[RE-wrenches] Photovoltaic Pilot Project Findings Report

2010-01-29 Thread Kurt Albershardt
From a link in today's RETScreen newsletter - nothing here any of us has not seen before, but it is a well put together piece that might be worth handing out to potential clients as an educational backgrounder http://www.toronto.ca/taf/pdf/solarcity-horse-palace-june2009.pdf

Re: [RE-wrenches] sources of DC equipment

2010-04-12 Thread Kurt Albershardt
On Apr 11, 2010, at 9:11 , Darryl Thayer wrote: Where are people getting 24 or 32 or 48 volt CFLs? Are there any LED now suitable at these voltages? Others have commented on the general state of things DC - I have a slightly different perspective coming form a telecom background and

Re: [RE-wrenches] low cost DAS systems

2010-04-21 Thread Kurt Albershardt
I spent some time researching power monitoring equipment for a commercial project earlier this year - a short list of the ones I found interesting follows: http://www.powerlogic.com/index.cfm http://www.dentinstruments.com/ http://www.elkor.net/ http://www.veris.com/ http://www.accuenergy.com/

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-14 Thread Kurt Albershardt
The Square-D catalogs are marginally clear on which breakers are listed for DC and for what voltages, but when I tried to select an appropriate load center for a DC application earlier this year I quickly ran into a number of conflicts in their catalogs. Here is the response from Schneider

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
nominal. Rebekah Hren North Carolina http://thecarbonfreehome.com/ --- On Sat, 5/15/10, Kurt Albershardt i...@es-ee.com wrote: From: Kurt Albershardt i...@es-ee.com Subject: Re: [RE-wrenches] AC breakers used in DC applications To: RE-wrenches re-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Voltage is not the issue here, it is current, and battery fault currents can be staggering - far more than one would ever encounter in a typical AC system fed from a distribution transformer. I have seen a 200A Class T fail to act on an 48V inverter fault which resulted in welding the metal

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
be undertaken. I like to have primary protection on each string, as close to the battery as possible - preferably bolted to the battery terminal. Cable limiters are nice, but a TPL style fuse is easier to get. On May 16, 2010, at 16:13 , Kurt Albershardt wrote: Voltage is not the issue here

Re: [RE-wrenches] off grid generators

2010-06-24 Thread Kurt Albershardt
I'd suggest finding out who the industrial engine dealers are in a large nearby city (Richmond, VA?) then see who is assembling gensets from which engines. I've had good relationships with a couple of small builders over the years, one Isuzu and one Kubota based (though mostly Diesels, after

Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump

2010-06-24 Thread Kurt Albershardt
Once you determine the real pump requirements (as others have mentioned, this is critical - IME particularly if the well guy sized and sold the pump) and if a larger than SQflex pump is needed, I have had good luck using VFDs to drive three-phase pumps with single phase power. You can pay

Re: [RE-wrenches] Lightning Protection System

2010-08-22 Thread Kurt Albershardt
A little late to the party here, but it might interest you all to know that the military has its own well-constructed standards for lightning protection. Army Technical Manual 5-690 is a wonderful educational resource that explains the rationale for various measures quite clearly (and covers

Re: [RE-wrenches] Battery Cable REvistied

2010-12-12 Thread Kurt Albershardt
The telecom industry uses a lot of Sanchem NO-OX-ID A Special - costs a fraction of what Penetrox E does and doesn't leave copper schmeer all over the place. We keep a tube in every tool bag. On Nov 30, 2010, at 12:53 , R Ray Walters wrote: We use the same inner melt heat shrink, I think.

Re: [RE-wrenches] grid-tie inverters generators

2008-11-20 Thread Kurt Albershardt
I'm hearing that it should be OK, but to CYA install a relay. Yes, but... The real answer is to find a genset and inverter which can peacefully coexist. I don't know what sort of regulator topology is used by the gensets we have heard about, but that seems to be the key. Many

Re: [RE-wrenches] tower lifting winches

2008-11-29 Thread Kurt Albershardt
--On Tuesday, November 25, 2008 3:07 PM -0500 Roy Butler [EMAIL PROTECTED] wrote: While I strongly recommend the use of a worm gear type winch (because of it's braking ability) I have to admit that they're getting harder to find. My elevator guy turned me on to the GoLo - an AC powered hoist

[RE-wrenches] Skystream 3.7 experiences?

