Re: [RE-wrenches] SolarEdge optimizers require amp deration?

2024-08-13 Thread Jason Szumlanski via RE-wrenches
I think the answers you want might be in this document. See Page 5. https://knowledge-center.solaredge.com/sites/kc/files/se_3p_system_design_and_nec.pdf (this document addresses 3-phase design, but it is still applicable) Jason Szumlanski Principal Solar Designer | Florida Solar Design Group NA

[RE-wrenches] SolarEdge optimizers require amp deration?

2024-08-13 Thread Mick Abraham via RE-wrenches
Hi, Wrench List colleagues~ I have a minor dispute with a technician at one of the solar superstores. He says the amp rating on SolarEdge optimizers needs a 25% "safety factor". SolarEdge's spec sheet says "Maximum Output Current" for model S500 is 15 amps. I'm not sure if the technician would tak

Re: [RE-wrenches] SolarEdge Car Charger

2023-07-25 Thread david quattro via RE-wrenches
I haven’t installed a Solaredge in years so my info might not be up to date, but I remember that the EV Charger units couldn’t be commissioned without an active internet connection. The early models had high failure rate, but that was within the first year or two that they offered the EV Charger/i

[RE-wrenches] SolarEdge Car Charger

2023-07-25 Thread Howie Michaelson via RE-wrenches
Hi All, I have never installed the SolarEdge car charger, and even though it seems to have some capacity advantages over a standalone charger, for some reason I've stayed away from them. I'd be interested to hear others' takes on the advantages/disadvantages of going that route. Thanks, Howie

[RE-wrenches] SolarEdge and Schneider Conext

2023-07-05 Thread Howie Michaelson via RE-wrenches
Hi all, Had anyone successfully established communications between a SolarEdge single phase inverter and a Schneider Gateway? I have a client with a battery backup system which included a dual stack of XW pros and 2 AC coupled SolarEdge inverters. He would really like to be able to use one monitori

[RE-wrenches] SolarEdge

2022-02-23 Thread Marco Mangelsdorf
Aloha, I’m in search of SolarEdge Optimizers. If any of you have any leads on a source, please contact me off list. Mahalo, marco ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@l

Re: [RE-wrenches] SolarEdge Monitoring Access

2022-02-07 Thread Mac Lewis
Hello Wrenches, I don't have a ton of SolarEdge experience, but I found that they seem pretty good at chat support. Fairly fast and effective the few times I've done it. Hopefully they could resolve this issue using this method. You can sign up as an installer and then log in here. https://www.

Re: [RE-wrenches] SolarEdge Monitoring Access

2022-02-07 Thread Dave Tedeyan
Maybe I just got lucky, but at least once I just called (or maybe even only submitted a ticket to) SolarEdge about an orphaned system asking for installer access and they just granted it. It's worth a shot. Cheers, Dave On Mon, Feb 7, 2022 at 3:57 PM Jason Szumlanski < ja...@floridasolardesigngrou

[RE-wrenches] SolarEdge Monitoring Access

2022-02-07 Thread Jason Szumlanski
Does anyone know if there is an easier way to get access to a client's monitoring site? The Site Transfer Form is an infuriating process and customer service takes forever to process forms in my experience. Enphase makes this SO much easier. I'm [reluctantly] taking on quite a few service clients d

[RE-wrenches] Solaredge/LG Troubleshooting

2022-02-06 Thread Jon Siegenthaler
Hi Michael, I've been there with Solaredge and LG so many times I just call them after it's all installed and make them walk me through the commissioning process. Yes, we are solar professionals and yes we can read and follow instructions BUT, I've sent back fully working inverters after tech supp

[RE-wrenches] Solaredge/LG Troubleshooting

2022-02-05 Thread Michael Morningstar
Wrenches, I received a call from a person who is having issues with his Solaredge/LG system. He’s got a SE7600A-US, StoreEdge connection unit, autotransformer, and LG battery. I’ve never laid hands on SE or LG equipment and could use some guidance here. He’s located several hours from me, and I

[RE-wrenches] SolarEdge Energy Hub

2022-01-20 Thread Jason Szumlanski
A homeowner reached out to me with an issue that I am not familiar with because I don't do a lot of work on SolarEdge. She has an Energy Hub and is disappointed that her contractor sold her a system with "future generator support firmware upgrade" promised. From what I read, this upgrade never came

