Re: [RE-wrenches] Outback Radian transfer time

2022-02-04 Thread jay
HI Eric, Check that the transfer delay is as short as it can go, about 6 cycles You might raise the lower voltage limit from 108 Check to make sure all the voltage readings on each inverter are as close as possible. A real weakness of the OB platform is that you have to calibrate each item:

Re: [RE-wrenches] Outback Radian transfer time

2022-02-04 Thread Howie Michaelson
Not sure about the radians (I've rarely used them) but with the VFX series, that symptom can sometimes be avoided by programming a cool down period so that the inverters drop the generator while it is still running at full speed. Alternatively, by narrowing the generator voltage window at the

[RE-wrenches] Outback Radian transfer time

2022-02-04 Thread Eric Smiley
I have an off grid system with three GS8048A inverters. Every time it switches from generator charging to inverting - at the end of absorption - the lights flicker and a propane boiler in the house goes into fault. I'm using Advanced AGS on the Mate3S. The loads don't exceed about 6 kW right now.