HI Eric,
Check that the transfer delay is as short as it can go, about 6 cycles
You might raise the lower voltage limit from 108
Check to make sure all the voltage readings on each inverter are as close as
possible. A real weakness of the OB platform is that you have to calibrate
each item:
Not sure about the radians (I've rarely used them) but with the VFX series,
that symptom can sometimes be avoided by programming a cool down period so
that the inverters drop the generator while it is still running at full
speed. Alternatively, by narrowing the generator voltage window at the
I have an off grid system with three GS8048A inverters.
Every time it switches from generator charging to inverting - at the end of
absorption - the lights flicker and a propane boiler in the house goes into
fault.
I'm using Advanced AGS on the Mate3S.
The loads don't exceed about 6 kW right now.