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2022-01-03 Thread Jason Szumlanski
Good feedback. I'll note that we haven't seen any issues with the Eaton 60A, but we decided to go with Square D because it is robust and cost effective. Jason Szumlanski Florida Solar Design Group On Mon, Jan 3, 2022, 4:49 PM Dave Tedeyan wrote: > Hi All, > I thought I would follow up to report

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2022-01-03 Thread Dave Tedeyan
Hi All, I thought I would follow up to report that I swapped out the old GE 60A switch with a SQD one, and there have been no blown fuses since! Cheers, Dave On Tue, Nov 2, 2021 at 4:50 PM Jerry Shafer wrote: > looks like one more failure, once they start there is no going back as the > fuse ret

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-02 Thread Jerry Shafer
looks like one more failure, once they start there is no going back as the fuse retainer loses its spring On Tue, Nov 2, 2021 at 1:38 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > Ugh - no joke - we just found another one this morning with a blown fuse. > Pic attached. It's re

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-02 Thread Jason Szumlanski
Trust me when I tell you that all of the line side conductors and taps are likely fine. It is unequivocally the switch contacts that are the issue. That said, I usually replace the conductors when there is any indication of overheating near the terminals. I have seen discolored copper, but it never

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-02 Thread Dave Tedeyan
It is always the left fuse! Thanks all for the pointers. I'll double check the monitoring, but am thinking that I will be replacing the switch with a SQD, and replacing the taps and AC wires as well while I'm at it. Cheers, Dave On Mon, Nov 1, 2021, 9:13 PM Jerry Shafer wrote: > Bad switch > > >

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Jerry Shafer
Bad switch On Mon, Nov 1, 2021 at 5:44 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > See attached image. Notice the discoloration on the top of the left fuse. > It's always the same thing, same place. > > Jason > > On Mon, Nov 1, 2021, 8:30 PM Jason Szumlanski < > ja...@flori

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Jason Szumlanski
I should also mention that it has nothing to do with ambient heat. This has occured in all seasons and with disconnects in direct sunlight on a south wall and disconnects in air conditioned garages. It's just a garbage product. We switched to Square D for 60A D222NRB fusible disconnects and are al

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Jason Szumlanski
It's the disconnect. We had dozens of this subpar disconnect design fail on Enphase systems. The 2 Pole has the same issue. GE gave us some nonsense answer that it's General Duty and not designed for continuous high power. Even 40A combined Enphase systems will blow a 60A fuse. What you will find

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Jerry Shafer
gt;>> ground, causing the fuse to fail over time. >>> >>> We had a similar situation with a much larger system where the culprit >>> was hard to notice… >>> >>> >>> >>> Best regards, >>> >>> Lloyd >>&

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Howie Michaelson
ausing the fuse to fail over time. >>> >>> We had a similar situation with a much larger system where the culprit >>> was hard to notice… >>> >>> >>> >>> Best regards, >>> >>> Lloyd >>> >>>

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread August Goers
>>> Best regards, >>> >>> Lloyd >>> >>> >>> >>> Lloyd Hoffstatter >>> >>> Sunstruck Consulting >>> >>> >>> >>> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986> for >

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Dave Tedeyan
larger system where the culprit >> was hard to notice… >> >> >> >> Best regards, >> >> Lloyd >> >> >> >> Lloyd Hoffstatter >> >> Sunstruck Consulting >> >> >> >> Sent from Mail <https://go.micr

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Jerry Shafer
/fwlink/?LinkId=550986> for > Windows > > > > *From: *Dave Tedeyan > *Sent: *Monday, November 1, 2021 4:26 PM > *To: *RE-wrenches > *Subject: *[RE-wrenches] SolarEdge inverter blowing fuses > > > > Hi All, > > > > I am servicing a system that keep

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread jay
HI Dave, Which exact fuses do they have installed? I’m guessing they are blowing due to not being constant load rated fuses and summer higher temps. jay peltz power > On Nov 1, 2021, at 2:26 PM, Dave Tedeyan wrote: > > Hi All, > > I am servicing a system that keeps blowing fuses on the AC

