends:
I am curious about what the rest of you are using for off-grid ground
mount
racks. We need a tilt
I've been using Direct Power and Water racks for ground mounting for some 14
years. Jeff offers a lot of support for custom needs/situations, easy to
assemble, can be adjustable (or fixed for a lower price). Never had any
issues, except very infrequently they'll forget to send some fasteners.
-wrenches
Subject: [RE-wrenches] Off-grid ground mount
Friends:
I am curious about what the rest of you
are using for off-grid ground mount
racks. We need a tilt angle of 45
degrees.
Thanks in advance
What do you do for a foundation?
thanks,
William
At 04:05 AM 3/23/2012, penobscotso...@midmaine.com wrote:
We use Direct Power and Water racking for ground mounts. They're
engineered for 90/120 mph winds, depending on where you're installing.
The two tier mounting is especially nice.
Larry:
Are you sure they go up to 45 degrees? I looked at the web site this
morning and it indicated a maximum of 30 degrees.
Thanks,
William
At 08:36 AM 3/23/2012, you wrote:
We use Unirac ULA. Good quality. We have winter use only systems in Mexico
so we set the arrays high for best
I am sure they have their reason but I have used them at that angle. The jobs
in Mexico don't ever get inspected but I've not had any failure.
BTW, I also build my own structure using KEE products (like this:
http://www.simplifiedbuilding.com/store/components/kee-klamp.html) and
galvanized
Carl,
We designed and built a custom solar power system for an alarm company about
4 years ago. They were installing the system on an un-occupied warehouse
that had no electricity. The two things we had to address was make sure we
had correct voltage/current battery charging arrangement as we
William;
Bogart engineering, hands down. Trimetric for most customers, and
Pentametric for high-information customers, if you need to measure
multiple shunts, or if you want to log and monitor on a computer or via
internet. Great customer service, owner and engineer Ralph will get you
going
HI William,
I second the 2025.
It has much better history than the 2020 but much more usable than the
Pentametric.
jay
peltz power
On Feb 15, 2011, at 8:35 AM, Maverick Brown [Maverick Solar] wrote:
A good replacement is the Bogart TM-2025-A. It is a refreshed version of the
TM-2020. It
Wrenches:
An off grid client has a system monitor that has not been very a
satisfactory. I belive it is a Trace Meter 500. It is not calibrateable
and the results are not reliable. Is there a newer monitor that will show
battery voltage and charging and discharging amps and amp/hours that
Hi Wrenches:
A few years ago our company set up an A/C coupled micro grid using a
quad stack of Outback 3648, with 2 SB6000 inverters tied to the output side
of the Outbacks. It worked marvelously, using the grid tied inverters to
push the current through the output terminals until the
Wrenches,
Thanks for the responses, on and off list, to my earlier question about what
off grid generator you recommend.
The Cummins Onan 20 kW GGMA (LP, 1,800 rpm, liquid cooled) we're considering
also has an optional coolant heater (120vAC, 1,500 watt) that the manual
recommends be used any
not ever believe anything, but seriously trust through
action.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Randy Brooks
Sent: Tuesday, January 25, 2011 10:04 AM
To: Wrenches RE
Subject: [RE-wrenches] Off grid generator
Wrenches
I'd suggest finding out who the industrial engine dealers are in a large nearby
city (Richmond, VA?) then see who is assembling gensets from which engines.
I've had good relationships with a couple of small builders over the years, one
Isuzu and one Kubota based (though mostly Diesels, after
I use a lot of MQ Power, especially the WhiperWatt diesel models for o-t-g. MQ
has known they are in o-t-g service and I use their Prime Power rated units,
they have never mentioned any issue with my applications on denied a warranty
claim. Maybe I'm slipping by but so far I'm well taken care
I know this topic has come up before, but am hoping there are some new products out there.
Although we are doing more grid tie these days, we still get more than our share of off grid systems due to the fact that e have been doing this for son long that there was a time when all systems were
attachments.
Date: Mon, 12 Apr 2010 17:38:47 -0400
From: penobscotso...@midmaine.com
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Off-Grid Diesel Generators
Ben,
Here in Maine we don't install diesel gennies in off grid applications.
Typically, diesel gennies require
is good.
Just another opinion,
Bob
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Monday, April 12, 2010 3:36 PM
To: Wrenches
Subject: [RE-wrenches] Off-Grid Diesel Generators
Wrenches,
Can anyone
Wrenches,
Can anyone in the off-grid market, in colder climate regions (i'm at latitude
53) suggest or recommend a reliable diesel generator for off-gird home back-up.
It will likely be coupled with two Outback VFX3648's and a 1500 to 2500 amp/hr
battery. Any experiences with pairing Lister
Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of benn
kilburn
Sent: Monday, April 12, 2010 12:36 PM
To: Wrenches
Subject: [RE-wrenches] Off-Grid Diesel Generators
Wrenches,
Can
Ben,
Here in Maine we don't install diesel gennies in off grid applications.
