Re: [RE-wrenches] Aquion Testing

2018-12-24 Thread Bradley Bassett
Better yet, use Amphenol connectors.

Brad

On Mon, Dec 24, 2018 at 1:43 PM Tom Duffy  wrote:

> If you’re showing a lower voltage tray in the stack… You can’t overcharge
> the whole set to get the 6 volt tray to come up but you can separate
> (electrically) not physically (leave the center bolt alone) and charge the
> single tray with a 6 volt charger.
>
>
>
> We’ve done this with success several times. Make sure the MC4 connector is
> clean as they seem to get funky with low voltage.
>
>
>
> Kind regards
>
>
>
> *Tom Duffy*
>
> *Senior Solar Design Engineer*
>
> [image: TSBLOGODPIx500x200]
>
> *t...@solar-biz.com *
>
> *MAIN TOLL FREE:** 888-826-0939*
>
> *DIRECT:** 888-503-6772*
>
> *International:* *001-575-539-2111*
>
> *PANAMA:* *507-836-5588 X 122*
>
> *FAX: 520-844-8442*
>
> *www.thesolarbiz.com <http://www.thesolarbiz.com>*
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *John Blittersdorf
> *Sent:* Saturday, November 10, 2018 6:48 PM
> *To:* RE-wrenches 
> *Subject:* Re: [RE-wrenches] Aquion Testing
>
>
>
> Lou, I recently discovered that each layer can be checked for voltage.  I
> had one battery test lower than the rest.  Looking at the battery closer, I
> found that my meter probe could get the voltage of each layer indivually.
> Through an opening in the case. The top layer had the reduced voltage
> output and it was one cell of the 4 cells in each layer.  I have 4
> customers with Aquions and we are seeing lower storage because the days are
>
> Shorter now and fewer sunny days here in the Northeast. These batteries
> really like long slow charges. I have one  customer with 8000 watts of Pv
> and a 12kw generator and he can’t figure out why his generator has to run
> so long.  It is the nature of the batteries and our darkest month.  His
> system is undersized with 12 battery stacks and he is driving to Maine
> tomorrow to buy 20 more from another unhappy Aquion user who is going back
> to lead acid.  I am hoping doubling his storage will solve another problem
> of voltage dropping to 36 volts when his 1.75hp well pump runs when no sun
> or generator.  Over sizing the battery bank is ok with Aquions as they
> don’t need to be fully charged.on a regular basis.
>
>
>
> John Blittersdorf
>
>
>
>
>
>
>
>
>
> .
>
>
>
>
>
> On Sat, Nov 10, 2018 at 5:33 PM Lou Russo 
> wrote:
>
> Aloha Wrenches,
>
>
>
> I have a orphaned system with 6 - Aquion Aspen 48Ss that is running out of
> energy nightly. This is a off-grid system with a Outback FP1. The logs from
> the Mate 3 do not show excess usage. Beyond testing the voltages of the
> individual stacks is there any way to check if a battery is good, bad, or
> failing?  I don't have much experience with Aquions and have yet to have
> any of the 40 or so stacks I have installed fail.
>
>
>
> Thanks for your insight.
>
>
>
> Aloha,
>
>
>
> Lou Russo
>
> l...@spreesolarsystems.com
>
> 808 345 6762
>
> Spree Solar Systems LLC
>
> CT-34322
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Aquion Testing

2018-12-24 Thread Tom Duffy
If you’re showing a lower voltage tray in the stack… You can’t overcharge the 
whole set to get the 6 volt tray to come up but you can separate (electrically) 
not physically (leave the center bolt alone) and charge the single tray with a 
6 volt charger.

We’ve done this with success several times. Make sure the MC4 connector is 
clean as they seem to get funky with low voltage.

