Greetings list,
I'd like to just offer yet another opinion on the thread going on regarding
the SC Sofa Store fire and a question earlier on what do / can local
authorities do when / if they find a building with an over taxed or under
designed system in it.
Presumably if you are performing inspec
Need more info. Where is coming from? What is it crossing? If it runs thru
the building there is fire resistant wiring. It must be protected from fire.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Wednesday, June 20, 2007 4:25 PM
Depending on which code you're using, the back-up power circuit from a
generator or alternate second source must be rated cable or
concrete-encased. Not sure about the primary ...
Steve Leyton
PROTECTION DESIGN & CONSULTING
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTE
Does the electric power source for a fire pump need to be encased in
concrete? Thanks Tom
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
Thanks guys, I was thinking a combined line needed to have the domestic
included for sizing the line.
Jamie Seidl
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Wednesday, June 20, 2007 3:54 PM
To: sprinklerforum@firesprinkler.org
Subj
Jamie - in the '02 edition, section 6.3 may be what you're looking for.
Ed Kramer
Littleton, CO
>
>
>I was just glancing thru 13D and I can't find the section on domestic
>demand. Is domestic demand required to be included in the calculations
>for 13D?
>
>Jamie Seidl
>___
Jamie,
With 13D, usually no domestic demand is required. The exception is when a
multipurpose piping system is being used and it is serving more than one
dwelling unit. See 13D 6.3 2002 ed.
Bob Knight
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jami
Frank-
I've used the NCI unit, nice but you can't calibrate it.
I was asked to check one against a playpipe once by FM (at the convention
ctr. here in Boston, site of the NFPA show) and it was WAY off, not even
close at multiple flows, both under and over. I wouldn't recommend it. I
have the pol
Craig,
Great question. The answer is yes we can legally stop them from storing
illegally. If the building is sprinklered and the commodity changes,
they have to prove to the AHJ that there is enough density in the system
to handle the commodity. I explain to the responsible party that they
need to
John,
I'd appreciate hearing some of the feedback you get. I'm looking at a
job where that might be appropriate.
At 08:12 AM 6/20/2007, you wrote:
Dear Forum,
I am looking for feedback from sprinkler contractors who have
installed the Viking "Cold Storage System" using K-25 ESFR heads and
I was just glancing thru 13D and I can't find the section on domestic
demand. Is domestic demand required to be included in the calculations
for 13D?
Jamie Seidl
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkl
Ditto.
I see it regularly. 11,500 square foot spec building with 25 foot
ceilings and 14 foot tall doors. Just under our local requirements for
sprinklers -- actually one guy split his building into three so he
didn't have put sprinklers in. Nearly every time I see a new tenant move
in, I stop in
This is kind of wordy (those who know me well, please stop snickering),
but I thought I'd share it anyway. Thanks Mark for calling attention
to that article; below is my correspondence to the writer.
To: Jason Ryan, The State
Re: The Sofa Super Store Fire
It appears that you were quoting other
I'm designing the suppression system for a new 17 story building. The
building sits next an existing 4 story building. The separation between
the two is just two feet. Our wall has a two rating and their wall also
has a two hour rating. However, their wall has an ERIS finish on it.
The t
Absolutely.
They are in violation of their Certificate of Occupancy if they have
non-approved conditions.
We just went through a situation were we found an excessive amount of
plastic pallets and totes stacked in a warehouse to full height (25') in
a 300,000 sq.ft. building. The area that contai
FYI, there is an article at
http://www.thestate.com/154/story/96873.html
which included the following statement:
"Given the swiftness and ferocity of the furniture-fueled fire,
officials speculated, the extra water might not have mattered."
I have sent the writer my opinion about the veracity
>From the pics, no, not historic. Looks like a typical metal/block
siding, steel bar joist type big-box building. Nothing special at all.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Dir
It will come down to the fact that as the local AHJ said, when the
building was built sprinklers weren't required. And if
not required why waste the money on something that will never be used.
Since there are no retrofit laws on the books, no requirement to update
the building. Do what you wan
Anyone know if this building was considered or registered as historic?
That might explain the absence of sprinklers, but not the permission to
occupy with a furniture warehouse store.
Steve Leyton
PROTECTION DESIGN & CONSULTING
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PR
Neil:
Most departments have an entry protocol. Unfortunately, the initial
reports indicated possibly 2 persons trapped. In fact it was one
employee of the furniture store and he was rescued fairly quickly. When
we receive a report of person(s) trapped, we are required to assess the
tenability an
On NPR as I drove home last night their report had extensive
discussion about no sprinklers, that they had not been required when
the building was built, that they would be required if the building
were to be built now and that the entire tragedy would have been
avoided if the building were sprink
It is scary that as many as 15 firemen were in an unsprinklered building
when the roof collapsed. There could be 15 dead firemen instead of 9.
I have never been a fireman but don't they have procedures for entering
burning buildings, especially ones without sprinklers.
Neil Stong
STONG FIRE PROTE
In cases like this, we've been required to put a suction supply control
valve. The valve has a sensing line that ties to the suction side of
the pump and if the supply pressure drops below 20psi the control valve
will throttle the discharge to maintain that 20 psi.
The 20 psi pressure limit (I b
Local news media reported that the building was NOT equipped with fire
sprinklers. I must commend their report. After a recent industrial
fire and not one word on whether the facility was protected by
sprinklers I sent an e-mail to the reporter making an inquiry and adding
a brief overview of spr
Dear Forum,
I am looking for feedback from sprinkler contractors who have installed the
Viking "Cold Storage System" using K-25 ESFR heads and propylene glycol in
pre-action system(s) in freezers. Please respond off-line via email or phone.
Thanks!
John R. O'Connor, SET
National Fire Sprinkle