an the peak, roughly 71% like a sine wave.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/op
V. In general, most of the world
uses the 230V standard. This also means that standard 230V equipment
can be used in most parts of the world, with only a minor change in
the equipment's electrical plug for a specific country."
Hugh
Darryl,
thank you for that! i've often wondered myse
tormy weather.
best
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.
additional functions.
Hugh Piggott
Warren:
I can see a few:
1. It will not interface with the SW plus,
2. It will not take advantage of the charging intelligence or load
start functions in the SW plus.
3. It will work on a 48 volt system.
4. Analog settings are generally very approximate, espec
OK mystery solved. Stuff has changed since the 1990s. I wonder why
it's not called the SW MINUS then? Good old Xantrex.
thanks
Hugh
Hugh:
I apologize for disagreeing, but the SW PLUS does not have internal
relays (the PS does not either). It relies on an external AGS
module tha
ambient if insulated.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches
r the theory anyway.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wre
ew
edition out last month so I will download and try that.
http://www.morningstarcorp.com/en/support/item.cfm?ItemId=400
Seems pretty self-explanatory to me but the manual is there for reference too.
I did not know that there was any other way to set them up.
--
Hugh Piggott
Scoraig
http://w
wild swings in voltage.
Not sure how clever a wizard would have to be to figure out all of
the circumstances in such cases but it does not take long to load and
test a new configuration on site in good test conditions. A few more
example configurations would be helpful.
cheers
Hugh Piggott
roach to parallel strings that has not been mentioned here
is to put in cross bonds to link the strings at each battery or cell
terminal. That way a single cell cannot affect the whole string, it
just pulls down the cells in parallel with it - which are a lot like
an extension of the same cell i
Hi Roy,
Hi temperatures will hit the battery capacity but
will the battery efficiency be that much
affected? If the battery capacity is inadequate
then you need to compare the aircon running cost
to the cost of buying a 10% larger battery.
Don't you?
Cheers
Hugh
Bob is correct,
o settings in a
slightly random fashion.
I am also puzzled by the above statement where Larry charges each
battery string at constant current, unregulated voltage. I wonder
what current is suitable?
thanks
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk_
echnology on an opportunity charging system where the
battery may be in any state of charge when the wind starts blowing,
or sun starts to shine.
best wishes,
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power m
p is 77-80°F. Lower
than normal temps. will reduce capacity,
slightly extend life, require a higher recharge
voltage, & cause SG readings to be adjusted
down. HIGHER TEMPS HAVE THE OPPOSITE EFFECT".
--
Hugh Piggott
Scoraig
http://ww
urther pointers...
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
At 07:36 -0700 24/4/11, jay peltz wrote:
Hi Hugh,
The other thing to consider with heat is that higher temperatures
while increasing capacity also decrease life ( more active chemical
reactions, and conversely lower temps increase battery life.
Yes this appears to be the only downside of
ttery properly without drying it out.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wr
ly without?
thanks!
Hugh
At 18:41 -0300 25/4/11, James Surrette wrote:
Content-Type: text/html; charset=US-ASCII
Content-Description: HTML
Hi Hugh,
Here is the charging information for our AGMs.
Please let us know if you need anything else.
<http://www.surrette.com/content/agm-faqs&
HI Hugh and all
As Hugh knows the Outback FNDC was meant for such operation, Apollo
can track the SOC but can not control off SOC.
I have been studying the FlexmaxDC manual and it is a wonderful
measurement instrument, but it has no direct communication with the
charge controller (set
ould
actually damage a sealed battery. Then I would simply charge them as
hard as the wind/sun allows while avoiding doing that.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine
List Address: RE-wrenches@
Hi Bill,
Hugh, .25 x C20 would be a C80 rate
Sorry I did not mean that, and I do not think that is what the
manufacturers instructions mean either. They mean 0.25 times the C20
capacity. That is closer to the C4 rate! (And they say 'up to 0.35
x capacity' ).