Typically, diesel gennies require a block heater which can use as much
as 1000 watts. Unless this is a tremendously large off grid system it
won't be a good idea to go that way.
Why not just use a propane gennie.
of the communication, including attachments.
Date: Mon, 12 Apr 2010 13:02:05 -0700
From: shigg...@outbackpower.com
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Off-Grid Diesel Generators
Benn,
The only thing I have heard about NL generators was about 5
years ago
wrote:
From: benn kilburn b...@daystarsolar.ca
Subject: Re: [RE-wrenches] Off-Grid Diesel Generators
To: Wrenches re-wrenches@lists.re-wrenches.org
Date: Monday, April 12, 2010, 9:22 PM
Steve,Thanks for the feedback. A Northern Lights dealer i spoke with is
selling Outback equipment as well
.
--- On Thu, 12/3/09, wind...@wind-sun.com wind...@wind-sun.com wrote:
From: wind...@wind-sun.com wind...@wind-sun.com
Subject: Re: [RE-wrenches] Off-Grid Sizing Case
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Thursday, December 3, 2009, 12:18 PM
Off-Grid Sizing Case
: Thursday,
December 03, 2009 10:56
AM
Subject: Re:
[RE-wrenches] Off-Grid
Sizing Case
So being able to achieve C10
charging from the PV is not so
important?
Mark
Frye
Berkeley Solar
Electric
Systems
303 Redbud
Way
Nevada
City, CA 95959
(530) 401
efficency
of a Honda inverter gen is hard to beat.
--- On Thu, 12/3/09, wind...@wind-sun.com wind...@wind-sun.com
wrote:
From: wind...@wind-sun.com
wind...@wind-sun.com
Subject: Re: [RE-wrenches] Off-Grid Sizing Case
To: "RE-wrenches" re-wrenches@lists.re-wrenches
Mark,
I always recommend more PV. In this case, doubling the array to 8
panels is probably the least expensive addition. The added 4 panels will max
out the C40. We always get many phone calls in November and December when
solar is low but the calls disappear as soon as the days get
Folks,
I have a customer with a 3 year old system in northern CA:
8 - Deka 370AH, 6V, 2x4 banks - 740Ah @ 24V
2 - DR2424 120/240V series
4 - EC-120-GL
1 - C40 CC
1 - 5000W, old portable gas gen
The problem is increased gen runtime probally due to chronic undercharging.
Based on estimated
, December 03, 2009 10:22 AM
Subject: [RE-wrenches] Off-Grid Sizing Case
Folks,
I have a customer with a 3 year old system in northern CA:
8 - Deka 370AH, 6V, 2x4 banks - 740Ah @ 24V
2 - DR2424 120/240V series
4 - EC-120-GL
1 - C40 CC
1 - 5000W, old portable gas gen
/
..
- Original Message -
From: Mark Frye
To: 'RE-wrenches'
Sent: Thursday, December 03, 2009 10:56 AM
Subject: Re: [RE-wrenches] Off-Grid Sizing Case
So being able to achieve C10 charging from the PV is not so important?
Mark Frye
Berkeley Solar Electric
505 424-1112
www.PositiveEnergySolar.com http://www.positiveenergysolar.com/
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Thursday, December 03, 2009 10:23 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] Off-Grid
Hi Mark,
I'd install as much PV as I could afford, a MPPT controller and a battery
capacity meter to keep an eye on things.
And if they are still looking to throw money around then a new generator as
Allan suggested.
jay
peltz power
On Dec 3, 2009, at 9:22 AM, Mark Frye wrote:
Folks,
I
Wrenches
a general contractor working on upgrades to a VA hospital has come up with the
big idea to use a series of lighted directional signs and landscape lights
along the driveway and walkways leading to the building complex.
To come up with a design to power these standalone natural stone
Hello Wrenchers,
I'm sure some of you guys and gals are familiar with this one: We
have a customer with an off-grid studio building that gets little
use, but has a nice 1.5 kw Unisolar array going unused most days. The
owner wants to use the excess capacity to pump water from a well into
contact me if you install off grid in Maine..
For a brighter energy future,
Geoff Greenfield
President
Third Sun Solar Wind Power Ltd.
340 West State Street, Unit 25
Athens, OH 45701
740.597.3111 Fax 740.597.1548
www.Third-Sun.com
Clean Energy - Expertly Installed
Bruce @ Medocino Solar asked about the best control strategy for making a
pump run only after the battery completes its absorption phase.
Mick says: The Morningstar Relay Driver might help. It seems very versatile but
also a bit tricky to figure out. One must really think like a controls
Bruce,
You may have already seen this on the Outback Users Forum, in the thread titled,
How do I use every last electron?
http://www.outbackpower.com/forum/viewtopic.php?f=29t=2865
Most of the discussion applies to the FX60 FX80, but I think there were some
tips for the MX60 as well.
Dick
301 - 359 of 359 matches