I don't know the reason of of limiting coverage area protected by one
sprinkler system. For example why should I determine maximum 52,000 sq.ft for
one sprinkler system in an ordinary hazard area?
imagine a 125,000 sq.ft factory which is an Ordinary Hazard Group II
occupancy with a
The British Standard allowed 1000 heads regardless of area or height.
Many items of the codes are many years old. Nobody questions them.
Let me offer one probable cause.
If a sprinkler is knocked of, the whole system is off until the sprinkler is
replaced. It takes more time to drain the
George,
Thanks for your prompt reply, thanks Dan too.
Sorry I forgot to search the forum, before posting my question, I will search
next times before posting, thanks for reminding.
Reza
George Church [EMAIL PROTECTED] wrote:
There's been some priot threads on this topic related to # of
The exact numbers (40,000 and 50,000 sq.ft.) come from 400 sprinklers at
either EH (100 sq.ft.) or OH(130 sq.ft.) spacing. This has been around
for many,many years and is a somewhat arbitrary number. It was done to
reduce the area affected during a sprinkler impairment and also to allow
a
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]
Sent: Saturday, September 15, 2007 7:46 AM
To: Thomas Reinhardt
Subject:
http://www.ocolly.com/2007/09/11/roll-out-the-bucket-brigade/
___
Sprinklerforum mailing list
There was a proposal submitted to the committee during the last open cycle
(2007 edition) where the submitter recommended changing the 52,000 sqft
limitation to 150,000 sqft.
The proposal noted that 3 floors of 50,000 sqft each, with one control valve in
permitted now - so why not permit the
I have a copy of the NFPA 13R ROP but I am having problems posting it to
the group.
Email me off forum [EMAIL PROTECTED] if you want a copy.
Pete
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan
Peterson
Sent: Thursday, September 13, 2007 1:32 PM
To:
Reza,
Whether or not shutting down George's 500,000 sqft system is good
practice or not was not a part of your question. 52,000 has been the
number for ordinary hazard and 40,000 for extra hazard. Light hazard
is a johnny come lately and when it came along logic would dictate
that the maximum be
If you know
Please tell me the intent of the 6.4.6 limiting the use of bushings to reduce
pipe sizes.
If there are existing ¾ reducers and ½ sprinklers are needed, what
detrimental effect would there be in using a ¾ x ½ bushing? I fail to see the
potential negative impact.
From the NFPA 13 Handbook -
The intent of 6.4.6.1 prohibits the use of bushings where a one-piece
reducing fitting is commercially
available at the time the system is installed.
For other than the circumstance cited in 8.14.19.2, in which bushings are
temporarily installed
to facilitate an
As I have mentioned before on this forum... We have a severe shortage of
local AHJ's here who can read between the lines. It is either taken
literally or ignored.
In this case there are 3/4 inch slip x thread adaptors installed for head
adaptors and a bushing could not protrude above the brass
Does anyone know of a spare head box that can stand up to a corrosive
environment?
Standard head boxes that are available as a standard do not do well
against direct exposure to the elements.
Any help/advice is appreciated
Pete Schwab
Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into The
We are in the process of designing a 13D system for a house that uses a well
for water supply. We are using a pump/tank set up and no float valve for the
tank connection to the well. Since this is a stand alone system and no
connection to a water supply, is a site plan required? I can't find
Plastic box with the heads put it in - like a tackle box without the tray?
Get it in red, then just add a label indicating it's spare heads.
glc
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Pete Schwab
Sent: Monday, September 17, 2007 11:39 AM
To:
Actually, the 2007 edition of the standard was changed slightly in this regard.
Please see the following sections.
6.4.6 Reducers and Bushings.
6.4.6.1 Unless the requirements of 6.4.6.2 or 6.4.6.3 are met, a one-piece
reducing fitting shall be used wherever a change is made in the size of
Thanks to my dears George, Joe, Ed, Ron, Bob, Dan special thanks to Travis
who is helping me more than I deserve!
I completely got the reason for this limitation.
Thanks to all,
Reza
I LOVE THIS FORUM!
Ron Greenman [EMAIL PROTECTED] wrote:
Reza,
Whether or not shutting down
A health club with weights, spinning,
sauna, raquetball, etc.
is this A-3 per 2003 IBC?
is it Assembly per 2006 NFPA?
seems to be.
just making sure we are not denying
a B-occupancy where others commonly
assign B-occupany to health and fitness
clubs.
scot deal
excelsior fire engineering
We've done the last two health clubs as A-3.
Your mileage may vary.
Jim Kettler
Buckingham Twp. FMO
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of å...
Sent: Monday, September 17, 2007 2:30 PM
To: SprinklerFORUM@firesprinkler.org
Subject:
Whats the occupant load ?.
John Drucker
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å...
Sent: Monday, September 17, 2007 2:30 PM
To: SprinklerFORUM@firesprinkler.org
Subject: health and fitness clubs
A health club with weights, spinning,
One aspect is that there is a magical trigger value of 50 before an
Assembly occupancy is assigned.
Roland
On Sep 17, 2007, at 11:48 AM, John Drucker wrote:
Whats the occupant load ?.
John Drucker
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Bingo, That's why I asked.
2003 IBC Section 303 Assembly Group A
303.1.1 Nonaccessory Assembly Use, by less than 50 Persons shall be considered
a B Occupancy.
John Drucker
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins
Sent:
There was one of the after market providers that used to have a
plastic sprinkler head box.
ARCO or FPPI ??
Mike Brown
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Pete
Schwab
Sent: Monday, September 17, 2007 11:39 AM
To:
22 matches
Mail list logo