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Lloyd Hoffstatter
tps://go.microsoft.com/fwlink/?LinkId=550986> for Windows From: Dave Tedeyan<mailto:d...@sungineersolar.com> Sent: Monday, November 1, 2021 4:26 PM To: RE-wrenches<mailto:re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] SolarEdge inverter blowing fuses Hi All, I am servicing a

[RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Dave Tedeyan
Hi All, I am servicing a system that keeps blowing fuses on the AC side, although it appears that everything is sized correctly. It is a SolarEdge SE11400A-US inverter. Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE TG3222R 60A AC disconnect, and it is wired up with #6 THH

[RE-wrenches] SolarEdge Site Monitoring Administration Rights Transfer Form

2020-08-26 Thread Jason Szumlanski
If anyone has a copy of this form, can you please send it to me off list? I don't understand why SolarEdge hides access to this document and makes it so hard to take over another installer's site. I'm cleaning up a lot of messes recently and it's really hard to support these service clients.

Re: [RE-wrenches] Solaredge Storedge backup operation

2020-08-21 Thread Kirk Herander, VT Solar, LLC
short answer: no. Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar] Owner|Principal, VT Solar, LLC Celebrating our 29th Anniversary 1991-2020 www.vermont.solar [https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d6853

Re: [RE-wrenches] Solaredge Storedge backup operation

2020-08-21 Thread Jerry Shafer
Wrenches Only if you turn off the disconnect on the inverter or the inverter itself, otherwise all will remain active. JERRY On Fri, Aug 21, 2020, 5:52 AM Mac Lewis wrote: > Hi Wrenches, > > Is this article correct when it states that the solar modules will shut > down in the event of a power ou

[RE-wrenches] Solaredge Storedge backup operation

2020-08-21 Thread Mac Lewis
Hi Wrenches, Is this article correct when it states that the solar modules will shut down in the event of a power outage with the Storedge system? https://www.solaris-shop.com/blog/hybrid-solar-systems-what-you-need-to-know/ That seems like a pretty weak offering if that's true. It seems to c

[RE-wrenches] SolarEdge - are you listening on here???

2019-09-05 Thread scot.arey
How did a company that I would tell customers had the very best tech support in the business fall so far, so quickly. This is the 5th exchange with tech support regarding StorEdge not charging. Used to work just great.until it did not. At least I'm only 34 in line. SolarEdge - your Dire

Re: [RE-wrenches] SolarEdge

2019-08-05 Thread William Miller
*Kirpal *Sent:* Monday, August 5, 2019 1:31 PM *To:* RE-wrenches *Subject:* [RE-wrenches] SolarEdge Hi FolksDoes anyone know how to reach SolarEdge support. We have numerous sites with issues and have been on phone hold for well over 3 hours. Multiple days in a row. No one answers. We tired

Re: [RE-wrenches] SolarEdge

2019-08-05 Thread Jason Szumlanski
One word: Enphase. They have had issues with customer support in the past, but nothing close to this, and recently it has made a remarkable turnaround. The support staff is exceptionally well trained. The strange thing is sometimes I can wait 20+ minutes and sometimes someone picks up immediately.

[RE-wrenches] SolarEdge

2019-08-05 Thread Kirpal
Hi FolksDoes anyone know how to reach SolarEdge support. We have numerous sites with issues and have been on phone hold for well over 3 hours. Multiple days in a row. No one answers. We tired their online chat tool and we are #49 on the wait list to be addressed. This is pretty ridiculous.

Re: [RE-wrenches] Solaredge inverter noise

2019-08-02 Thread Chris Worcester
Turn off the cb to the inverter and try it Chris Worcester  ch...@solarwindworks.com 530-448-9692on my Samsung Galaxy S7. Original message From: Ron Young Date: 8/2/19 3:42 PM (GMT-08:00) To: RE-wrenches Subject: [RE-wrenches] Solaredge inverter noise I have a client

Re: [RE-wrenches] Solaredge inverter noise

2019-08-02 Thread Rick Brown
Has your client verified that it’s the inverter, i.e. have they turned off the inverter? Could also be the utility meter. rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergyAlternatives.com Check, Virginia 24072 540.808.9502 VA Class A Contrac

[RE-wrenches] Solaredge inverter noise

2019-08-02 Thread Ron Young
I have a client complaining about RF noise from his Solaredge 5kw GT inverter installed in 2018. He believes it is causing static on his radio no matter where he locates it in the house. I haven’t been able to visit the site yet but wondering if there are any suggestions for mitigating RF or lin

