Re: [RE-wrenches] small wind generators

2012-04-11 Thread Hugh Piggott
Interesting thread!

We are having some success with a Kestrel turbine here on Scoraig

I second the idea that Ampair offer a modest but very robust range of products 
for high wind sites.

cheers


Hugh Piggott

On 3 Apr 2012, at 20:36, Richard L Ratico wrote:

 Does anyone have any experience with Kestrel Wind Turbines?
 
 Dick Ratico
 Solarwind Electric
 
 
 --- You wrote:
 SWWP has changed their turbines again. They are now called the the Air 30, Air
 40 and Air Breeze. The 30 is like the old X land, the 40 is like the old 
 Breeze
 Land and the Breeze is like the old Breeze Marine. The Breeze is the only 
 marine
 model available. Confusing enough? The 40 and Breeze have a limited lifetime
 warranty and all have a new, higher price. 
 
 Historically the Air products have lasted fairly well and been moderate
 performers. Air X and Air Breeze parts are still available but SWWP has
 discontinued support for all other models. We service, sell and recommend them
 for small PV/wind hybrid systems. AND...they are still USA made! Hurrah!
 
 Larry Crutcher
 Starlight Solar Power Systems
 (928) 342-9103
 
 On Apr 3, 2012, at 7:04 AM, Roy Butler wrote:
 
 Hi Drake,
 
 The Air 403/ Air-X/ Air Breeze/ whatever it's name is now, is fairly 
 dependable.
 In most wind regimes it's the equivalent of a 10 or 20 watt solar module but
 seems to work just fine. FYI- it's ~ 200 watts or so.
 
 It's not the quietest thing though, being a fairly high rpm turbine.
 
 But the Sunforce 600 is not a 600. The rotor diameter tells the truth, making 
 it
 somewhere around a 200 - 250 watt machine. Perhaps they have the bugs worked
 out but when they first came out, there were many reliability and performance
 issues.
 
 What's the application for this?
 Roy Butler
 --- end of quote ---
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Grid tied PV to subpanel on detached garage?

2012-04-11 Thread Aladdin Solar
Wrenches:

There's probably an obvious answer but please help me think this through. 
Here's the situation--comes up all the time: The PV array and grid-tied 
inverter will be located on a detached building (garage or pole barn, etc.). 
The existing power to the building is a 240V 60A subpanel connected to the main 
panelboard at the house or main building via buried cable. If we obey buss bar 
loading and wire sizing, etc, is there any reason why we can't or shouldn't 
install the small grid tied PV system and tie it into the garage subpanel 
instead of trenching new lines back to the house and hit the main panel there? 
One hitch I see is that if we want a PV system AC disconnect near the main 
meter, the whole garage would end up on that. Have I overlooked an NEC or 
inverter requirement?

Thanks for your comments.

Charlie Pickard
Aladdin Solar


__ Information from ESET NOD32 Antivirus, version of virus signature 
database 7045 (20120411) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tied PV to subpanel on detached garage?

2012-04-11 Thread Mark Frye

1 - What is the AC output rating of the PV inverter?
2 - What is the size of the feeder conductors?
3 - Does the sub panel at the garage have a main breaker of it's own?
4 - Does your AHJ or utility require anAC disconnect or not?

Mark Frye
Berkeley Solar Electric Systems



On 4/11/2012 7:09 AM, Aladdin Solar wrote:

Wrenches:
There's probably an obvious answer but please help me think this 
through. Here's the situation--comes up all the time: The PV array and 
grid-tied inverter will be located on a detached building (garage or 
pole barn, etc.). The existing power to the building is a 240V 60A 
subpanel connected to the main panelboard at the house or main 
building via buried cable. If we obey buss bar loading and wire 
sizing, etc, is there any reason why we can't or shouldn't install the 
small grid tied PV system and tie it into the garage subpanel instead 
of trenching new lines back to the house and hit the main panel 
there? One hitch I see is that if we want a PV system AC disconnect 
near the main meter, the whole garage would end up on that. Have 
I overlooked an NEC or inverter requirement?

Thanks for your comments.
Charlie Pickard
Aladdin Solar


__ Information from ESET NOD32 Antivirus, version of virus 
signature database 7045 (20120411) __


The message was checked by ESET NOD32 Antivirus.

http://www.eset.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tied PV to subpanel on detached garage?