2008-12-22 Thread Kurt Albershardt
Anyone have realworld experience with the SWWP Skystream 3.7 they can share? The AnemErgonics foundation kit looks fairly well thought out. -- Kurt Albershardt Eastern Sierra Energy Engineering Reno, NV 775-853-1800 ___ List sponsored by Home Power

Re: [RE-wrenches] small grid-tie wind

2008-12-23 Thread Kurt Albershardt
--On Tuesday, December 23, 2008 8:57 AM -0800 Randy Brooks ra...@brookssolar.com wrote: I had a Bergey Xl.1 grid tied through an OutBack GFX2524 for a couple years as a demo project at my home/office.  It worked fine.  I did not keep track of production because I had it on a 40' tower in a

[RE-wrenches] Multi-structure PV install

2008-12-25 Thread Kurt Albershardt
of the structures. Enphase inverters look like a good fit for this, but I am curious about disconnects labeling. Has anyone done a job like this? -- Kurt Albershardt Eastern Sierra Energy Engineering Reno, NV Silver City, NM ___ List sponsored

Re: [RE-wrenches] Building integrated thermal collectors?

2008-12-27 Thread Kurt Albershardt
--On Saturday, December 27, 2008 8:08 AM -0700 mick abraham m...@abrahamsolar.com wrote: I'm looking for thermal collectors which integrate into the roof of the building. These would heat glycol to modest temperatures, for domestic hot water. Dawn Solar uses a design which effectively

Re: [RE-wrenches] Multi-structure PV install

2008-12-29 Thread Kurt Albershardt
--On Monday, December 29, 2008 8:29 AM -0800 Marv Dargatz mdarg...@enphaseenergy.com wrote: The NEC provides for, and the AHJs have accepted the use of the connectors as a form of disconnect. Of course, each branch is also connected to a dedicated branch overcurrent device (circuit

Re: [RE-wrenches] Multi-structure PV install

2008-12-29 Thread Kurt Albershardt
--On Monday, December 29, 2008 10:06 AM -0700 Jason Lombard openhandso...@gmail.com wrote: I worked on a elderly housing site in northern Ca in which we connected to the main service on each structure (total of 12) or building. I'm assuming all those buildings have service billed to the

Re: [RE-wrenches] Low Voltage Alarm Based on cell phone text message

2009-01-31 Thread Kurt Albershardt
--On January 31, 2009 8:09:27 AM -0800 Peter Parrish peter.parr...@calsolareng.com wrote: We have sold an off grid system delivering 24 volts DC. The application is “mission important”. We have built in a LVD and alarm, but the client wants an early warning system based on sending text

Re: [RE-wrenches] 300A panel

2009-02-04 Thread Kurt Albershardt
--On February 4, 2009 6:28:25 PM -1000 Marco Mangelsdorf ma...@pvthawaii.com wrote: I know that it's an oddball size, but I'm looking for a 300A indoor, surface-mounted 120/240V distribution panel. Anyone know of an available model and manufacturer out there? Major manufacturers' 400A

Re: [RE-wrenches] On demand Electric with pre heated water

2009-02-09 Thread Kurt Albershardt
On 2/9/09 12:24 PM, Karl Schwingel wrote: Have any of you experience with on demand electric water heaters? At the recommendation of someone on this list a few years back, we purchased a Stiebel-Eltron Tempra 36 for a project. It seems quite happy with preheated water and is nicely

Re: [RE-wrenches] Heat pump water heaters (was: On demand Electric with pre heated water)

2009-02-09 Thread Kurt Albershardt
On 2/9/09 3:36 PM, wlbr...@pineridgeproducts.com wrote: We are trying a HeatPump heater as backup for a solar hotwater system. Trying to get away from propane. http://www.airgenerate.com/products/specs.html If that 7,000 BTU/hr rating is correct, it equates to 2kW of resistance heat, which

Re: [RE-wrenches] tankless gas water heaters

2009-02-10 Thread Kurt Albershardt
On 2/10/09 12:20 AM, Bill Loesch wrote: What I can offer is that there are five (5) major _manufacturers_ of tankless water heaters that market to North America. Alphabetically: Bosch, Noritz, Paloma, Rinnai, and Takagi. A multitude of other companies market gas tankless. Even more market

