[RE-wrenches] Supply Side Tap Overcurrent Protection

2010-10-07 Thread Peter Parrish
Bill and others. I don’t remember what type fuses are needed in conjunction with the AC disconnect. - Peter Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP Cert. 031806-26 peter.parr...@calsolareng.com Ph

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-04-01 Thread Hans Frederickson
Behalf Of Ryan LeBlanc Sent: Wednesday, March 31, 2010 4:29 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Steven, A Line Side Tap, by nature, allows us 100% of the Service Entrance Conductor Ampacity. This typically ~equals Main Breaker r

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-04-01 Thread Richard L Ratico
Seconded! AMEN. Dick Ratico Solarwind Electric --- You wrote: Steven, A Line Side Tap, by nature, allows us 100% of the Service Entrance Conductor Ampacity. This typically ~equals Main Breaker rating, but is regardless of the Main Breaker rating or size of Loads, it's about the conductor. NEC

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Ryan LeBlanc
rom the backup load panel. Steven Lawrence __ Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT) From: Nick Soleil To: RE-wrenches Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Message-ID: <342120.66732...@web44904.mail.sp1.yahoo.com> Content-Type: text/plain; ch

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
n a client. Steven Lawrence Date: Wed, 31 Mar 2010 11:39:32 -0700 From: "Hans Frederickson" To: "'RE-wrenches'" Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Message-ID: <3ee2af007f5d4ebe96831c2254b5e...@frederickson.local> Content-Type: t

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread August Goers
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil Sent: Wednesday, March 31, 2010 12:15 PM To: RE-wrenches Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection I feel confident that the load will not be over 80 Amps at any time, and therefore do not think

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Nick Soleil
Sent: Wed, March 31, 2010 9:19:48 AM Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection We recommend to the customer to upgrade their service if it’s not adequate (old/outdated/too small). In the grand scheme of things, that’s a small add-on. Whenever there’s a questionable in

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Hans Frederickson
wrenches-boun...@lists.re-wrenches.org] On Behalf Of Steven Lawrence Sent: Wednesday, March 31, 2010 11:04 AM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection 230.80 "Where the service disconnecting means consists of more than one switch or

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
n Lawrence ___ Message: 1 Date: Wed, 31 Mar 2010 10:24:17 -0700 From: "Hans Frederickson" To: "'RE-wrenches'" Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Message-ID: <71328cbb96b745889f63e627c93e8...@frederickson.local> Content-Type: text/

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Hans Frederickson
f Of Steven Lawrence Sent: Wednesday, March 31, 2010 9:54 AM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Why can't you do a line side tap and downsize the main breaker? Use a 60A main disconnect for the line side tap, and use a 60A mai

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
n the main service panel that can be fed from the backup load panel. Steven Lawrence __ Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT) From: Nick Soleil To: RE-wrenches Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Eric Andrews
-9037 _ From: Eric Andrews To: RE-wrenches Sent: Tue, March 30, 2010 10:25:45 AM Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Nick- Just downsize the main breaker. For example, a 200 amp panel w/ a 200 amp main breaker could be reduced to a 150 amp main breake

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Nick Soleil
Office: 707-789-9537 Fax:707-769-9037 From: Eric Andrews To: RE-wrenches Sent: Tue, March 30, 2010 10:25:45 AM Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Nick- Just downsize the main breaker. For example, a 200 amp panel w/ a 200

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-30 Thread Eric Andrews
Nick- Just downsize the main breaker. For example, a 200 amp panel w/ a 200 amp main breaker could be reduced to a 150 amp main breaker to allow for more solar to be connected. You need to calculate for the 120% rule. Eric R. Andrews NABCEP Certified PV Installer _

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-30 Thread Nick Soleil
, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax:707-769-9037 From: Bill Brooks To: RE-wrenches Sent: Sun, March 28, 2010 10:04:22 PM Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Dave, All line side connections must have

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-29 Thread August Goers
ches-boun...@lists.re-wrenches.org] On Behalf Of Dave Palumbo Sent: Sunday, March 28, 2010 10:53 AM To: 'Wrench List' Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Wrenches, I am tasked with reviewing an installation by a licensed electrician in Vermont and would like help

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-29 Thread Dave Click
Looks like your question is answered but something else to look out for- this is pretty straight-forward for batteryless systems but for battery-backup and a line-side tie, you're adding a big load to the service conductors for battery charging and pass-through current to critical loads. If you

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Bill Brooks
Behalf Of Dave Palumbo Sent: Sunday, March 28, 2010 10:53 AM To: 'Wrench List' Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Wrenches, I am tasked with reviewing an installation by a licensed electrician in Vermont and would like help with the following:

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Darryl Thayer
I have always thought it was the same calculation as the Fault current as calculated in NFPA 70E.  but I will ask some one whom I respect. Darryl --- On Sun, 3/28/10, R Ray Walters wrote: From: R Ray Walters Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection To: "RE-wre

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Darryl Thayer
rvice to Overcurrent protection. Darryl --- On Sun, 3/28/10, Scott McCalmont wrote: > From: Scott McCalmont > Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection > To: "RE-wrenches" > Date: Sunday, March 28, 2010, 9:22 PM > I would add the following NEC article

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread R Ray Walters
This brings up a related question, that I can't seem to find an NEC answer to: How do we calculate the available fault current, for picking our AIC rating? I used to always throw 20,000 amps AIC rating fuses and breakers for large battery banks, but on grid, it seems we would have to know things

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Scott McCalmont
I would add the following NEC article relevant to services: 230.91 Location. The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto. Fifteen feet isn't "immediately adjacent." Regards, Scott Scott McCalmont, P

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Bob-O Schultze
Dave, OK, here's my shot at this. Your mileage may vary. I think 240.86(A) applies here. Unless the CB in the Xantrex XW has a higher interrupt ratting (AIC) than the available fault current from that supply side tap and the CB is so marked (240.83(C), a disconnect using appropriate current limi

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Dave Palumbo
Wrenches, I am tasked with reviewing an installation by a licensed electrician in Vermont and would like help with the following: Grid-tied PV system with battery back-up. AC point of connection is a supply side tap (done on customer side of utility meter ) then traveling 5 feet of #2 THHWN