Re: Pipe passing thru Electrical Equipment Rooms

2009-04-09 Thread bverhei
What did the PE's spec's say? Bruce V. - Original Message - From: "Thom McMahon" To: sprinklerforum@firesprinkler.org Sent: Tuesday, April 7, 2009 8:32:36 AM GMT -08:00 US/Canada Pacific Subject: RE: Pipe passing thru Electrical Equipment Rooms Exhibit 110-21,22,23 indicate the sp

RE: Storz

2009-04-09 Thread Ken Holsopple (forum)
NFPA 13 2002 16.2.1.10 - Piping BETWEEN exterior FDC and check valve in the fire department inlet pipe shall be hydrostatically tested in the same manner as the rest of the system. Ken Holsopple Rowe Sprinkler Systems, Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.o

Re: Storz

2009-04-09 Thread Forest Wilson
Fdc piping is supposed to be part of the acceptance test. Should be hydro tested. --Original Message-- From: Forest Wilson Sender: sprinklerforum-boun...@firesprinkler.org To: sprinklerforum@firesprinkler.org ReplyTo: sprinklerforum@firesprinkler.org Subject: Re: Storz Sent: Apr 9, 2009 7

Re: Storz

2009-04-09 Thread Forest Wilson
Are you staying that Stortz is not UL listed? How could this be possible? --Original Message-- From: Ken Holsopple \(forum\) Sender: sprinklerforum-boun...@firesprinkler.org To: sprinklerforum@firesprinkler.org ReplyTo: sprinklerforum@firesprinkler.org Subject: RE: Storz Sent: Apr 9, 200

Idaho Senate kills push to dump International Fire Code

2009-04-09 Thread Bob Knight
Idaho won a victory for the Fire Protection Industry today. We still have work to do as the Senate wants to revisit this issue to look at using a "little hammer" later this summer. Read the full story here, http://www.firebyknight.com/news.htm. Bob Knight, CET (208) 318-3057 b...@firebyknight.com

Re: Storz

2009-04-09 Thread Tiffany M. Winner
Can anyone tell me what I need to do to unsubscribe? I have typed that in the email subject line and sent several times but I am still getting these. Sent from my iPhone On Apr 9, 2009, at 5:58 PM, "Ken Holsopple (forum)" wrote: > Instead of listing, why not a 150psi (higher if particula

RE: Storz

2009-04-09 Thread Ken Holsopple (forum)
Instead of listing, why not a 150psi (higher if particular system requires it) Hydrostatic test added to the acceptance test? Ken Holsopple Rowe Sprinkler Systems, Inc. Speaking or Storz, did they ever get listed for use as fire protection equipment? It must be great to have such strong dema

RE: Storz

2009-04-09 Thread Ken Holsopple (forum)
I am with you John, however I think the concern is more of a manufacturing thing. If you get a Storz connection from "Billy Bob's House of Hoses and Stuff", will it take the 150 psi or blow apart instantly. Leaving you with no connection at all. Casting the piece is easier than confirming the alloy

RE: Fire Protection Performance Intent - 2002 NFPA-13- 8.14.5.1 & 8.14.5.2

2009-04-09 Thread John Drucker
Mark, You're on to something; "There is also the chance of a small leak under high pressure becoming a cloud of atomized combustible fluid, which in turn can find an ignition source and become a blow touch of sorts." Anyone else ? John Drucker -Original Message- From: sprinklerforum-bo

RE: Storz

2009-04-09 Thread Ken Holsopple (forum)
>Speaking or Storz, did they ever get listed for use as fire protection >equipment? While I understand the original question, I have to ask another two If we left a 4" pipe w/ NPT threads sticking out the wall cuz the fire department would bring there own adapter, would that make it bett

RE: 100ft from FDC to hydrant?

2009-04-09 Thread John Drucker
2006 IBC-901.4 Threads. "Threads provided for fire department connections to sprinkler systems, standpipes, yard hydrants or any other fire hose connection SHALL BE compatible with the connections used by the local fire department." But to answer the question, not exactly. The Storz fittings bein

RE: Fire Protection Performance Intent - 2002 NFPA-13- 8.14.5.1 & 8.14.5.2

2009-04-09 Thread Chris Cahill
What's odd is you assume there is some connection between goals of fire protection and code requirements. And an AHJ cares about the reasoning? You my friend are a rare bird. I suppose like Mark said it has something to do with atomized fuel? The other thing might be debris alone isn't going a

RE: Fire Protection Performance Intent - 2002 NFPA-13- 8.14.5.1 & 8.14.5.2

2009-04-09 Thread Mark Sornsin
I can only go on a limb and suppose that the combination of combustible fluids with the potential debris pile is of more concern that just the debris pile...(?) The fire hazard from the combustible fluids relates to the potential leakage of fluid and possibility for a pool fire. There is also

RE: 100ft from FDC to hydrant?

2009-04-09 Thread John Denhardt
Agree. I have not found a listed one. John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -Original Message- From: sprin

Re: 100ft from FDC to hydrant?