Re: [RE-wrenches] SolarEdge woes

2019-08-02 Thread penobscotsolar
ffice) > > 530-217-8385 (Cell) > >  > >     > > > > From: RE-wrenches on behalf of > Marco Mangelsdorf > Sent: Wednesday, July 31, 2019 12:08:46 PM > To: 'RE-wrenches' > Subject: [RE-wrenches] Sola

Re: [RE-wrenches] SolarEdge woes

2019-08-01 Thread MiJo Nels
roup.com> 530-273-4422 (Office) 530-217-8385 (Cell)      From: RE-wrenches on behalf of Marco Mangelsdorf Sent: Wednesday, July 31, 2019 12:08:46 PM To: 'RE-wrenches' Subject: [RE-wrenches] SolarEdge woes Aloha, Does anyone know any

Re: [RE-wrenches] SolarEdge woes

2019-07-31 Thread Howard Arey
they have done is pass customer support onto our backs. Howard "Scot" Arey 254-300-1228 <mailto:scot.a...@solarcentex.com> scot.a...@solarcentex.com From: RE-wrenches On Behalf Of Marco Mangelsdorf Sent: Wednesday, July 31, 2019 2:09 PM To: 'RE-w

Re: [RE-wrenches] SolarEdge woes

2019-07-31 Thread Matt Partymiller
I believe calling at 2 AM your time would help. Once you hit about 8:30 AM EST, you might as well just do the online thing. Often online just takes 10-30 minutes and you get a valid answer (though I was told by a tech today he spent three hours going this route - hopefully that was a one-time occ

[RE-wrenches] SolarEdge woes

2019-07-31 Thread Marco Mangelsdorf
Aloha, Does anyone know any special tricks to get through to a live person at SolarEdge support? We've been dealing with nightmare waits of HOURS while my field crew wait, wait and wait and wait some more. Thanks, marco ___ List sponsored by

Re: [RE-wrenches] SolarEdge reliability declining...???

2019-07-25 Thread Martin Herzfeld
Good to know. 1. I just installed the latest SetApp inverters (the ones without displays) for a ground-mounted array with the inverter in the dwelling. 2. The ground-mounted system had to comply with CEC 2016/NEC 2014 690.12 in California because the system was "in the building." Would the inve

Re: [RE-wrenches] SolarEdge AC coupled off-grid (part 2)

2019-07-25 Thread Ray
I've AC coupled off grid with the Sunny Island, but I haven't tried it with Solar Edge.  Can you adjust the Solar Edge coupling window to outside the IEEE set points?  We used to have set all GT inverters in Hawaii wider, because the utility wanted them to stay on longer in a brown out. Ray W

Re: [RE-wrenches] SolarEdge AC coupled off-grid (part 2)

2019-07-25 Thread Howie Michaelson
Hi Ray, I get the issues with AC coupling. However, this system already has a 3+ kW DC coupled array, the new array is close to 200' away, and it would take 2 more charge controllers of any of high voltage ones for this size array. Are there any battery based inverters that folks have had decent l

Re: [RE-wrenches] SolarEdge AC coupled off-grid (part 2)

2019-07-24 Thread Ray
I do not recommend AC coupling for off grid, except to offset daytime loads or to add PV at remote buildings.  Besides coupling errors like you're experiencing, the entire system will shut down and not recharge, if the VFX inverters shut down.   With a DC coupled array, the batteries can rechar

[RE-wrenches] SolarEdge AC coupled off-grid (part 2)

2019-07-24 Thread Howie Michaelson
sorry, prematurely emailed previous post: I'm wondering if the VFXs are just not capable of putting out clean enough power in order to hold the SE HD inverter. I had it operating on this same system for a couple of hours with not this problem. Is it likely that this inverter combo is not going to

[RE-wrenches] SolarEdge AC coupled off-grid

2019-07-24 Thread Howie Michaelson
I have used SolarEdge to AC couple a smaller Array in the past, with no issues. I recently added a fairly significant array (6.2k DC via a SE6K (setap) inverter in an off-grid home which has had a dual stack VFX3648 for many years. I also added 32kWh of Blue Ion batteries replacing an 80kWh older

Re: [RE-wrenches] SolarEdge reliability declining...???

