Hi Mac and All, If you are about to do a Supply-side tap I'd encourage you to look into the many advantages of using a Feeder Tap instead - one of which is that since it's not on the load side of the Main the equipment need not be Service Rated. (not that you might not want it to be anyway.)

Re: [RE-wrenches] Service rated tap devices

2023-07-20 Thread August Goers via RE-wrenches
Hi Mac - Here's a list of NEC 230.46 compliant multitap connectors from NSI, maker of Polaris brand: https://www.nsiindustries.com/line-side-skus/ Note that only the two-port variants are currently on their list, which is sort of a pain. We've been using the IT-350 which has dual-side wire

[RE-wrenches] Service rated tap devices

2023-07-19 Thread Mac Lewis via RE-wrenches
Hello Wrenches, Is there any tap devices (piercing or other) that are UL Listed for tapping on the utility side of a main breaker for a solar interconnection? Our AHJ won't allow anything that isn't service rated. Thanks in advance! -- Mac Lewis *"Yo solo sé que no sé nada." -Sócrates*