I think the answers you want might be in this document. See Page 5.
https://knowledge-center.solaredge.com/sites/kc/files/se_3p_system_design_and_nec.pdf
(this document addresses 3-phase design, but it is still applicable)
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NA
Hi, Wrench List colleagues~ I have a minor dispute with a technician at one
of the solar superstores. He says the amp rating on SolarEdge optimizers
needs a 25% "safety factor".
SolarEdge's spec sheet says "Maximum Output Current" for model S500 is 15
amps. I'm not sure if the technician would tak
I haven’t installed a Solaredge in years so my info might not be up to
date, but I remember that the EV Charger units couldn’t be commissioned
without an active internet connection. The early models had high failure
rate, but that was within the first year or two that they offered the EV
Charger/i
Hi All,
I have never installed the SolarEdge car charger, and even though it seems
to have some capacity advantages over a standalone charger, for some reason
I've stayed away from them. I'd be interested to hear others' takes on the
advantages/disadvantages of going that route.
Thanks,
Howie
Hi all,
Had anyone successfully established communications between a SolarEdge
single phase inverter and a Schneider Gateway? I have a client with a
battery backup system which included a dual stack of XW pros and 2 AC
coupled SolarEdge inverters. He would really like to be able to use one
monitori
Aloha,
I’m in search of SolarEdge Optimizers.
If any of you have any leads on a source, please contact me off list.
Mahalo,
marco
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@l
Hello Wrenches,
I don't have a ton of SolarEdge experience, but I found that they seem
pretty good at chat support. Fairly fast and effective the few times I've
done it. Hopefully they could resolve this issue using this method.
You can sign up as an installer and then log in here.
https://www.
Maybe I just got lucky, but at least once I just called (or maybe even only
submitted a ticket to) SolarEdge about an orphaned system asking for
installer access and they just granted it. It's worth a shot.
Cheers,
Dave
On Mon, Feb 7, 2022 at 3:57 PM Jason Szumlanski <
ja...@floridasolardesigngrou
Does anyone know if there is an easier way to get access to a client's
monitoring site? The Site Transfer Form is an infuriating process and
customer service takes forever to process forms in my experience. Enphase
makes this SO much easier. I'm [reluctantly] taking on quite a few service
clients d
Hi Michael,
I've been there with Solaredge and LG so many times I just call them after
it's all installed and make them walk me through the commissioning process.
Yes, we are solar professionals and yes we can read and follow instructions
BUT, I've sent back fully working inverters after tech supp
Wrenches,
I received a call from a person who is having issues with his Solaredge/LG
system. He’s got a SE7600A-US, StoreEdge connection unit, autotransformer, and
LG battery. I’ve never laid hands on SE or LG equipment and could use some
guidance here. He’s located several hours from me, and I
A homeowner reached out to me with an issue that I am not familiar with
because I don't do a lot of work on SolarEdge. She has an Energy Hub and is
disappointed that her contractor sold her a system with "future generator
support firmware upgrade" promised. From what I read, this upgrade never
came
Good feedback. I'll note that we haven't seen any issues with the Eaton
60A, but we decided to go with Square D because it is robust and cost
effective.
Jason Szumlanski
Florida Solar Design Group
On Mon, Jan 3, 2022, 4:49 PM Dave Tedeyan wrote:
> Hi All,
> I thought I would follow up to report
Hi All,
I thought I would follow up to report that I swapped out the old GE 60A
switch with a SQD one, and there have been no blown fuses since!
Cheers,
Dave
On Tue, Nov 2, 2021 at 4:50 PM Jerry Shafer
wrote:
> looks like one more failure, once they start there is no going back as the
> fuse ret
looks like one more failure, once they start there is no going back as the
fuse retainer loses its spring
On Tue, Nov 2, 2021 at 1:38 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> Ugh - no joke - we just found another one this morning with a blown fuse.
> Pic attached. It's re
Trust me when I tell you that all of the line side conductors and taps are
likely fine. It is unequivocally the switch contacts that are the issue.
That said, I usually replace the conductors when there is any indication of
overheating near the terminals. I have seen discolored copper, but it never
It is always the left fuse! Thanks all for the pointers. I'll double check
the monitoring, but am thinking that I will be replacing the switch with a
SQD, and replacing the taps and AC wires as well while I'm at it.
