I have to agree with Larry… a properly sized, designed and charged series 
battery bank does not need “magic elixir” and if you add it to an old poorly 
designed bank it still will be poorly designed, even if you could fix the hard 
sulphation the problem would re-appear. I have never seen this stuff work 
however in my 45 years in the battery business.

Kind Regards

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
[email protected]
For: Customer Service and Accounting 888-895-6810  Grid tie sales 888-895-7847
Off Grid sales 888-895-7765 Other Product Sales 888-895-9612
Shipping and Receiving 888-895-6497 Tech Support 888-895-8179

From: [email protected] 
[mailto:[email protected]] On Behalf Of William Dorsett
Sent: Monday, May 28, 2012 3:16 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] De-Sulphators. The last word?

If this is a fancy name for EDTA, perhaps 10 years ago I went through virtually 
all of the previous 15 years of Chemical Abstracts to see if there were ANY 
reference to its working. And while there were hundreds of scholarly abstracts 
on lead acid chemistry, there was only 1 that mentioned EDTA and that was a 
mixed review and attributed any benefit to the ion with which EDTA was combined 
as a salt. Like desulfators, there may be anecdotal hearsay, but little science.

Bill Dorsett
Sunwrights
Manhattan, KS

From: 
[email protected]<mailto:[email protected]>
 
[mailto:[email protected]]<mailto:[mailto:[email protected]]>
 On Behalf Of Jonathan Hill
Sent: Monday, May 28, 2012 12:33 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] De-Sulphators. The last word?

Try Thermoil deslphator additive. Has good reviews. We are selling it.

Jon Hill
Sierra Solar Systems

On May 28, 2012, at 7:17 PM, "Larry Crutcher, Starlight Solar Power 
Systems"<[email protected]<mailto:[email protected]>> wrote:
Dan,

I'm perplexed. Where was anything mentioned about de-sulphators? Where was 
anyone "slammed"? What in the world are you talking about? Perhaps you meant to 
reply to someone else's thread. BTW, I do not recommend a desulfator or pulser 
be installed on batteries.

I'll reiterate my points:
1. KC-120's from a certain production era fail and can be warranted.
2. Applying enough load will cause full current to flow from a PV array.
3. Sulfated batteries have high resistance causing a quick rise in voltage.

I welcome your response but please reply off list.

Respectfully yours,

Larry

On May 28, 2012, at 6:42 AM, 
<[email protected]<mailto:[email protected]>> 
<[email protected]<mailto:[email protected]>> wrote:

Seems I have a stalwart "Battery Specialist" in the neighborhood still 
convincing folks that de sulphators are the smartest thing since sliced bread 
(And slamming anyone who disagrees). In my experience, sparklers have little to 
no effect on battery longevity and in most cases add unlisted, hazardous and 
unnecessary wiring devices to a potentially hazardous environment. Is tar and 
feathering still an acceptable means of dispute resolution.. or am I totally 
missing something? tks db

Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com<http://www.Foxfire-Energy.com/>
NABCEP #092907-44

-------- Original Message --------
Subject: Re: [RE-wrenches] Troubleshooting Off-grid PV
From: "Larry Crutcher, Starlight Solar Power Systems"
<[email protected]<mailto:[email protected]>>
Date: Sun, May 27, 2012 7:37 pm
To: RE-wrenches 
<[email protected]<mailto:[email protected]>>

Hi Eric,

Check the dates on the KC-120 module label. If any were manufactured between 
January 1999 and December 2002, they have or will fail. We have been replacing 
these modules for over 8 years now. There was a defective solder joint during 
manufacture. Kyocera will still replace them under warranty even though they 
have no legal requirement to do so. They will ship you remanufactured 120's and 
pay for return shipping. Contact Kyocera about the procedure.

If the batteries are sulfated, they will not produce the load necessary to 
drive the current high. Capacity has nothing to do with it; internal resistance 
does. You can test the array by pulling the voltage down (turn on some big 
loads) at solar noon. This will force the controller into bulk and reveal the 
maximum current the array can produce. I think you have two problems here. With 
bad modules, you may not see much.

It is typical for a controller to transition to float very early in the charge 
cycle if the battery is sulfated. Look for a fast rise in voltage in the 
morning. This is an indicator of sulfated battery. A healthy battery will 
slowly climb in voltage.

Let me k now if you need more understanding about batteries, charging and why 
MOST of them never see old age. It's my speciality.

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103


_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]