Re: [RE-wrenches] another firefighter mis-information link (was: Panel Fire)

2009-02-11 Thread Kurt Albershardt
On 2/11/09 6:48 PM, Michael Welch wrote: This seems corroborating. It has GOT to be the same situation: http://www.examiner.com/x-432-Wedding-and-Marriage-Examiner~y2009m2d10-Our-wedding-anniversary-like-a-house-on-fire-literally

Re: [RE-wrenches] SHW Production Estimator

2009-02-20 Thread Kurt Albershardt
On 2/20/09 6:34 AM, Darryl Thayer wrote: HI I partook in some calculation to real comparasions several years ago. In general the results from F-Chart software and I think Maui? did a rather good job. The RetScreen is very limited at present, to bad because it is so easy and accessable. ( I

Re: [RE-wrenches] 2 PV utility interconnect disconnects?

2009-02-21 Thread Kurt Albershardt
On 2/21/09 10:24 AM, Joel Davidson wrote: January 1, 2009 LADWP added another interconnection requirement. See page 8-11 at http://www.ladwp.com/ladwp/cms/ladwp004344.pdf I found what I think is the relevant section on p. 36 of the PDF (called out as p. 1-32 at the top of the page.) This

Re: [RE-wrenches] CSST source

2009-02-26 Thread Kurt Albershardt
Can someone point me at a supplier for CSST, tools, and fittings? I've Googled my way into oblivion searching for these and can only find references to gas tubing. One of my vendors who uses it guards their sources far too compulsively. thanks... On 2/26/09 2:19 AM, Bill Loesch wrote:

Re: [RE-wrenches] Efficient water softener?

2009-02-27 Thread Kurt Albershardt
On 2/27/09 12:20 AM, Bill Loesch wrote: My compliments to solve a water quality problem. Tremendous benefits for every other water using appliance, valve, and faucet in the dwelling. Agreed, and I'll add that it's critical to have the water tested before you propose a treatment strategy.

Re: [RE-wrenches] CSST source

2009-02-28 Thread Kurt Albershardt
On 2/28/09 5:12 PM, Bill Loesch wrote: One of the several CSST manufacturers is Omegaflex who currently sells the TrackPipe product. Thanks - I'll be in touch with them Monday. Following a brief conversation with one of their people Friday, I learned the gas pipe is made from 304 stainless

Re: [RE-wrenches] Is a Smart Phone a Useful Tool in PV?

2009-03-01 Thread Kurt Albershardt
On 2/28/09 11:14 AM, cvsol...@aol.com wrote: What can I reasonably expect to get out of this thing for the $$? (that I can't do with a phone). Having fairly extensive experience with both Treo and BlackBerry phones over the past decade, here are a few thoughts: BB is overrated in most

Re: [RE-wrenches] How large is too large?

2009-03-02 Thread Kurt Albershardt
On 3/2/09 6:08 PM, Travis Creswell wrote: FYI, HUP now has a 1990 AH battery. Of course that’s still way too many stings to get to 19,000 AH (900+ kWh, wow) Exide makes 3,000 - 4,000 AH wet cells in their solar and telecom product families.

Re: [RE-wrenches] grid tie sync with big stiff genny?

2009-03-13 Thread Kurt Albershardt
On 3/13/09 9:34 AM, Mark Edmunds wrote: We did a test installation in northern British Columbia with 28kW of PV and GT5 inverters selling to a 90kW Genny system in a remote off-grid community. So far we have just stuck to the normal 1741 islanding settings, and the system has been working

Re: [RE-wrenches] Frostek-240 Propane Freezer

2009-03-30 Thread Kurt Albershardt
On 3/30/09 1:23 PM, Jeff Yago wrote: I have an off grid client out west we designed and installed a large pv system about 8 years ago that recently contacted me to say they needed an installation and operator manual for their Frostek-240 Propane Freezer. I have tried all the normal channels

[RE-wrenches] Solar flares and PV

2009-04-05 Thread Kurt Albershardt
Seems the predicted 2012 Carrington Event could have some interesting side effects. Wondering how PV panels themselves might respond, and if the existing input stage protection (6 kV IIRC) on charge controllers and inverters would protect them?