Cheers,
Dave
On Mon, Nov 1, 2021, 9:13 PM Jerry Shafer wrote:
> Bad switch
>
>
>
Bad switch
On Mon, Nov 1, 2021 at 5:44 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> See attached image. Notice the discoloration on the top of the left fuse.
> It's always the same thing, same place.
>
> Jason
>
> On Mon, Nov 1, 2021, 8:30 PM Jason Szumlanski <
> ja...@flori
I should also mention that it has nothing to do with ambient heat. This has
occured in all seasons and with disconnects in direct sunlight on a south
wall and disconnects in air conditioned garages.
It's just a garbage product. We switched to Square D for 60A D222NRB
fusible disconnects and are al
It's the disconnect. We had dozens of this subpar disconnect design fail on
Enphase systems. The 2 Pole has the same issue.
GE gave us some nonsense answer that it's General Duty and not designed for
continuous high power. Even 40A combined Enphase systems will blow a 60A
fuse.
What you will find
gt;>> ground, causing the fuse to fail over time.
>>>
>>> We had a similar situation with a much larger system where the culprit
>>> was hard to notice…
>>>
>>>
>>>
>>> Best regards,
>>>
>>> Lloyd
>>&
ausing the fuse to fail over time.
>>>
>>> We had a similar situation with a much larger system where the culprit
>>> was hard to notice…
>>>
>>>
>>>
>>> Best regards,
>>>
>>> Lloyd
>>>
>>>
>>> Best regards,
>>>
>>> Lloyd
>>>
>>>
>>>
>>> Lloyd Hoffstatter
>>>
>>> Sunstruck Consulting
>>>
>>>
>>>
>>> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986> for
>
larger system where the culprit
>> was hard to notice…
>>
>>
>>
>> Best regards,
>>
>> Lloyd
>>
>>
>>
>> Lloyd Hoffstatter
>>
>> Sunstruck Consulting
>>
>>
>>
>> Sent from Mail <https://go.micr
/fwlink/?LinkId=550986> for
> Windows
>
>
>
> *From: *Dave Tedeyan
> *Sent: *Monday, November 1, 2021 4:26 PM
> *To: *RE-wrenches
> *Subject: *[RE-wrenches] SolarEdge inverter blowing fuses
>
>
>
> Hi All,
>
>
>
> I am servicing a system that keep
HI Dave,
Which exact fuses do they have installed?
I’m guessing they are blowing due to not being constant load rated fuses and
summer higher temps.
jay
peltz power
> On Nov 1, 2021, at 2:26 PM, Dave Tedeyan wrote:
>
> Hi All,
>
> I am servicing a system that keeps blowing fuses on the AC
tps://go.microsoft.com/fwlink/?LinkId=550986> for Windows
From: Dave Tedeyan<mailto:d...@sungineersolar.com>
Sent: Monday, November 1, 2021 4:26 PM
To: RE-wrenches<mailto:re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] SolarEdge inverter blowing fuses
Hi All,
I am servicing a
Hi All,
I am servicing a system that keeps blowing fuses on the AC side, although it
appears that everything is sized correctly. It is a SolarEdge SE11400A-US
inverter.
Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE
TG3222R
60A AC disconnect, and it is wired up with #6 THH
If anyone has a copy of this form, can you please send it to me off list?
I don't understand why SolarEdge hides access to this document and makes it
so hard to take over another installer's site. I'm cleaning up a lot of
messes recently and it's really hard to support these service clients.
short answer: no.
Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar]
Owner|Principal, VT Solar, LLC
Celebrating our 29th Anniversary 1991-2020
www.vermont.solar
[https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d6853
Wrenches
Only if you turn off the disconnect on the inverter or the inverter itself,
otherwise all will remain active.
JERRY
On Fri, Aug 21, 2020, 5:52 AM Mac Lewis wrote:
> Hi Wrenches,
>
> Is this article correct when it states that the solar modules will shut
> down in the event of a power ou
Hi Wrenches,
Is this article correct when it states that the solar modules will shut
down in the event of a power outage with the Storedge system?
https://www.solaris-shop.com/blog/hybrid-solar-systems-what-you-need-to-know/
That seems like a pretty weak offering if that's true. It seems to
c
How did a company that I would tell customers had the very best tech support
in the business fall so far, so quickly.
