trades on the job. An impossible environment for making sensitive adjustments. More fine tuning to come...Bruce Fiero-RMIWillpower Electric LLC
Original Message
Subject: Re: [RE-wrenches] Outback Chargers
From: Steve Higgins st...@surrette.com
Date: Tue, February 11, 2014 7:59 am
Hi Matt,
With two systems on the thread right now with pretty much the same problem, I
am suspecting a problem with one or more inverters. Most all the Outback
inverter issues I've have been have been on stacked systems.
Having installed a lot of these inverters I have yet to see the exact
One of the issues to be aware of is power factor, and most people will not
be able to determine power factor. If the Outback operates at a poor power
factor, your 10KW generator will become a about a 6KW generator. A lot of
the current will be wasted and will not produce charging power.
On Tue,
Subject: Re: [RE-wrenches] Outback Chargers
Kevin,
I am curious about what you are seeing on the Outbacks as well.
Have dozens of these out in the field. They have been pretty reliable for me.
The biggest issue that I have had with them is when the inverters are
transferring from generator charging
this is good advice, but beware: if you set the time too low, the inverter will
never go to sleep. this is an issue with grid tie units where you do not want
the inverter wasting power, running all night long.
todd
On Tuesday, February 11, 2014 7:03am, Doug Wells
o unstable, and blow the inverter. Not a guaranteed failure .. but an enhanced possibility.
Dan
On Mon, 2/10/14, br...@willpowerelect.com br...@willpowerelect.com wrote:
Subject: Re: [RE-wrenches] Outback Chargers
To: "RE-wrenches"
...@lists.re-wrenches.org]On Behalf Of
m...@solar-energy-solutions.com
Sent: February 10, 2014 4:09 PM
To: RE-wrenches
Subject: [RE-wrenches] Outback Chargers
Wrenches,
Based on Kevin's comments about Outback Chargers in the HUP thread I am
hopeful that some of you well-versed in the off grid world can
how it works.Bruce Fiero-RMIWillpower Electric LLC
Original Message
Subject: [RE-wrenches] Outback Chargers
From: m...@solar-energy-solutions.com
Date: Mon, February 10, 2014 4:09 pm
To: "RE-wrenches" re-wrenches@lists.re-wrenches.org
Wrenches,
Based on Kevin's comm
On Mon, 2/10/14, br...@willpowerelect.com br...@willpowerelect.com wrote:
Subject: Re: [RE-wrenches] Outback Chargers
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Monday, February 10, 2014, 10:43 PM
Matt,
I don't have a lot of experience with undersized generators
i would love to see a spectrum analyzer's view of the fx's harmonics. does
anyone have this available?
interesting (and sad) how silent outback is on this list now.
todd
On Monday, February 10, 2014 9:37pm, Exeltech exelt...@yahoo.com said:
Bruce,
The capacitors may or may not
10 matches
Mail list logo