[RE-wrenches] Aging Batteries

2023-10-27 Thread White, Will via RE-wrenches
Hello Wrenches, I installed my off-grid system in 2008. It’s 24 V using 2 V industrial FLA batteries. As you can imagine after 15 years the capacity of my battery bank is significantly less than it used to be. For logistic reasons, I won’t be able to replace them till around June of next

[RE-wrenches] Sol-Ark phantom loads

2023-10-26 Thread White, Will via RE-wrenches
Don, Your Fluke clamp meter should indicate the current flow by showing a negative or positive current reading unless you've got an old meter. On the top of the meter inside the jaw is an arrow that points in the direction of current flow if the reading is positive. If it's negative, the

Re: [RE-wrenches] Cleaning PV mods

2023-10-23 Thread White, Will via RE-wrenches
I worked with a guy who had done installs in Arizona. He had an off-grid customer spray down their array with cold well water in the middle of the day, which shattered the module glass. I’m sure it was an isolated incident, but it happened. Thanks, Will From: RE-wrenches On Behalf Of Jason

Re: [RE-wrenches] [EXTERNAL] Voltage Rise

2023-02-23 Thread White, Will via RE-wrenches
I’ve run into a similar issue, and the problem was on the utilities side. They had shut down the local substation for repairs and were pumping power in from the next town over. To push the power that far, they increased the line voltage, which was causing issues with the PV inverter. I’d

Re: [RE-wrenches] [EXTERNAL] IQ Gateway outside straw bale house

2023-04-26 Thread White, Will via RE-wrenches
Drake, I can't speak to your specific situation, but I live in a strawbale house and have no problem getting a Wi-Fi signal outside within reasonable distance of the router. Thanks, Will -Original Message- From: RE-wrenches On Behalf Of Drake Chamberlin via RE-wrenches Sent:

Re: [RE-wrenches] [EXTERNAL] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-10 Thread White, Will via RE-wrenches
Ray, I can’t speak to the Fortress product, but Discover will do what they call “dynamic charging” in closed-loop installations. Basically, the BMS will tell the power electronics how to charge the battery, which will lead to a better charging cycle. For example, if the batteries are

Re: [RE-wrenches] [EXTERNAL] Re: Lithium battery recommendation

2023-07-14 Thread White, Will via RE-wrenches
I’d also look at Victron. They can close loop communicate with several battery systems, and my sources say they’ve also got an EV charger that works with their off-grid systems that can be programmed to charge the EV when you have excess solar. Kienan Maxfield, who’s on the list, is

Re: [RE-wrenches] SMA TL-22 insulation resistance error

2023-12-13 Thread White, Will via RE-wrenches
It depends on how bad the fault is. Insulation resistance testing can definitely find some intermittent ground faults. Thanks, Will From: RE-wrenches On Behalf Of Dave Tedeyan via RE-wrenches Sent: Wednesday, December 13, 2023 2:46 PM To: RE-wrenches Cc: Dave Tedeyan Subject: [EXTERNAL] Re:

Re: [RE-wrenches] [EXTERNAL] Re: Optics

2024-05-24 Thread White, Will via RE-wrenches
I ran into a guy from EG4 at RE+ Texas last week. He confirmed that Outback was purchased by the parent company of EG4 and Signature Solar. From: RE-wrenches on behalf of Kirk Bailey via RE-wrenches Sent: Saturday, May 18, 2024 3:24 PM To: RE-wrenches Cc: Kirk