2010-08-21 Thread dan
-wrenches] Voltage discrepancy From: boB Gudgel b...@midnitesolar.com Date: Thu, August 19, 2010 8:09 pm To: RE-wrenches re-wrenches@lists.re-wrenches.org Jeff Oldham wrote: I have seen this on my last 3 MX60 controllers and it is very frustrating and looks to be a design flaw. I can calibrate

Re: [RE-wrenches] Voltage discrepancy

2010-08-21 Thread Darryl Thayer
Bob you know the architecture of the MX60 is it a design problem or is it a component problem, I have not noticed this problem in older MX60s but I was not looking for it either. I have been able to adjust the meter and I typically would not check it again. I use my meter and adjust the MX60

Re: [RE-wrenches] Voltage discrepancy

2010-08-20 Thread Exeltech
Wire gauge isn't the only consideration.  Check all crimps and connections in the DC path.  A bad one can cause more drop than the wire. Dan --- On Fri, 8/20/10, Jeff Oldham starpowe...@juno.com wrote: From: Jeff Oldham starpowe...@juno.com Subject: Re: [RE-wrenches] Voltage discrepancy

Re: [RE-wrenches] Voltage discrepancy

2010-08-20 Thread Drake Chamberlin
Correction: it is number 6 to the charge control, and 3/0 or 4/0 to the batteries. At 09:40 AM 8/20/2010, you wrote: boB, It looks like 3/0 or 4/0. It is a short run. At 08:09 PM 8/19/2010, you wrote: Jeff Oldham wrote: I have seen this on my last 3 MX60 controllers and it is very

Re: [RE-wrenches] Voltage discrepancy

2010-08-19 Thread Jeff Oldham
I have seen this on my last 3 MX60 controllers and it is very frustrating and looks to be a design flaw. I can calibrate the meters to be accurate at either the Absorb point OR the Float point but NOT both!! Not only that but the meter calibrations tend to drift a bit in just a matter of days,

Re: [RE-wrenches] Voltage discrepancy

2010-08-19 Thread boB Gudgel
Jeff Oldham wrote: I have seen this on my last 3 MX60 controllers and it is very frustrating and looks to be a design flaw. I can calibrate the meters to be accurate at either the Absorb point OR the Float point but NOT both!! Not only that but the meter calibrations tend to drift a bit in

Re: [RE-wrenches] Voltage discrepancy

2010-08-19 Thread Drake Chamberlin
Thanks Jeff, That could be the explanation. Outback has metering issues with the Mate too. When I talked to a tech support about he fact that the Mate on my system seemed woefully inaccurate, she chuckled and affirmed that the were pretty approximate. -Drake At 07:12 PM 8/19/2010, you

Re: [RE-wrenches] Voltage discrepancy

2010-08-15 Thread Richard L Ratico
Drake, --- You wrote: I called her back just now, and the voltage readings on the Mate, MX and Trimetric all match. Humm. The batteries are 4, 4 1/2 year old, U.S. Battery L-16s wired in 24 volt configuration. It seems that I remember postings of Wrenches having problems with these

[RE-wrenches] Voltage discrepancy

2010-08-14 Thread Drake Chamberlin
Hello Wrenches, I just got off the phone with an off grid system owner who has a voltage discrepancy showing between the reading on her MX-60 and both her Mate and Trimetric meter. The MX-60 shows 28.8 V and the Trimetric and the Mate both show around 25 volts. The batteries are using a

Re: [RE-wrenches] Voltage discrepancy

2010-08-14 Thread Allan Sindelar
Drake, I'd start by having her disconnect the temp sensor. If it has failed, it can cause false voltage compensation. However, if the MX60 is reading higher than actual, as your post suggests, I would more expect it to regulate sooner, thus leading to less