Re: [RE-wrenches] De-Sulphators. The last word?

2012-06-01 Thread Tom Duffy
I have to agree with Larry… a properly sized, designed and charged series 
battery bank does not need “magic elixir” and if you add it to an old poorly 
designed bank it still will be poorly designed, even if you could fix the hard 
sulphation the problem would re-appear. I have never seen this stuff work 
however in my 45 years in the battery business.

Kind Regards

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
t...@thesolar.biz
For: Customer Service and Accounting 888-895-6810  Grid tie sales 888-895-7847
Off Grid sales 888-895-7765 Other Product Sales 888-895-9612
Shipping and Receiving 888-895-6497 Tech Support 888-895-8179

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Dorsett
Sent: Monday, May 28, 2012 3:16 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] De-Sulphators. The last word?

If this is a fancy name for EDTA, perhaps 10 years ago I went through virtually 
all of the previous 15 years of Chemical Abstracts to see if there were ANY 
reference to its working. And while there were hundreds of scholarly abstracts 
on lead acid chemistry, there was only 1 that mentioned EDTA and that was a 
mixed review and attributed any benefit to the ion with which EDTA was combined 
as a salt. Like desulfators, there may be anecdotal hearsay, but little science.

Bill Dorsett
Sunwrights
Manhattan, KS

From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Jonathan Hill
Sent: Monday, May 28, 2012 12:33 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] De-Sulphators. The last word?

Try Thermoil deslphator additive. Has good reviews. We are selling it.

Jon Hill
Sierra Solar Systems

On May 28, 2012, at 7:17 PM, Larry Crutcher, Starlight Solar Power 
Systemsla...@starlightsolar.commailto:la...@starlightsolar.com wrote:
Dan,

I'm perplexed. Where was anything mentioned about de-sulphators? Where was 
anyone slammed? What in the world are you talking about? Perhaps you meant to 
reply to someone else's thread. BTW, I do not recommend a desulfator or pulser 
be installed on batteries.

I'll reiterate my points:
1. KC-120's from a certain production era fail and can be warranted.
2. Applying enough load will cause full current to flow from a PV array.
3. Sulfated batteries have high resistance causing a quick rise in voltage.

I welcome your response but please reply off list.

Respectfully yours,

Larry

On May 28, 2012, at 6:42 AM, 
d...@foxfire-energy.commailto:d...@foxfire-energy.com 
d...@foxfire-energy.commailto:d...@foxfire-energy.com wrote:

Seems I have a stalwart Battery Specialist in the neighborhood still 
convincing folks that de sulphators are the smartest thing since sliced bread 
(And slamming anyone who disagrees). In my experience, sparklers have little to 
no effect on battery longevity and in most cases add unlisted, hazardous and 
unnecessary wiring devices to a potentially hazardous environment. Is tar and 
feathering still an acceptable means of dispute resolution.. or am I totally 
missing something? tks db

Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.comhttp://www.Foxfire-Energy.com/
NABCEP #092907-44

 Original Message 
Subject: Re: [RE-wrenches] Troubleshooting Off-grid PV
From: Larry Crutcher, Starlight Solar Power Systems
la...@starlightsolar.commailto:la...@starlightsolar.com
Date: Sun, May 27, 2012 7:37 pm
To: RE-wrenches 
re-wrenches@lists.re-wrenches.orgmailto:re-wrenches@lists.re-wrenches.org

Hi Eric,

Check the dates on the KC-120 module label. If any were manufactured between 
January 1999 and December 2002, they have or will fail. We have been replacing 
these modules for over 8 years now. There was a defective solder joint during 
manufacture. Kyocera will still replace them under warranty even though they 
have no legal requirement to do so. They will ship you remanufactured 120's and 
pay for return shipping. Contact Kyocera about the procedure.

If the batteries are sulfated, they will not produce the load necessary to 
drive the current high. Capacity has nothing to do with it; internal resistance 
does. You can test the array by pulling the voltage down (turn on some big 
loads) at solar noon. This will force the controller into bulk and reveal the 
maximum current the array can produce. I think you have two problems here. With 
bad modules, you may not see much.

It is typical for a controller to transition to float very early in the charge 
cycle if the battery is sulfated. Look for a fast rise in voltage in the 
morning. This is an indicator of sulfated battery. A healthy battery will 
slowly climb in voltage.