This is the 5th exchange with tech support regarding StorEdge not charging.
Used to work just great.until it did not.
At least I'm only 34 in line.
SolarEdge - your Dire
*Kirpal
*Sent:* Monday, August 5, 2019 1:31 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] SolarEdge
Hi FolksDoes anyone know how to reach SolarEdge support. We have
numerous sites with issues and have been on phone hold for well over 3
hours. Multiple days in a row. No one answers. We tired
One word: Enphase.
They have had issues with customer support in the past, but nothing close
to this, and recently it has made a remarkable turnaround. The support
staff is exceptionally well trained. The strange thing is sometimes I can
wait 20+ minutes and sometimes someone picks up immediately.
Hi FolksDoes anyone know how to reach SolarEdge support. We have
numerous sites with issues and have been on phone hold for well over 3
hours. Multiple days in a row. No one answers. We tired their online chat
tool and we are #49 on the wait list to be addressed. This is pretty
ridiculous.
Turn off the cb to the inverter and try it Chris Worcester
ch...@solarwindworks.com 530-448-9692on my Samsung Galaxy S7.
Original message From: Ron Young
Date: 8/2/19 3:42 PM (GMT-08:00) To: RE-wrenches
Subject: [RE-wrenches] Solaredge inverter
noise I have a client
Has your client verified that it’s the inverter, i.e. have they turned off the
inverter? Could also be the utility meter.
rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergyAlternatives.com
Check, Virginia 24072
540.808.9502
VA Class A Contrac
I have a client complaining about RF noise from his Solaredge 5kw GT inverter
installed in 2018. He believes it is causing static on his radio no matter
where he locates it in the house. I haven’t been able to visit the site yet but
wondering if there are any suggestions for mitigating RF or lin
ffice)
>
> 530-217-8385 (Cell)
>
> 
>
>    
>
>
>
> From: RE-wrenches on behalf of
> Marco Mangelsdorf
> Sent: Wednesday, July 31, 2019 12:08:46 PM
> To: 'RE-wrenches'
> Subject: [RE-wrenches] Sola
roup.com>
530-273-4422 (Office)
530-217-8385 (Cell)

   
From: RE-wrenches on behalf of
Marco Mangelsdorf
Sent: Wednesday, July 31, 2019 12:08:46 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] SolarEdge woes
Aloha,
Does anyone know any
they have done is pass
customer support onto our backs.
Howard "Scot" Arey
254-300-1228
<mailto:scot.a...@solarcentex.com> scot.a...@solarcentex.com
From: RE-wrenches On Behalf Of
Marco Mangelsdorf
Sent: Wednesday, July 31, 2019 2:09 PM
To: 'RE-w
I believe calling at 2 AM your time would help. Once you hit about 8:30
AM EST, you might as well just do the online thing. Often online just
takes 10-30 minutes and you get a valid answer (though I was told by a
tech today he spent three hours going this route - hopefully that was a
one-time occ
Aloha,
Does anyone know any special tricks to get through to a live person at
SolarEdge support?
We've been dealing with nightmare waits of HOURS while my field crew wait,
wait and wait and wait some more.
Thanks,
marco
___
List sponsored by
Good to know.
1. I just installed the latest SetApp inverters (the ones without
displays) for a ground-mounted array with the inverter in the dwelling.
2. The ground-mounted system had to comply with CEC 2016/NEC 2014 690.12
in California because the system was "in the building." Would the inve
I've AC coupled off grid with the Sunny Island, but I haven't tried it
with Solar Edge. Can you adjust the Solar Edge coupling window to
outside the IEEE set points? We used to have set all GT inverters in
Hawaii wider, because the utility wanted them to stay on longer in a
brown out.
Ray W
Hi Ray,
I get the issues with AC coupling. However, this system already has a 3+
kW DC coupled array, the new array is close to 200' away, and it would take
2 more charge controllers of any of high voltage ones for this size array.