2012-04-11 Thread Brian Mehalic
Well the size of the subpanel sounds like a limiting factor, unless you
find someway  around that via a bus/breaker size difference or upgrading to
something larger.  And the AHJ/utility may want the PV disconnect by the
main as you mentioned. However, 705.12(7) allows connecting to panelboards
connected in series; and additional labeling requirements in 690.54 and
690.56(B) would apply if the PV system disconnecting means is not located
with the service disconnecting means.

On Wed, Apr 11, 2012 at 10:09 AM, Aladdin Solar
cpick...@aladdinsolar.comwrote:

 **
 Wrenches:

 There's probably an obvious answer but please help me think this through.
 Here's the situation--comes up all the time: The PV array and grid-tied
 inverter will be located on a detached building (garage or pole barn,
 etc.). The existing power to the building is a 240V 60A subpanel connected
 to the main panelboard at the house or main building via buried cable. If
 we obey buss bar loading and wire sizing, etc, is there any reason why we
 can't or shouldn't install the small grid tied PV system and tie it into
 the garage subpanel instead of trenching new lines back to the house and
 hit the main panel there? One hitch I see is that if we want a PV system AC
 disconnect near the main meter, the whole garage would end up on that. Have
 I overlooked an NEC or inverter requirement?

 Thanks for your comments.

 Charlie Pickard
 Aladdin Solar


 __ Information from ESET NOD32 Antivirus, version of virus
 signature database 7045 (20120411) __

 The message was checked by ESET NOD32 Antivirus.

 http://www.eset.com

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 

Brian Mehalic
NABCEP Certified Solar PV Installerâ„¢ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132
PV Curriculum Developer and Instructor
Solar Energy International
Carbondale, CO 81623
http://www.solarenergy.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tied PV to subpanel on detached garage?

2012-04-11 Thread Mark Frye

Also,

Was a ground conductor run with the feeder?

Mark Frye

On 4/11/2012 7:09 AM, Aladdin Solar wrote:

Wrenches:
There's probably an obvious answer but please help me think this 
through. Here's the situation--comes up all the time: The PV array and 
grid-tied inverter will be located on a detached building (garage or 
pole barn, etc.). The existing power to the building is a 240V 60A 
subpanel connected to the main panelboard at the house or main 
building via buried cable. If we obey buss bar loading and wire 
sizing, etc, is there any reason why we can't or shouldn't install the 
small grid tied PV system and tie it into the garage subpanel instead 
of trenching new lines back to the house and hit the main panel 
there? One hitch I see is that if we want a PV system AC disconnect 
near the main meter, the whole garage would end up on that. Have 
I overlooked an NEC or inverter requirement?

Thanks for your comments.
Charlie Pickard
Aladdin Solar


__ Information from ESET NOD32 Antivirus, version of virus 
signature database 7045 (20120411) __


The message was checked by ESET NOD32 Antivirus.

http://www.eset.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tied PV to subpanel on detached garage?

2012-04-11 Thread Aladdin Solar
I meant the question largely to be a generic one but I can give you an example:

Buried conductors are 6AWG. No additional grounding conductor exists between 
the main and detached building. As Brian Mehalic already responded, the 60A 
subpanel would tough to deal with for inverter sizing. Assume the AC disconnect 
is required near the main meter and so would have to disconnect all circuits in 
the subpanel.

So say we put a 50A main breaker in the 60A subpanel to allow a Fronius IG 3.0 
(3000 watt) and a string of 12 Sharp ND240s or similar.

The PV ground would have to hit a ground rod at the garage and a grounding 
conductor would need to be buried back for bonding at the main building--right?
 
  - Original Message - 
  From: Mark Frye 
  To: RE-wrenches 
  Sent: Wednesday, April 11, 2012 9:25 AM
  Subject: Re: [RE-wrenches] Grid tied PV to subpanel on detached garage?


  1 - What is the AC output rating of the PV inverter?
  2 - What is the size of the feeder conductors?
  3 - Does the sub panel at the garage have a main breaker of it's own?
  4 - Does your AHJ or utility require anAC disconnect or not?

