Thanks Dave,
We have installed many systems and we only had this problem with Sanyo
modules and we had a rash of these crop up about the same time-frame and
the issue only affected part of the array. Panasonic denied our claim
because they stated it was a lightning strike. The cause is
Yes I did Brian, with and without the diode. That's how I found what I
thought was a bad diode.
On Thu, Jul 6, 2017 at 4:21 PM, Brian Mehalic wrote:
> Did you test the voltage of the individual cell banks in the module with
> the diodes out?
>
>
> Brian Mehalic
> NABCEP
The diode check on a dvm is useful but may not show a diode breaking down
at higher voltage. Yes lightning can open up the tabs or connecting foil
inside a solar panel. It can do alot more than that! One of the best
reasons for using an SPD at the array is also preventing the latent damage
that
Did you test the voltage of the individual cell banks in the module with
the diodes out?
Brian Mehalic
NABCEP Certified Solar PV Installation Professionalâ„¢ R031508-59
520.204.6639
Solar Energy International
http://www.solarenergy.org
SEI Professional Services
http://www.seisolarpros.com
On
Hi Brian,
Thanks for the info. Yes I tested the diode properly. I was concerned that
I needed to test the diode under a load to get a valid test.
Taiyoko
On Thu, Jul 6, 2017 at 4:14 PM, Brian Mehalic wrote:
> Did you use the Diode Test function on the meter? If the
Did you use the Diode Test function on the meter? If the diode is good you
should see around 0.4-0.8 V in the forward bias, and OL in reverse. If it
is bad (open) you'll get OL in both directions, and if it is shorted closed
you'll get the 0.4-0.8 V reading in both directions.
Shorted closed
6 matches