2019-07-24 Thread Brett Bartmasser
707-923-2001 ext. 100 >> >> 1150 #1 Evergreen Rd >> >> Redway, CA 95560 >> >> www.greenwired.com >> >> [image: Description: signature] >> >> >> >> >> >> >> >> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wre

Re: [RE-wrenches] SolarEdge reliability declining...???

2019-07-24 Thread Jerry Shafer
w.greenwired.com > > [image: Description: signature] > > > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Howard Arey > *Sent:* Wednesday, July 24, 2019 7:37 AM > *To:* 'RE-wrenches' > *Subject

Re: [RE-wrenches] SolarEdge reliability declining...???

2019-07-24 Thread Andrew
g] On Behalf Of Howard Arey Sent: Wednesday, July 24, 2019 7:37 AM To: 'RE-wrenches' Subject: [RE-wrenches] SolarEdge reliability declining...??? Have any of you seen significant declines in SolarEdge inverter reliability? We are having more inverter failures that at any time in the pas

[RE-wrenches] SolarEdge reliability declining...???

2019-07-24 Thread Howard Arey
Have any of you seen significant declines in SolarEdge inverter reliability? We are having more inverter failures that at any time in the past five years of installing SolarEdge. Lots of Code 181 hardware failures mostly in the latest SetApp inverters (the ones without displays.) To compound matt

Re: [RE-wrenches] SolarEdge change over with SunPower Modules??

2017-12-19 Thread August Goers
Tom - I was just asking a SunPower rep about this. My understanding is that a PID (Potential Induced Degredation) discharge device is required to use SunPower positively grounded modules with a transformerless inverter. These are expensive and not listed for the US market. Long story short, I don't

[RE-wrenches] SolarEdge change over with SunPower Modules??

2017-12-19 Thread Tom Lane
I have a Postive grounded SunPower System with two private labeled SMA 6000 watt Inverters installed in 2009 and want to use SolarEdge 7600 and their optimizers at least for half the array ? Modules are SunPower 210 watt modules - how do I work this out ? GatorTom PS : 48 modules ground mounted i

[RE-wrenches] SolarEdge tech help

2017-08-28 Thread Jeremy Rodriguez
Does anyone have a dealer only phone number to reach SolarEdge tech support? Jeremy Rodriguez Solar Installation And Design Expert All Solar, Inc. 1463 M St Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand! ___ List spon

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Chris Mason
Yes, correct on both. The generator support is there, I did not use it. On Fri, Jun 17, 2016 at 3:07 PM, Carl Adams wrote: > Chris, > > Nice finish on the Sonnen install. It looks fabulous. My understanding > is the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW > radian.

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Carl Adams
Chris, Nice finish on the Sonnen install. It looks fabulous. My understanding is the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW radian. I assume generator support is fully supported On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason wrote: > I promised a picture of the So

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Chris Mason
I promised a picture of the Sonnen installation. As these units are getting close to being appliances in the same vein as home audio, we wanted to have a clean finish so we made some mill work to complete the top of the unit to the ceiling and hide the ugly conduits. https://www.dropbox.com/s/vlh0u

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-16 Thread Marco Mangelsdorf
Dunno exactly, Carl. Twas not I who installed it. marco Marco, Are the two switch gear boxes integral to the installation. If so can you give me an idea of what their function/purpose is? On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf wrote: Provides an idea of size and scale

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-16 Thread Carl Adams
Marco, Are the two switch gear boxes integral to the installation. If so can you give me an idea of what their function/purpose is? On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf wrote: > Provides an idea of size and scale. > > [image: Tesla Battery system Aalto residence2. 6 may 2016] > >

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Chris Mason
> >>> Best regards, >>> >>> Lloyd >>> >>> >>> >>> Lloyd Hoffstatter >>> >>> M.S. in Applied Solar Energy >>> >>> NABCEP Solar PV Installer #102503-23 >>> >>> >

[RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Marco Mangelsdorf
Marco Mangelsdorf Sent: Monday, June 13, 2016 11:43 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall Yes, Howie…their SE StorEdge. Not my install. Sunrun did it on Oahu. Did a big press whoopdeedo and even got the governor of Hawaii and mayor of Ho