Are there any battery based inverters that folks have had decent l
I do not recommend AC coupling for off grid, except to offset daytime
loads or to add PV at remote buildings. Besides coupling errors like
you're experiencing, the entire system will shut down and not recharge,
if the VFX inverters shut down. With a DC coupled array, the batteries
can rechar
sorry, prematurely emailed previous post:
I'm wondering if the VFXs are just not capable of putting out clean enough
power in order to hold the SE HD inverter. I had it operating on this same
system for a couple of hours with not this problem. Is it likely that this
inverter combo is not going to
I have used SolarEdge to AC couple a smaller Array in the past, with no
issues. I recently added a fairly significant array (6.2k DC via a SE6K
(setap) inverter in an off-grid home which has had a dual stack VFX3648 for
many years. I also added 32kWh of Blue Ion batteries replacing an 80kWh
older
707-923-2001 ext. 100
>>
>> 1150 #1 Evergreen Rd
>>
>> Redway, CA 95560
>>
>> www.greenwired.com
>>
>> [image: Description: signature]
>>
>>
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wre
w.greenwired.com
>
> [image: Description: signature]
>
>
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Howard Arey
> *Sent:* Wednesday, July 24, 2019 7:37 AM
> *To:* 'RE-wrenches'
> *Subject
g] On
Behalf Of Howard Arey
Sent: Wednesday, July 24, 2019 7:37 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] SolarEdge reliability declining...???
Have any of you seen significant declines in SolarEdge inverter reliability?
We are having more inverter failures that at any time in the pas
Have any of you seen significant declines in SolarEdge inverter reliability?
We are having more inverter failures that at any time in the past five years
of installing SolarEdge. Lots of Code 181 hardware failures mostly in the
latest SetApp inverters (the ones without displays.)
To compound matt
Tom - I was just asking a SunPower rep about this. My understanding is that
a PID (Potential Induced Degredation) discharge device is required to use
SunPower positively grounded modules with a transformerless inverter. These
are expensive and not listed for the US market. Long story short, I don't
I have a Postive grounded SunPower System with two private labeled SMA 6000
watt Inverters installed in 2009 and want to use SolarEdge 7600 and their
optimizers at least for half the array ? Modules are SunPower 210 watt
modules - how do I work this out ? GatorTom PS : 48 modules ground mounted
i
Does anyone have a dealer only phone number to reach SolarEdge tech support?
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
___
List spon
Yes, correct on both. The generator support is there, I did not use it.
On Fri, Jun 17, 2016 at 3:07 PM, Carl Adams wrote:
> Chris,
>
> Nice finish on the Sonnen install. It looks fabulous. My understanding
> is the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
> radian.
Chris,
Nice finish on the Sonnen install. It looks fabulous. My understanding is
the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
radian. I assume generator support is fully supported
On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason
wrote:
> I promised a picture of the So
I promised a picture of the Sonnen installation. As these units are getting
close to being appliances in the same vein as home audio, we wanted to have
a clean finish so we made some mill work to complete the top of the unit to
the ceiling and hide the ugly conduits.
https://www.dropbox.com/s/vlh0u
Dunno exactly, Carl.
Twas not I who installed it.
marco
Marco,
Are the two switch gear boxes integral to the installation. If so can you give
me an idea of what their function/purpose is?
On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf wrote:
Provides an idea of size and scale
Marco,
Are the two switch gear boxes integral to the installation. If so can you
give me an idea of what their function/purpose is?
On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf
wrote:
> Provides an idea of size and scale.
>
> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>
>
>
>>> Best regards,
>>>
>>> Lloyd
>>>
>>>
>>>
>>> Lloyd Hoffstatter
>>>
>>> M.S. in Applied Solar Energy
>>>
>>> NABCEP Solar PV Installer #102503-23
>>>
>>>
>
Marco Mangelsdorf
Sent: Monday, June 13, 2016 11:43 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
Yes, Howie…their SE StorEdge.
Not my install. Sunrun did it on Oahu. Did a big press whoopdeedo and even
got the governor of Hawaii and mayor of Ho
enches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
I would love to hear more about that install. Design, sense of equipment
quality and development (is programming and function well thought out and
implemented), availability, pictures, etc. are all significant questions.
