Re: [RE-wrenches] Outback Radian transfer time

2022-02-04 Thread jay
HI Eric, Check that the transfer delay is as short as it can go, about 6 cycles You might raise the lower voltage limit from 108 Check to make sure all the voltage readings on each inverter are as close as possible. A real weakness of the OB platform is that you have to calibrate each item:

Re: [RE-wrenches] Outback Radian transfer time

2022-02-04 Thread Howie Michaelson
Not sure about the radians (I've rarely used them) but with the VFX series, that symptom can sometimes be avoided by programming a cool down period so that the inverters drop the generator while it is still running at full speed. Alternatively, by narrowing the generator voltage window at the