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Lloyd Hoffstatter
enches Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall I would love to hear more about that install. Design, sense of equipment quality and development (is programming and function well thought out and implemented), availability, pictures, etc. are all significant questions. Thanks f

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Howie Michaelson
loyd Hoffstatter >> >> M.S. in Applied Solar Energy >> >> NABCEP Solar PV Installer #102503-23 >> >> >> >> Director >> >> Sunstruck Consulting >> >> ll...@sunstruckconsulting.com >> >> 845-657-8132 >> >> >> >>

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Chris Mason
ter > > M.S. in Applied Solar Energy > > NABCEP Solar PV Installer #102503-23 > > > > Director > > Sunstruck Consulting > > ll...@sunstruckconsulting.com > > 845-657-8132 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wren

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Lloyd Hoffstatter
RE-wrenches' Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall Yes, Howie…their SE StorEdge. Not my install. Sunrun did it on Oahu. Did a big press whoopdeedo and even got the governor of Hawaii and mayor of Honolulu to attend. marco From: RE-wrenches [mailto:re-wrenches-

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Marco Mangelsdorf
: Monday, June 13, 2016 4:55 PM To: RE-wrenches Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall Hi Marco, I assume that is the StorEdge 7600? Is this your install? What was your access to the StorEdge? Thanks for the photo, Howie Howie Michaelson NABCEP Certified Solar PV Installer™ Sun

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-13 Thread Howie Michaelson
Hi Marco, I assume that is the StorEdge 7600? Is this your install? What was your access to the StorEdge? Thanks for the photo, Howie Howie Michaelson NABCEP Certified Solar PV Installer™ Sun Catcher Renewable Energy Systems Sales and Service VT Solar Electric Incentive Partner 802-272-0004 On Ju

[RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-13 Thread Marco Mangelsdorf
Provides an idea of size and scale. Tesla Battery system Aalto residence2. 6 may 2016 >From left to right-disconnect, kWh meter, SolarEdge 7600, switch gear, two Tesla Powerwalls. --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus ___

Re: [RE-wrenches] SolarEdge comm card failures

2016-04-19 Thread Carl Adams
Howie, Thanks for your response. I would agree that we have not seen this problem with systems installed after 2012. The technology has improved, and the Comm card in the inverter has been thru several iterations since then. I would also agree that SE has improved on their tech support respons

Re: [RE-wrenches] SolarEdge comm card failures

2016-04-18 Thread Howie Michaelson
Carl, We experienced a rash of Comm Card issues with several SE installs over several years, but none exactly as you describe. Our issues were almost all resolved with a board replacement, but a few were particularly vexing with many return service calls to get a resolution. We seemed to have th

[RE-wrenches] SolarEdge comm card failures

2016-04-18 Thread Carl Adams
Hello Wrenches, Anyone experiencing issues with comm card failures on SolarEdge inverters? We have some systems installed in 2012 exhibiting similar behaviors. The systems are producing data, it is registering on the inverter, and our independent utilty meter, but is not reported to the SolarEdg

Re: [RE-wrenches] Solaredge Storedge

2015-07-02 Thread William Miller
Kirk: And a PR nightmare for integrators. The customer will be very disappointed that you have to charge at least several times the cost of the battery pack to make it provide back-up power. The overly rosy picture painted is a disservice to the industry. On a related note: It is 201

Re: [RE-wrenches] Solaredge Storedge

2015-07-02 Thread Kirk Herander
t: Monday, June 29, 2015 2:56 PM To: RE-wrenches Subject: Re: [RE-wrenches] Solaredge Storedge I would think that Solar City would know all about this. Or, maybe I wouldn't ? boB On 6/29/2015 11:06 AM, Rebekah Hren wrote: I don't have any info, but the StorEdge diagram is con

Re: [RE-wrenches] Solaredge Storedge

2015-07-01 Thread Rebekah Hren
RE Incentive Program Partner > > 802.863.1202 > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *b...@midnitesolar.com > *Sent:* Monday, June 29, 2015 2:56 PM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Solaredge

Re: [RE-wrenches] Solaredge Storedge

2015-06-30 Thread Chris Mason
Just to add a little perspective on the development of inverter based storage, I have just attended InterSolar Europe in Munich. Every inverter manufacturer is showing some type of add-on battery storage system. SolarEdge was huge, they had the largest visibility of the inverter manufacturers. The