Thanks f
loyd Hoffstatter
>>
>> M.S. in Applied Solar Energy
>>
>> NABCEP Solar PV Installer #102503-23
>>
>>
>>
>> Director
>>
>> Sunstruck Consulting
>>
>> ll...@sunstruckconsulting.com
>>
>> 845-657-8132
>>
>>
>>
>>
ter
>
> M.S. in Applied Solar Energy
>
> NABCEP Solar PV Installer #102503-23
>
>
>
> Director
>
> Sunstruck Consulting
>
> ll...@sunstruckconsulting.com
>
> 845-657-8132
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wren
RE-wrenches'
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
Yes, Howie…their SE StorEdge.
Not my install. Sunrun did it on Oahu. Did a big press whoopdeedo and even
got the governor of Hawaii and mayor of Honolulu to attend.
marco
From: RE-wrenches [mailto:re-wrenches-
: Monday, June 13, 2016 4:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your access
to the StorEdge?
Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun
Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your
access to the StorEdge?
Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Ju
Provides an idea of size and scale.
Tesla Battery system Aalto residence2. 6 may 2016
>From left to right-disconnect, kWh meter, SolarEdge 7600, switch gear, two
Tesla Powerwalls.
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Howie,
Thanks for your response. I would agree that we have not seen this problem
with systems installed after 2012. The technology has improved, and the
Comm card in the inverter has been thru several iterations since then. I
would also agree that SE has improved on their tech support respons
Carl,
We experienced a rash of Comm Card issues with several SE installs over
several years, but none exactly as you describe. Our issues were almost
all resolved with a board replacement, but a few were particularly vexing
with many return service calls to get a resolution. We seemed to have th
Hello Wrenches,
Anyone experiencing issues with comm card failures on SolarEdge inverters?
We have some systems installed in 2012 exhibiting similar behaviors. The
systems are producing data, it is registering on the inverter, and our
independent utilty meter, but is not reported to the SolarEdg
Kirk:
And a PR nightmare for integrators. The customer will be very disappointed
that you have to charge at least several times the cost of the battery pack to
make it provide back-up power. The overly rosy picture painted is a disservice
to the industry.
On a related note: It is 201
t: Monday, June 29, 2015 2:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Solaredge Storedge
I would think that Solar City would know all about this.
Or, maybe I wouldn't ?
boB
On 6/29/2015 11:06 AM, Rebekah Hren wrote:
I don't have any info, but the StorEdge diagram is con
RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *b...@midnitesolar.com
> *Sent:* Monday, June 29, 2015 2:56 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Solaredge
Just to add a little perspective on the development of inverter based
storage, I have just attended InterSolar Europe in Munich. Every inverter
manufacturer is showing some type of add-on battery storage system.
SolarEdge was huge, they had the largest visibility of the inverter
manufacturers.
The
cant
VT RE Incentive Program Partner
802.863.1202
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of b...@midnitesolar.com
Sent: Monday, June 29, 2015 2:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Solaredge Storedge
I would think that Solar City would know
On
Behalf Of b...@midnitesolar.com
Sent: Monday, June 29, 2015 2:56 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Solaredge Storedge
I would think that Solar City would know all about this.
Or, maybe I wouldn't ?
boB
On 6/29/2015 11:06 AM, Rebekah Hren wrote:
I don't have any info, bu
I would think that Solar City would know all about this.
Or, maybe I wouldn't ?
boB
On 6/29/2015 11:06 AM, Rebekah Hren wrote:
I don't have any info, but the StorEdge diagram is confusing to me
when it says "energy independence." I can see a simple compatibility
between the Powerwall DC vo
I don't have any info, but the StorEdge diagram is confusing to me when it
says "energy independence." I can see a simple compatibility between the
Powerwall DC voltage (300 to 400VDC) and the SolarEdge operating voltage,
~350VDC, and I can also see how this setup could be used to maximize
self-con
Hello,
Anyone have detailed info on the Storedge battery-compatible system from
Solaredge? I only found a brochure on their website. Apparently batteries
can be added to a new or existing Solaredge inverter (the brochure says they
have partnered with Tesla's Powerwall) for backup power. They call
Anyone heard any issues with SolarEdge optimizers not being encapsulated
and corroding in salt water climates?
