At 12:16 -0700 30/11/11, Larry Crutcher,
Here's a scenario: Sun is up and voltage rises slowly to the diversion controller set point. PWM starts and maintains the voltage. Current continues to increase but the load is keeping the voltage constant until the controller is overloaded.

I think the point that most people don't get is that you can't overload the controller if you choose the correct dump load. You can get to the point where the dump load is fully turned on (100% duty cycle) and then it is 'overloaded' in the sense that it has not further ability to limit the rise in voltage. However it will not be damaged. Then the voltage will rise further and hopefully another controller will start dumping or something good will happen to protect the batteries from damage.

If you have 2 controllers with dump loads that can handle 150% of the incoming PV current between them then you can be sure of never 'overloading' them. But it will not matter if you 'overload' one before the other comes on because it will never draw more current than the dump load takes at the prevailing voltage.

Here is a calculation:

3.8 kW at float voltage 54 volts gives 3800/54 = 70.4 amps.
According to NEC you multiply this by 1.5 to get 106 amps.
Now you need to choose dump loads that will each dump at least 53 amps at 54 volts. (1.02 ohms, maybe one ohm plus resistance of leads.) These will be the same loads as will do 60 amps at 61 volts and they are the lowest resistance you can safely use with the TS60. If you plan to EQ at voltages higher than 61 then you need to use higher resistance and you cannot meet the NEC target of 150% of incoming current at float voltages.

That's how I see it anyway. It's possible that the NEC thing does not required you to look at float voltage.

all the best,
--
Hugh Piggott

Scoraig
http://www.scoraigwind.co.uk
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to