All controllers
At 13:10 -0700 28/4/11, Starlight Solar, Larry Crutcher wrote:
Hugh,
One last point about the Solar Boost IPN product: Once you have
programmed the 2512iX charge controller from the IPN Pro, the
controller retains the information and can be installed as a
stand-alone unit. That means you can
ttery whilst preventing the balloon
of gas in your dramatic photo.
I will read the document that you reference (about thermal runaway)
carefully. I am sorry if I seem a slow learner. This list is an
invaluable resource for the industry. I like to ask naive questions
and I get a deeper underst
lers.
To me the issues of unbalanced charging are much worse for batteries
in series than they are for batteries in parallel. Now I will go and
hide from the wrath of the list :-)
have fun,
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk___
List
demands of variable renewable inputs and limited,
expensive electricity availability. Loads that turns off at low Hz
and others that turn on with high Hz could be very good for the grid.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsor
I've got a copy of the 'Handbook of Homemade Power' 1974 by the staff
of mother earth news. But you can't have it,
nah.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List
battery, given enough surplus energy
availability (which is usually the key thing for battery health).
Just a thought.
The snag is the cost. ho hum.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
L
% efficient and probably ending in tears.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cg
25% of the time and it takes 4 times
longer for everything to go pear shaped.
Another option I've been reading up on is a Battery Equalizer/Battery
Balancer.
This seems like a valid solution, yes.
best wishes,
--
Hugh Piggott
Scoraig
http://w
;t be long before Dairy Queen will be selling
inverters with a large shake.
Jeffrey Yago, pres.
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options
and before recharging, ask them to check each battery with this
meter? That would identify or rule out the intermittent internal
resistance theory. If it exists, it's just in one battery.
Presumably.
Hugh
Larry, the customer has been fully charging and equalizing every
week to two weeks fo
More about the subject here. http://scoraigwind.co.uk/?page_id=637
Best wishes,
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
h
sible that the NEC thing does
not required you to look at float voltage.
all the best,
--
Hugh Piggott
Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settin
a
new wiring system called Protective Multiple Earthing where the
ground and neutral are combined into one wire (saving on cost). This
has the interesting side effect that the whole house will become
'hot' in the event of a failure of this one conductor.
--
Hugh Piggott
Scora
fuses, breakers and switch contacts.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/
e-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk___
portant to have a voltage regulator on the hydro. There
is also plenty of dump power to be allocated.
I got my controller from "Nigel Smith" .
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List spo
is reached. So...if you set that for a high
value the same high rate would be present not only when the battery
is highly depleted but also when the battery is approaching 80%
state of charge. That seems scary to me.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.sc
ted to the largest house or the nearest.
Seemed to work pretty well. Better than I expected actually. The
inverters behaved gracefully under system overload for example. If
the hydro flow drops off a bit they do not crash the system.
have fun.
Hugh
Esteemed fellow wrenches: May we put
guaranteed to have a lethal voltage between the generator
frame and house ground. That doesn't seem likely to be the safest
solution although it might be the simplest to install.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.
tant death due to carelessness.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/
e negatives,
to parallel the battery, then the only issue is where you connect
the charge source and/or inverter."
Hugh,
The connection is very easy, if you look at the photos on the page I
linked to the connections to the inverter breaker (which is where I
also connected the charge source) c
e difference in mentality between solar users (who count out the
amp hours and know exactly what they have to work with each day) and
wind users (who can party like mad sometimes and then have nothing at
other times).
Hugh
Hugh,
Feeding off diagonal corners, as you are describing, only keep
at do I tell my customers about the end-of-discharge voltage for
sustainable cycling of their Rolls batteries? And is it temp
compensated?
thanks
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List sponsored by
on of such
devices after a few partial charge swings up and down over period of
days. So the reality is that we rely on inverter LBCO settings or
rules of thumb such as "never let the voltage drop below 47" to
ensure that the batteries do not get abused.