Kind regards

Tom Duffy
Senior Solar Design Engineer
[TSBLOGODPIx500x200]
t...@solar-biz.com<mailto:t...@solar-biz.com>
MAIN TOLL FREE: 888-826-0939
DIRECT: 888-503-6772
International: 001-575-539-2111
PANAMA: 507-836-5588 X 122
FAX: 520-844-8442
www.thesolarbiz.com

From: RE-wrenches  On Behalf Of John 
Blittersdorf
Sent: Saturday, November 10, 2018 6:48 PM
To: RE-wrenches 
Subject: Re: [RE-wrenches] Aquion Testing

Lou, I recently discovered that each layer can be checked for voltage.  I had 
one battery test lower than the rest.  Looking at the battery closer, I found 
that my meter probe could get the voltage of each layer indivually. Through an 
opening in the case. The top layer had the reduced voltage output and it was 
one cell of the 4 cells in each layer.  I have 4 customers with Aquions and we 
are seeing lower storage because the days are
Shorter now and fewer sunny days here in the Northeast. These batteries really 
like long slow charges. I have one  customer with 8000 watts of Pv and a 12kw 
generator and he can’t figure out why his generator has to run so long.  It is 
the nature of the batteries and our darkest month.  His system is undersized 
with 12 battery stacks and he is driving to Maine tomorrow to buy 20 more from 
another unhappy Aquion user who is going back to lead acid.  I am hoping 
doubling his storage will solve another problem of voltage dropping to 36 volts 
when his 1.75hp well pump runs when no sun or generator.  Over sizing the 
battery bank is ok with Aquions as they don’t need to be fully charged.on a 
regular basis.

John Blittersdorf




.


On Sat, Nov 10, 2018 at 5:33 PM Lou Russo 
mailto:l...@spreesolarsystems.com>> wrote:
Aloha Wrenches,

I have a orphaned system with 6 - Aquion Aspen 48Ss that is running out of 
energy nightly. This is a off-grid system with a Outback FP1. The logs from the 
Mate 3 do not show excess usage. Beyond testing the voltages of the individual 
stacks is there any way to check if a battery is good, bad, or failing?  I 
don't have much experience with Aquions and have yet to have any of the 40 or 
so stacks I have installed fail.

Thanks for your insight.

Aloha,

Lou Russo
l...@spreesolarsystems.com<mailto:l...@spreesolarsystems.com>
808 345 6762
Spree Solar Systems LLC
CT-34322

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Aquion Testing

2018-11-10 Thread John Blittersdorf
Lou, I recently discovered that each layer can be checked for voltage.  I
had one battery test lower than the rest.  Looking at the battery closer, I
found that my meter probe could get the voltage of each layer indivually.
Through an opening in the case. The top layer had the reduced voltage
output and it was one cell of the 4 cells in each layer.  I have 4
customers with Aquions and we are seeing lower storage because the days are
Shorter now and fewer sunny days here in the Northeast. These batteries
really like long slow charges. I have one  customer with 8000 watts of Pv
and a 12kw generator and he can’t figure out why his generator has to run
so long.  It is the nature of the batteries and our darkest month.  His
system is undersized with 12 battery stacks and he is driving to Maine
tomorrow to buy 20 more from another unhappy Aquion user who is going back
to lead acid.  I am hoping doubling his storage will solve another problem
of voltage dropping to 36 volts when his 1.75hp well pump runs when no sun
or generator.  Over sizing the battery bank is ok with Aquions as they
don’t need to be fully charged.on a regular basis.

John Blittersdorf




.


On Sat, Nov 10, 2018 at 5:33 PM Lou Russo  wrote:

> Aloha Wrenches,
>
> I have a orphaned system with 6 - Aquion Aspen 48Ss that is running out of
> energy nightly. This is a off-grid system with a Outback FP1. The logs from
> the Mate 3 do not show excess usage. Beyond testing the voltages of the
> individual stacks is there any way to check if a battery is good, bad, or
> failing?  I don't have much experience with Aquions and have yet to have
> any of the 40 or so stacks I have installed fail.
>
> Thanks for your insight.
>
> Aloha,
>
> Lou Russo
> l...@spreesolarsystems.com
> 808 345 6762
> Spree Solar Systems LLC
> CT-34322
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Aquion Testing

2018-11-10 Thread Lou Russo
Aloha Wrenches,

I have a orphaned system with 6 - Aquion Aspen 48Ss that is running out of
energy nightly. This is a off-grid system with a Outback FP1. The logs from
the Mate 3 do not show excess usage. Beyond testing the voltages of the
individual stacks is there any way to check if a battery is good, bad, or
failing?  I don't have much experience with Aquions and have yet to have
any of the 40 or so stacks I have installed fail.

Thanks for your insight.

Aloha,

Lou Russo
l...@spreesolarsystems.com
808 345 6762
Spree Solar Systems LLC
CT-34322
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org