Or overheating?
What do you know about SolarEdge as a product?
--
Stay Energized, PEACE>
Aur J Beck,
NABCEP Certified Solar PV Installer™ 032611-24
NABCEP Certified PV Technical Sales™
Hi Tom,
I might be missing your question, but I believe that you would couple the
SolarEdge inverter to the AC1 line of the Sunny Island, just like with any
grid tie inverter. In other words, the SolarEdge inverter would tie into
the critical loads panel that is fed by the Sunny Island.
Best, Aug
Does anyone have a diagram on how to AC couple SolarEdge Inverters that use the
DC Optimizers to AC coupling with a Sunny Island like SMA 6048 . John Berdner
started a link quite a while ago that I do not think included a diagram . John
did mention that the SMA had the correct or best Algorithm
.
Personally, I think an "interlock" on a string system is a reasonable request,
and likely to appear in future models from different manufacturers. It's just
going to take time.
Dan
On Fri, 2/14/14, Chris Mason wrote:
Subject: Re: [RE
The "Door Open" switch is a very useful feature. I am trying to get Fronius
to put a digital shutdown terminal on its CL line of inverters, or all
inverters preferably. We need to pressure all the inverter manufacturers to
provide a logic in or dry contact method of shutdown.
Most ATS will provide
I have done systems in Hawaii, here is one with a 30 k PV system and with a
250k Cummins back up genny. We have a contactor in the ATS that will open
if the genny is operating, this in turn sends a door open signal to the
Satcon shutting it down I don't want anything effecting the genset
operation
That's total nonsense. Most of our installs involve a generator, as
generators are very common here due to intermittent electrical supply and
hurricanes. We also sell and install generators and I am a tech.
A decent heavy generator will produce electricity that will fall within the
IEEE 1547 specif
Hello,
I recently posed the question to Solaredge tech support, wondering if their
inverter, in this case a 20kw 480 3-phase, would have any issues if it were
connected to an AC panel backed up by a generator. They told me no problem,
for the inverter's anti-islanding will work if it sees the "
Hello,
Has anyone on list installed a Solaredge 480/227 3-phase inverter? The spec
sheet says that the nominal input DC+ to DC- is 840vdc. I assume this is the
regulated operational voltage, and so the system installation falls under
the code rules for 1000vdc systems, correct? My local utility
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge Optimizer - Was: Tigo and SMA AFCI - Was:
AC coupled, grid-tied Sunny Island - contactor & bypass
SolarEdge makes an optimizer / inverter system. We just installed one. Our
clients are happy. So are we.
Don't know if you can AC couple the
SolarEdge makes an optimizer / inverter system. We just installed one. Our
clients are happy. So are we.
Don't know if you can AC couple the inverter. Their website says they are about
to release a version of the optimizer that will work with other manufacturer's
inverters.
Dick Ratico
Solarwind
94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk Herander
Sent: Tuesday, February 26, 2013 8:04 AM
To: 'RE-wrenches'
Subject: Re: [RE-wr
ent: Wednesday, December 19, 2012 1:35 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Solaredge AC-coupling
Kirk:
We have a new version of firmware (in production January 1, 2013) that
supports frequency shift power control, e.g. Sunny Island.
I am preparing a white paper on how to set it up bu
te of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk Herander
Sent: Tuesday, December 18, 2012 1:16 PM
To: RE-wrenches
Subject: [RE-wrenches] Solaredge AC-coupling
Hello,
Anyone ou
Hello,
Anyone out successfully AC-coupled a Solaredge inverter with an Outback or
other battery-based inverter? Thanks. I may want to do it for an upcoming
job.
Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified Inaugural Certificant
NYSERDA-eligible Installer
PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge v Enphase
Wrenches,
I wish this urban myth about electrolytic capacitors would
die, but it won't. It's been a wonderful marketing ploy for
some time now.
Simply stated, existence of electrolytic capacitors in inverters
does NOT me
obile: +530.392.0356
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of conrad geyser
Sent: Thursday, January 12, 2012 1:30 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] SolarEdge v Enphase
Andrew,
We installed a Solar Edge sys