Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Christopher Warfel via RE-wrenches
I talked to SolArk about the input amperage limitation on a recent project. Someone correct me if I am wrong, but SolArk does automatically limit excess amperage.  We were very close on the limit and it made no sense to me that they would design something with parallel MPPT that limit one to

Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Kirk Herander via RE-wrenches
t;> William Miller >> >> >> >> Miller Solar >> >> 17395 Oak Road, Atascadero, CA 93422 >> >> 805-438-5600 >> >> www.millersolar.com >> >> CA Lic. 773985 >> >> >> >> >> >> *From:* RE-wrenches [m

Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Kirk Herander via RE-wrenches
gt; > William Miller > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Beha

Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Darryl Thayer via RE-wrenches
Hi, Ron, Yes, you must be careful of the MPPT inputs. You state Sol-Ark has an 18 amp max input, meaning you can not have more than 1 string supplying an MPPT if your 60 cell modules are 10 amps Isc. You state Sol-Ark has a maximum voltage per MPPT of 500 volts, this voltage is *not Voc x number

Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Kirk Herander via RE-wrenches
I feel the same way about the Outback Radian GSLC box, once it's fully wired there's no room whatsoever, and sometimes you have to remove breakers and layers of wiring to re-access things for debug. Don't know how it meets code and ETL approval for wire space. On Thu, Apr 14, 2022 at 11:20 AM

Re: [RE-wrenches] Sol-Ark install

2022-04-14 Thread Jason Szumlanski via RE-wrenches
This problem is not limited to one manufacturer. One example is the Enphase smart controller. While the small holes are big enough for #6 ground and neutral, you have to strip the wires perfectly and have the hand of a heart surgeon to get them in there. And conduit entry is a royal pain because

[RE-wrenches] Sol-Ark install

2022-04-14 Thread Dana Orzel via RE-wrenches
We have done one Solark installation & I was shocked as to the lack of ground wire landing terminals & space. We added a 12126 metal box below to ease the # of entrances to two 11/4”. I jumpered a # 8 to a second ground bar to allow for additional landing locations. I called Solark to question

Re: [RE-wrenches] Sol-Ark install

2022-04-13 Thread Maverick Brown via RE-wrenches
Ron The Sol-Ark has two MPPT channels and has two separate landing spots for each MPPT channels. Each landing pair needs matching strings. 8 AWG wire barely fits so the Sol-Ark PV terminals so they may only be rated for 10AWG. I’m assuming you have a ground array The most common stringing

Re: [RE-wrenches] Sol-Ark install (Admin Post)

2022-04-13 Thread Michael Welch via RE-wrenches
Hi gang, let's take any further discussion of Wrench List qualifications off-list, please email me directly with any questions or concerns. First, this is not a NABCEP-only list. If I had to guess, less than half of you have pro installer certifications. In fact, this list predates NABCEP and

Re: [RE-wrenches] Sol-Ark install

2022-04-13 Thread Mac Lewis via RE-wrenches
NABCEP PV Installation Pro certified? > > > > Scot Arey > > Owner, Solar CenTex > > > > *From:* RE-wrenches *On > Behalf Of *Jerry Shafer via RE-wrenches > *Sent:* Tuesday, April 12, 2022 10:27 PM > *To:* RE-wrenches > *Cc:* Jerry Shafer > *Subject:

Re: [RE-wrenches] Sol-Ark install

2022-04-13 Thread Scot Arey via RE-wrenches
??? How can this be asked here? Ron, are you NABCEP PV Installation Pro certified? Scot Arey Owner, Solar CenTex From: RE-wrenches On Behalf Of Jerry Shafer via RE-wrenches Sent: Tuesday, April 12, 2022 10:27 PM To: RE-wrenches Cc: Jerry Shafer Subject: Re: [RE-wrenches] Sol-Ark

Re: [RE-wrenches] Sol-Ark install

2022-04-13 Thread William Miller via RE-wrenches
:* Tuesday, April 12, 2022 7:42 PM *To:* RE-wrenches *Cc:* Ron Young *Subject:* [RE-wrenches] Sol-Ark install Hi Wrenches, trying to wrap my head around a first time Sol-Ark install. Because the max DC voltage is 500v at 18a and the PV I’m using is 40v DC each I will have to create three strings each

Re: [RE-wrenches] Sol-Ark install

2022-04-12 Thread Jerry Shafer via RE-wrenches
Need more than this, we have amperage, we need distance, temp, # of wires per conduit, also at 480 you may want to verify cold temp for over the top voltage @ VOC, any RSD device(s) being used? Help to have total module count, as an example use a combiner to make 4 strings, 2 of equal voltage per

[RE-wrenches] Sol-Ark install

2022-04-12 Thread Ron Young via RE-wrenches
Hi Wrenches, trying to wrap my head around a first time Sol-Ark install. Because the max DC voltage is 500v at 18a and the PV I’m using is 40v DC each I will have to create three strings each 480v. What would be the best choice for a home run wire? I’ve always used smaller strings with micro