Re: [RE-wrenches] A Wrench's computer

2009-04-10 Thread Kurt Albershardt
As yet another long-time PC veteran (after IBM SNA and PDP-11s) with way too much Windows internals experience, I also just purchased my first Mac. Installed Parallels to support Quickbooks (still no integrated payroll on their Mac version.) I have a maxed-out MacBook Pro as a desktop

Re: [RE-wrenches] DSL routers for off grid

2009-04-13 Thread Kurt Albershardt
On 4/13/09 10:41 AM, jeff Wongstrom wrote: We have had an ongoing problem with slow internet speed caused by multiple issues, most of which seem to have been corrected over the past three years with much troubleshooting and with several service calls. However, one issue remains and seems to

Re: [RE-wrenches] Desulfators oil

2009-06-19 Thread Kurt Albershardt
On 6/19/09 7:43 AM, Jeff Oldham wrote: The jury is still out with me, but so far I'm feeling optimistic with my experiences with Duo-regen technology. I use both the mineral solution additive and the pulse units. The testimonials are impressive and my experience over the last 5 months is

Re: [RE-wrenches] Lightning protection (was: Grounding on a glacier??)

2009-07-24 Thread Kurt Albershardt
Check out Nott Ltd. http://www.nottltd.com/lightning.html I know a couple of RF engineers who swear by these and will not setup a tower without them. We are looking at putting small ones on each end of every row on a large array next year. On 7/22/09 13:57 , toddc...@finestplanet.com

Re: [RE-wrenches] SOVs (was: Surge protector update?)

2009-08-01 Thread Kurt Albershardt
On 8/1/09 4:49 , Richard L Ratico wrote: 2)At a different training, by a well respected professional engineer who frequently posts here, they were judged to likely be as effective in preventing damage as a voodoo doll. I'm not disputing this, but would like to know more. Perhaps our PE

Re: [RE-wrenches] down-sizing main breaker

2009-08-01 Thread Kurt Albershardt
On 8/1/09 11:08 , William Miller wrote: Our best solution would be to install a 200 amp meter panel with a 100 amp breaker. The application is an agricultural based residence, so based on how one interpreted this, the back feed allowance would be either 100 amps or 120 amps, enough to cover

Re: [RE-wrenches] DC positive and negative in same conduit, other inspection issues

2009-08-19 Thread Kurt Albershardt
On 8/19/09 15:41 , Dave Click wrote: Wiring was free air until it got near the disconnect, then the positive wires entered an open 3' section of FNMC (no strain relief or box at the other end of the FNMC). The negative wires ran through a *separate* 3' section of FNMC. 1. Running the

Re: [RE-wrenches] Exeltech Inverters

2009-11-14 Thread Kurt Albershardt
I can not speak to their grid tie product (which they have been trying to get out the door for almost a decade now) but their XP MX lines have served well over the years and Exeltech has always been a good company to deal with and has stood behind what they sold. I notice a new module

Re: [RE-wrenches] Hotel exclusion

2009-12-15 Thread Kurt Albershardt
Anyone have a link to the IRS or ARRA that details this? Can't find anything on http://www.treas.gov/recovery/1603.shtml or http://www.treas.gov/recovery/docs/guidance.pdf or the IRS site. TIA... On Dec 13, 2009, at 23:52 , Michael Gullo wrote: Hi All, I was bidding a job for a

[RE-wrenches] Trace SW repair assistance

2021-10-29 Thread Kurt Albershardt
Good morning, all. Long time no write. We have a client with an SW4024 that recently suffered a lightning hit. The inverter is actually working fine (those things were truly tough) but the cooling fan now runs continuously. The SW design team long ago scattered to the winds of Outback,

Re: [RE-wrenches] Trace SW repair assistance

2021-10-29 Thread Kurt Albershardt
t; Hello Kurt, > > Craig Wilburn at Phantom Power Services should be able to help. > 425-501-7280 > https://phantompowerservices.com/ > > Best of luck, > Lloyd > > Lloyd Hoffstatter > Sunstruck Consulting > > > > Sent from Mail <https://go.microsoft.com/fwlin