  Mark Frye
  Berkeley Solar Electric Systems



  On 4/11/2012 7:09 AM, Aladdin Solar wrote: 
Wrenches:

There's probably an obvious answer but please help me think this through. 
Here's the situation--comes up all the time: The PV array and grid-tied 
inverter will be located on a detached building (garage or pole barn, etc.). 
The existing power to the building is a 240V 60A subpanel connected to the main 
panelboard at the house or main building via buried cable. If we obey buss bar 
loading and wire sizing, etc, is there any reason why we can't or shouldn't 
install the small grid tied PV system and tie it into the garage subpanel 
instead of trenching new lines back to the house and hit the main panel there? 
One hitch I see is that if we want a PV system AC disconnect near the main 
meter, the whole garage would end up on that. Have I overlooked an NEC or 
inverter requirement?

Thanks for your comments.

Charlie Pickard
Aladdin Solar


__ Information from ESET NOD32 Antivirus, version of virus 
signature database 7045 (20120411) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



  __ Information from ESET NOD32 Antivirus, version of virus signature 
database 7045 (20120411) __

  The message was checked by ESET NOD32 Antivirus.

  http://www.eset.com



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org




  __ Information from ESET NOD32 Antivirus, version of virus signature 
database 7045 (20120411) __

  The message was checked by ESET NOD32 Antivirus.

  http://www.eset.com




__ Information from ESET NOD32 Antivirus, version of virus signature 
database 7045 (20120411) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Helios Modules

2012-04-11 Thread Kristopher Schmid
Dick,

I assume that you are referring to Helios, USA out of Milwaukee, WI.
I put in about 12kW last year with no issues.  They seem like a good
solid product.  I try to use them whenever i can since they are an
in-state manufacturer for me.

Kris

On Tue, Apr 10, 2012 at 8:01 PM, Richard L Ratico
richard.l.rat...@valley.net wrote:
 Wrenches,

 Does anyone have experience with Helios Modules they wish to share?
 Thanks,

 Dick Ratico
 Solarwind Electric
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




-- 
Shine On!

Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installer
BSEE
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Helios Modules

2012-04-11 Thread Tom Duffy
Dick

We have been a distributor for these modules for more than a half a year. They 
are a first class, well-made module and they are a good company to work with

Kind Regards

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
t...@thesolar.biz
For: Customer Service and Accounting 888-895-6810  Grid tie sales 888-895-7847 
Off Grid sales 888-895-7765 Other Product Sales 888-895-9612 
Shipping and Receiving 888-895-6497 Tech Support 888-895-8179

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Richard L Ratico
Sent: Tuesday, April 10, 2012 7:02 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Helios Modules

Wrenches,

Does anyone have experience with Helios Modules they wish to share?
Thanks,

Dick Ratico 
Solarwind Electric
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] small wind generators

2012-04-11 Thread b...@midnitesolar.com



We are also hearing very good reports of longevity with Kestrel's too.

For instance, there is one (110) in Hawaii that has been running with a
Classic without any trouble for about 3 years now.

boB



On 4/11/2012 3:08 AM, Hugh Piggott wrote:

Interesting thread!

We are having some success with a Kestrel turbine here on Scoraig 
http://scoraigwind.co.uk/?s=kestrel


I second the idea that Ampair offer a modest but very robust range of 
products for high wind sites.


cheers


Hugh Piggott




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tied PV to subpanel on detached garage?

2012-04-11 Thread Mark Frye
Not necessarily. NEC 2008, 250.32 (B), Exception allows you to use the 
neutral conductor for existing structure so long as several requirements 
are met.


Check it out.

On 4/11/2012 8:41 AM, Aladdin Solar wrote:
I meant the question largely to be a generic one but I can give you an 
example:
Buried conductors are 6AWG. No additional grounding conductor exists 
between the main and detached building. As Brian Mehalic already 
responded, the 60A subpanel would tough to deal with for inverter 
sizing. Assume the AC disconnect is required near the main meter and 
so would have to disconnect all circuits in the subpanel.
So say we put a 50A main breaker in the 60A subpanel to allow a 
Fronius IG 3.0 (3000 watt) and a string of 12 Sharp ND240s or similar.
The PV ground would have to hit a ground rod at the garage and a 
grounding conductor would need to be buried back for bonding at the 
main building--right?
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org