Best wishes
Hugh
Hi Hugh & W
ain. I do have a few more
that I will save for now. Thanks for any more comments.
best wishes
Hugh
Hi Hugh, When discussing battery characteristics with a chemist at
my supplier years ago I was told the capacity at 0 deg c is around
50% of that at 25 deg c because the ion transfer rate
w
battery disconnect, genstart, etc). I would be interested to know if
this type of temperature compensation exists and indeed whether it is
legitimate in terms of sustainable battery management.
Hugh
Hugh,
Sorry if you found my response limited but have been traveling since
early this am
scharge rate is reduced. To what
extent is the capacity actually lost by using high discharge rates
and to what extent is it just a voltage effect that impacts on the
terminal voltage, rather than the actual chemical state of the
battery?)
I hope you can follow my descriptions.
--
Hugh Piggot
ittle bit like current of 10 amps entering one end of a piece
of wire and only 9 amps coming out the other end. I understand that
the volts go down due to voltage drop (in this analogy) but loss of
current is entirely a different matter.
Thanks for any help with this rather obscure question.
ent. Fair
enough but what are the numbers used in the negotiation, and are they
temperature dependant?
Thanks, Joel for the reading matter which I am working on! I hope to
become wiser in due course.
best
Hugh
At 17:45 -0800 15/1/10, Joel Davidson wrote:
Some charge energy is lost in heat
not true.
That's probably enough for now, if anyone has bothered to read this
far. Thanks for any reactions.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine
List Address: RE-
n-member Julie Haugh:
- - - - -
Hugh Piggot writes:
According to Peukert's law (and manufacturers' data bears this out
well) the capacity of a battery depends on the rate of discharge.
Everyone who knows anything about batteries knows that the capacity
is specified at a certain r
he backup.
Thanks again for all the input to this thread.
best
Hugh
At 11:47 -0800 18/1/10, Kent Osterberg wrote:
Hugh,
You may be interested in this article "A critical review of using
the Peukert equation for determining the remaining capacity of
lead-acid and lithium-ion bat
age. It does not tell you the SOC of
a battery. This last is a very hard thing to ascertain.
:-)
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.r
shows windspeed and other data.
http://www.logic-energy.com/
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
spreadsheet or even do the
calcs quickly in your head to a useful level of accuracy once you
have a bit of experience. As I say its a lot easier with metric
units where the wires sizes are multiples of 1 sqmm, and about 28
metres of that stuff is one ohm.
--
Hugh Piggott
Scoraig Wind El
ct reverse power and add a dump load?
Seems a shame to kill the renewable input when the grid is down.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenche
I have used a load resistor on a voltage controlled relay VCS from solar
converters and a USB data logger. I only used the relay because I didn't want
to kill the battery or sit watching. USB voltage loggers are good things to own
anyway.
Hugh
On 6 August 2017 17:18:51 BST, Steve Hi
tres
is a better choice for normal ambiences.
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-
i...@solarenergy.org
Maybe I will get to meet some of you there.
Best wishes,
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Optio
to feel any shortage of solar energy. Days are
long. Charge current is low.
As I said it’s a very interesting thread on which I often feel like a lone
heretic.
cheers
Hugh
> On 13 Sep 2018, at 02:55, Sindelar Solar <mailto:al...@sindelarsolar.com>> wrote:
>
> Bill and all,
I am trying out an insulated box and small heater. It doesn't get very cold
in West Coast scotland so 120W seems useful. Also automatic vents used on
greenhouses, to open up the sealed box.
On Fri 17 May 2019, 18:09 Dave Angelini Offgrid Solar,
wrote:
> The risk may be worth it if the battery is
pieces and try to figure out a hardware failure but
I wonder if anyone has seen this and can give me a clue?
cheers
Hugh
Hugh Piggott
Scoraig Wind Electric
Dundonnell
Ross shire
IV23 2RE, UK
+44 77 1315 7600
h...@scoraigwind.co.uk
www.scoraigwind.co.uk <http://www.scoraigwind.co
they do seem to need it.
cheers
Hugh
Scoraig
Scotland
> On 9 Mar 2020, at 18:20, Ray wrote:
>
> We had one last year with a bad relay, the customer had been charging a Tesla
> EV through it (pass through from the grid) and smoked the relay. It was
> pretty obvious, the clear rela
Hi All,
Just to wrap this one up I can report that the problem was in the control board
in this instance, and having replaced this board it is now working again.