Let me k now if you need more understanding about batteries, charging and why 
MOST of them never see old age. It's my speciality.

Larry Crutcher

[RE-wrenches] C100 controller repair

2012-06-01 Thread All Solar, Inc.
Wrenches,
Anyone know how to contact John Klima, past COSEIA president.  I had used his 
services in the past to repair an old C100 Diff. Controller.

Thanks in advance!

Jeremy,

All Solar, Inc.
Jeremy and Amy Rodriguez
1463 M St
Penrose, CO 81240
www.asolarelectric.com
Phone 719-372-3808
Fax 719-372-3804
Email allso...@scswifi.net
Email allso...@live.com___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling

2012-06-01 Thread Steve Higgins
Dana,

Please contact me off list and I'll get you a couple of drawings...

They are too big for the list.

If anyone else wants them I'll send them to you to.

Also keep and eye on Solar Pro, we just finished a good article on ac coupling.

Steve Higgins
Sales Application Engineering Mgr
African Business Development Mgr.
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223




From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, May 31, 2012 5:34 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] AC Coupling

I currently have a dual Outback GTVFX system for the office at home and am 
adding an SMA 4KW GIT system. We are going for 100% solar powered on the office 
 home. Yahoo!

I would like to be able to AC support the battery based GTVFX system in the 
event of an extended power outage. I spoke with Outback and they said to feed 
the output of the GTVFX[s],  that they did not have a drawing to support this 
installation.

Would anyone who has done this setup, be willing to share a one line or 
schematic drawing?

Thanks in advance.

Dana Orzel - Great Solar Works, Inc -  E - d...@solarwork.com -  V 970.626.5253
F - 970.626.4140 C - 970.209.4076 web - www.solarwork.com
Responsible Technologies for Responsible People since 1988
Please consider the environment before printing this email   NABCEP # 051112-136

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] SMA HF inverters

2012-06-01 Thread Marco Mangelsdorf
We're seeing a disturbing frequency of problems with the 2, 2.5 and 3 kW
Sunny Boy HF inverters.

 

Anyone else having issues as well?

 

Thanks,

marco

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrective EQ question

2012-06-01 Thread Kent Osterberg

Allan,

My first thought about the high s.g. measurements is that the 
electrolyte level may have been low when the measurements were made. 
When full, there is about a liter of electrolyte above the plates in a 
L16. The s.g. will rise by 0.03 if the electrolyte level is at the top 
of the plates.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 6/1/2012 1:28 PM, Allan Sindelar wrote:

Wrenches,
A long-time off grid client has a 48V Outback VFX system, with 1,680 
watts of PV and two strings (16 batteries total) of Deka L16s, 
installed last October. The array is undersized, as the system is 
running three households; one efficient home and two single-person 
tiny homes, but still too much for the system. We learned a few weeks 
ago that the system had apparently stayed at 30-50% SOC for the entire 
winter (this is approximate, as her TriMetric monitors would 
eventually drift away from % accuracy if never allowed to get full and 
reset). Eventually the batteries became sufficiently sulfated that the 
system began shutting down.


As the batteries were nearly new, we figured that the sulfation had 
not yet become permanently crystallized, and they could recover. We 
initiated a long corrective equalization from her combined generator 
(45A DC from the single inverter) and MX60 controller, for a maximum 
C/12.5 charge rate; less in proportion to any loads that were on while 
charging. She ran this procedure for three hours/day for five days, 
and when that offered only partial recovery (as measured by specific 
gravity measured with a refractometer), ran for six hours/day for five 
days. During this time the MX60 was also manually set to EQ each 
morning, with a 62V EQ voltage and 3 hour EQ time, so that the array 
would add its amperage to the gennie until the batteries had been 
above this setting for three hours.


We went out there yesterday, arriving while the EQ was in process. All 
of the cells had recovered, as measured by SG. SG readings were all in 
the 1.280 - 1.300 range, with most above 1.290. We had never seen SG 
readings this high before. Given the situation and the back story, 
should we have any concern about the high SG readings?


Thank you,
Allan
--
*Allan Sindelar*
_Allan@positiveenergysolar.com_ mailto:al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
_www.positiveenergysolar.com_ http://www.positiveenergysolar.com/

*
*




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org