Re: [RE-wrenches] Solaredge Storedge

2015-06-29 Thread toddcory
cant VT RE Incentive Program Partner 802.863.1202 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of b...@midnitesolar.com Sent: Monday, June 29, 2015 2:56 PM To: RE-wrenches Subject: Re: [RE-wrenches] Solaredge Storedge I would think that Solar City would know

Re: [RE-wrenches] Solaredge Storedge

2015-06-29 Thread Kirk Herander
On Behalf Of b...@midnitesolar.com Sent: Monday, June 29, 2015 2:56 PM To: RE-wrenches Subject: Re: [RE-wrenches] Solaredge Storedge I would think that Solar City would know all about this. Or, maybe I wouldn't ? boB On 6/29/2015 11:06 AM, Rebekah Hren wrote: I don't have any info, bu

Re: [RE-wrenches] Solaredge Storedge

2015-06-29 Thread b...@midnitesolar.com
I would think that Solar City would know all about this. Or, maybe I wouldn't ? boB On 6/29/2015 11:06 AM, Rebekah Hren wrote: I don't have any info, but the StorEdge diagram is confusing to me when it says "energy independence." I can see a simple compatibility between the Powerwall DC vo

Re: [RE-wrenches] Solaredge Storedge

2015-06-29 Thread Rebekah Hren
I don't have any info, but the StorEdge diagram is confusing to me when it says "energy independence." I can see a simple compatibility between the Powerwall DC voltage (300 to 400VDC) and the SolarEdge operating voltage, ~350VDC, and I can also see how this setup could be used to maximize self-con

[RE-wrenches] Solaredge Storedge

2015-06-29 Thread Kirk Herander
Hello, Anyone have detailed info on the Storedge battery-compatible system from Solaredge? I only found a brochure on their website. Apparently batteries can be added to a new or existing Solaredge inverter (the brochure says they have partnered with Tesla's Powerwall) for backup power. They call

[RE-wrenches] SolarEdge

2014-06-25 Thread Advanced Energy Solutions
Anyone heard any issues with SolarEdge optimizers not being encapsulated and corroding in salt water climates? Or overheating? What do you know about SolarEdge as a product? -- Stay Energized, PEACE> Aur J Beck, NABCEP Certified Solar PV Installer™ 032611-24 NABCEP Certified PV Technical Sales™

Re: [RE-wrenches] SolarEdge with AC coupling / Sunny Island

2014-03-11 Thread August Goers
Hi Tom, I might be missing your question, but I believe that you would couple the SolarEdge inverter to the AC1 line of the Sunny Island, just like with any grid tie inverter. In other words, the SolarEdge inverter would tie into the critical loads panel that is fed by the Sunny Island. Best, Aug

[RE-wrenches] SolarEdge with AC coupling / Sunny Island

2014-03-11 Thread Tom Lane
Does anyone have a diagram on how to AC couple SolarEdge Inverters that use the DC Optimizers to AC coupling with a Sunny Island like SMA 6048 . John Berdner started a link quite a while ago that I do not think included a diagram . John did mention that the SMA had the correct or best Algorithm

Re: [RE-wrenches] Solaredge inverters w/ backup generator

2014-02-14 Thread Exeltech
. Personally, I think an "interlock" on a string system is a reasonable request, and likely to appear in future models from different manufacturers. It's just going to take time. Dan On Fri, 2/14/14, Chris Mason wrote: Subject: Re: [RE

Re: [RE-wrenches] Solaredge inverters w/ backup generator

2014-02-14 Thread Chris Mason
The "Door Open" switch is a very useful feature. I am trying to get Fronius to put a digital shutdown terminal on its CL line of inverters, or all inverters preferably. We need to pressure all the inverter manufacturers to provide a logic in or dry contact method of shutdown. Most ATS will provide

Re: [RE-wrenches] Solaredge inverters w/ backup generator

2014-02-13 Thread Jerry Shafer
I have done systems in Hawaii, here is one with a 30 k PV system and with a 250k Cummins back up genny. We have a contactor in the ATS that will open if the genny is operating, this in turn sends a door open signal to the Satcon shutting it down I don't want anything effecting the genset operation