Thanks for all who helped with advice, especially Jay and Kris.
cheers
Hugh
Hugh Piggott
Scoraig Wind Electric
Dundonnell
Ross
ge depending on various factors, one of
which is whether it is "separated" (floating and well insulated) or not.
Many of us work with battery systems, and not everyone is a certified
electrician. I'd love to know some ground rules.
thanks!
Hugh
Hugh Piggott
Scoraig Wind Electric
defined?
What other factors are applicable such as status (homeowner, installer,
paid/unpaid) and location (inside home, wet location, etc)?
Thanks for any observations.
Hugh
On 5 Mar 2014, at 08:34, Hugh Piggott wrote:
> hi All,
>
> I am trying to find some general statements that ca
hi wrenches,
I am installing some load controls for a client who has a FM80 controller. I
don't have experience with this product. It has a 12V aux output that I wish to
drive an SSR but the wiring is complicated by the fact that this SSR also needs
a power supply as well as a control signal. I
Hi Hugh again
Just to clarify the set up:
The SSR controls the AC power from the inverter to the heating load. It
switches partway through each half cycle and thus controls the power to the
load.
The input to the SSR requires a power supply 8-32 V present all the time it is
working. I suppose
to do this for sure.
I would check the potential of the aux negative but I don't have any such
controllers here on scoraig and I want to know the score before I go on site to
install the SSR.
thanks to all
Hugh
On 6 Dec 2014, at 00:09, jay peltz wrote:
> Hi Hugh
>
> I use 3-32vd
PG is the last resort for us.
Hugh
On 4 Dec 2014, at 01:14, Dave wrote:
> I'm looking at Bosch # 16083 ($ 765) dishwasher - any problems running this
> on OutBack inverter power?
>
> and also a Samsung, or LG, front load clothes washer. I'm a little gun shy
> with t
ne is just good for peak usage and
the fact that there is another house connected.
good times! My favorite thing (almost) about renewable energy is the fact that
sometimes there is way too much of it.
Hugh
On 7 Dec 2014, at 16:43, frenergy wrote:
> Hugh,
>
> We've d
neutral, but where a number of
diverse circuits are connected there will be some imbalance, so you need a wire
there, but it need not be as heavy as the 3 “hot" ones.
cheers
Hugh
Hugh Piggott
Scoraig Wind Electric
Dundonnell
Ross shire
IV23 2RE, UK
+44 77 1315 7600
h...@scoraigwind.
fix to it using
“genman mode”.
I just wonder if you have witnessed the process and checked whether the
generator’s own built-in cool down period could be the cause.
cheers
Hugh
> On 30 Dec 2016, at 00:43, Lou Russo wrote:
>
> Thanks to all for the input and suggestions, it is much ap
lies to two strings that
are connected each to its own regulated supply. If a tiny difference in
voltage matters (which I doubt) then you will have the same issues with a
single string.
What am I missing?
thanks
Hugh
___
List sponsored by Home Pow
Interesting thread!
We are having some success with a Kestrel turbine here on Scoraig
I second the idea that Ampair offer a modest but very robust range of products
for high wind sites.
cheers
Hugh Piggott
On 3 Apr 2012, at 20:36, Richard L Ratico wrote:
> Does anyone have any experie
I have installed a lot of BP 380 and BP 485 panels that I think have the same
frames. But it's all on a what you can find basis now since they have given up
on the retail market, I am told.
cheers
Hugh (with a nice array of 275s still doing good work on my old house)
On 13 Apr 2012, at
First time I cycled my BYD batteries I got 20% more than rated kWh out of them.
Based on third party Ah reading.
Hugh
Get BlueMail for Android
On 24 Aug 2020, 23:32, at 23:32, jay wrote:
>
>Dear lithium experts
>
>Do lithium LFP or NMC batteries have a break in period ( a cer
78 matches
Mail list logo