We have done several of these systems with various inverter combinations. We
used a voltage activated relay in the stone age to switch inverters between
battery banks and the grid before the Trace SW came on scene. This little
switch opens and closes a relay based on user adjustable set points.
Daryl was right on the charge rates. What is not referenced is the
configuration of the battery bank.
Since it is a 24 volt system it could possibly have multiple series strings
paralled together. There will always be imbalances in the individual strings
resulting in higher resistance in one
Allan,
A very simple way to do this is install a float in the tank you are pumping to
with a shutoff valve controlled by the float. Install a Square D pressure
switch with a DC rating by the pump. As the float rises to full in the tank
and chokes off the discharge outlet the pressure in the
- www.solarwork.com
Responsible Technologies for Responsible People since 1988
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of solardude97
Sent: Friday, October 15, 2010 4:05 PM
To: al...@positiveenergysolar.com;
re-wrenches@lists.re
The Grundfos switch is voltage only. I'm not sure I would run it 700 ft or not,
regardless. For that distance I would probably install a float switch in the
discharge tank that shut off the inlet flow and backed water pressure down the
pipe to a pressure switch located close to the pump. As the