Re: [RE-wrenches] Solaredge inverters w/ backup generator

2014-02-09 Thread Chris Mason
That's total nonsense. Most of our installs involve a generator, as generators are very common here due to intermittent electrical supply and hurricanes. We also sell and install generators and I am a tech. A decent heavy generator will produce electricity that will fall within the IEEE 1547 specif

[RE-wrenches] Solaredge inverters w/ backup generator

2014-02-08 Thread Kirk Herander
Hello, I recently posed the question to Solaredge tech support, wondering if their inverter, in this case a 20kw 480 3-phase, would have any issues if it were connected to an AC panel backed up by a generator. They told me no problem, for the inverter's anti-islanding will work if it sees the "

[RE-wrenches] Solaredge 480v 3-phase inverters

2013-08-09 Thread Kirk Herander
Hello, Has anyone on list installed a Solaredge 480/227 3-phase inverter? The spec sheet says that the nominal input DC+ to DC- is 840vdc. I assume this is the regulated operational voltage, and so the system installation falls under the code rules for 1000vdc systems, correct? My local utility

Re: [RE-wrenches] SolarEdge Optimizer - Was: Tigo and SMA AFCI - Was: AC coupled, grid-tied Sunny Island - contactor & bypass

2013-06-05 Thread Steve Higgins
To: RE-wrenches Subject: Re: [RE-wrenches] SolarEdge Optimizer - Was: Tigo and SMA AFCI - Was: AC coupled, grid-tied Sunny Island - contactor & bypass SolarEdge makes an optimizer / inverter system. We just installed one. Our clients are happy. So are we. Don't know if you can AC couple the

Re: [RE-wrenches] SolarEdge Optimizer - Was: Tigo and SMA AFCI - Was: AC coupled, grid-tied Sunny Island - contactor & bypass

2013-06-05 Thread Richard L Ratico
SolarEdge makes an optimizer / inverter system. We just installed one. Our clients are happy. So are we. Don't know if you can AC couple the inverter. Their website says they are about to release a version of the optimizer that will work with other manufacturer's inverters. Dick Ratico Solarwind

Re: [RE-wrenches] Solaredge AC-coupling revisited

2013-02-26 Thread John Berdner
94538 USA (*Please note of our new address.) T: 510.498.3200, X 747 M: 530.277.4894 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk Herander Sent: Tuesday, February 26, 2013 8:04 AM To: 'RE-wrenches' Subject: Re: [RE-wr

Re: [RE-wrenches] Solaredge AC-coupling revisited

2013-02-26 Thread Kirk Herander
ent: Wednesday, December 19, 2012 1:35 PM To: RE-wrenches Subject: Re: [RE-wrenches] Solaredge AC-coupling Kirk: We have a new version of firmware (in production January 1, 2013) that supports frequency shift power control, e.g. Sunny Island. I am preparing a white paper on how to set it up bu

Re: [RE-wrenches] Solaredge AC-coupling

2012-12-19 Thread John Berdner
te of our new address.) T: 510.498.3201 ext 747 M: 530.277.4894 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk Herander Sent: Tuesday, December 18, 2012 1:16 PM To: RE-wrenches Subject: [RE-wrenches] Solaredge AC-coupling Hello, Anyone ou

[RE-wrenches] Solaredge AC-coupling

2012-12-18 Thread Kirk Herander
Hello, Anyone out successfully AC-coupled a Solaredge inverter with an Outback or other battery-based inverter? Thanks. I may want to do it for an upcoming job. Kirk Herander VT Solar, LLC dba Vermont Solar Engineering NABCEPTM Certified Inaugural Certificant NYSERDA-eligible Installer

Re: [RE-wrenches] SolarEdge v Enphase

2012-01-13 Thread Darryl Thayer
PM To: RE-wrenches Subject: Re: [RE-wrenches] SolarEdge v Enphase   Wrenches, I wish this urban myth about electrolytic capacitors would die, but it won't.  It's been a wonderful marketing ploy for some time now. Simply stated, existence of electrolytic capacitors in inverters does NOT me

Re: [RE-wrenches] SolarEdge v Enphase

2012-01-12 Thread Marv Dargatz
obile: +530.392.0356 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of conrad geyser Sent: Thursday, January 12, 2012 1:30 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] SolarEdge v Enphase Andrew, We installed a Solar Edge sys