2009-04-09 Thread Roland Huggins
Speaking or Storz, did they ever get listed for use as fire protection equipment? It must be great to have such strong demand by the AHJ that you don't have to bother with listing your device. I wonder if Mastercard will use it in their ads? Roland On Apr 9, 2009, at 9:41 AM, Thom McMahon

removed

2009-04-09 Thread Fine, Michael
OK Michael Fine Mechanical Engineer 100 South Wacker Drive, Suite 1400 Chicago, Illinois 60606 Phone: 312-578-2402 Fax: 312-558-1849 http://www.greeley-hansen.com/ ___ Sprinklerf

RE: Fire Protection Performance Intent - 2002 NFPA-13- 8.14.5.1 & 8.14.5.2

2009-04-09 Thread Craig.Prahl
Yeah it is kind of confusing: 8.14.5.1 requires the sprinkler due to accumulation of debris in the pit. 8.14.5.2 does not require the sprinkler if there' no combustible hydraulic fluids. Seems that if there is no combustible fluids then debris doesn't want to hang out in the pit. T'would be i

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Ken Holsopple (forum)
>"Min. Demand 6000 Gpm @ 160 Psi" If the time comes when that much water/pressure is needed, then the pipe it is supposed to distribute through is already on the ground with the rest of the steel me thinks. Hydrants side by side to feed the engines that are stacked on top of each other? 12" Stor

RE: 100ft from FDC to hydrant?

2009-04-09 Thread George Church
We did bid on a very large pump for a local University years ago. Ironic, told em to do it years earlier, before they built 6 more buildings with 5 more fire pumps. FGOL has been there, shut down, people getting feet wet 2 blocks away. Anyway, it was fun pointing out the 6-way FDC they had with 2.

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Thom McMahon
Yeah! I haven't seen any Multi port Storz connections yet. Nice free standing 6 Storz x3 w/chrome to a 12" Dia. riser at the front gate to the property. Nice little sign, "In Case of Fire please connect three largest pumper trucks to this connection and crank em up!" "Min. Demand 6000 Gpm @ 160

RE: 100ft from FDC to hydrant?

2009-04-09 Thread George Church
Yes, I believe we've kicked this one around before and even Roland has pronounced that the large lady sang. I'll be counting on that outa the archive as we skinny a 6" FDC down to 4" on a pump we're doing now. Neither 4" or 6" is going to make a dif if our 3,000 at 160 doesn't start, and the fire c

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Thom McMahon
Just another thought, if your 3000Gpm fire pump failed, how many fire dept. even have a pumper capable of replacing that volume? Multi connections and multi pumpers? If the pump failed, the battle was most likely lost before the first engine arrived. Monitor time!! Supplemental only. Thom McMahon,

Re: 100ft from FDC to hydrant?

2009-04-09 Thread Roland Huggins
better yet - look at the Annex at A.6.8.1 Ron - one or the other check will not be open expect for that rare occurrence with the supply curves match. Roland On Apr 9, 2009, at 8:21 AM, Reed Roisum wrote: > NFPA 13, 2007 ed. Handbook 6.8 > > Reed A. Roisum, CET > Fire Protection Technician > >

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Reed Roisum
NFPA 13, 2007 ed. Handbook 6.8 Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

Fire Protection Performance Intent - 2002 NFPA-13- 8.14.5.1 & 8.14.5.2

2009-04-09 Thread John Drucker
Members, Could someone please explain the fire protection goals of 2002 NFPA-13- 8.14.5.1 and 8.14.5.2 with regards to combustible hydraulic fluids. Now before you say "Duh, this code officials gone mad, to put the fire out of course" I'd like you to identify the fire hazard in detail, the exte

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Jessica Lutz
Some commentary states that the FDC is not intended to be a substitute for the normal water supply (GPM) but a supplementary source used to boost pressure. With that being the intent, the smaller size makes more sense. With the test header, you are testing the actual flow (gpm) characterist

RE: 100ft from FDC to hydrant?

2009-04-09 Thread George Church
Because you could have 1000 GPM coming in from street and boosted by a fire pump to 150, and the FDC chk open and 500 GPM coming in off pumper, 1500 going up riser to 50 open heads. Without a fire pump, tho- you may be right. Too much in my head with other stuff to clear it and think it thru, so t

Re: PA IRC Hearings-your support is needed

2009-04-09 Thread Ron Greenman
PA is not an isolated case. There is a Washington Residential Sprinkler Coalition of which I'm a member. NAHB hit certain target states (those most likely to pass legislation AGAINST sprinklers including Arizona--ironically considering Scottsdale) early and hard. They caught us underfunded, underst

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Fletcher, Ron
The riser check is required to prevent re-circulating the water from the FDC back to city main and thus the hydrant used by the pumper truck. How could both check valves could be open at the same time? Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ 85024 -Original Message- From: sprin

RE: 100ft from FDC to hydrant?

2009-04-09 Thread George Church
If you have enough flow and pressure that a FD pumper can't open the check at all, then you don't need the supplement, I suppose. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron Sent: Thursd

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Fletcher, Ron
How do you supplement pressure without flow? There is a check valve held shut by the incoming system pressure. If enough pressure is delivered to the supply side of the FDC check to open won't the check valve in the riser close? Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ 85024 -Origin

RE: 100ft from FDC to hydrant?

2009-04-09 Thread John Drucker
Ron, Fear not the IBC/IFC have it covered, well at least the location criteria. For those in NJ this section has been amended by the state to include height and flush type connection requirements amongst others. John Drucker Fire Protection Subcode Official New Jersey 2006 IBC SECTION 912 FIRE D

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Autry, David
"Ever hear of a save because the water supply into the building was impaired and the arriving fire dept. used the FDC as the secondary supply?" Never have. David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Craig.Prahl
Some commentary states that the FDC is not intended to be a substitute for the normal water supply (GPM) but a supplementary source used to boost pressure. With that being the intent, the smaller size makes more sense. With the test header, you are testing the actual flow (gpm) characteristics

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Fletcher, Ron
NFPA #13 gives the same amount of attention to the placement of the FDC as it does it's adequacy to handle the flow required for the hazard, none. If the location is critical then shouldn't the connection size and number of inlets be critical? A 3000 gpm pump requires a 10" test header with 12 2.5

Re: PA IRC Hearings-your support is needed

2009-04-09 Thread Todd Williams
Actually, the auto companies lobbied against air bags, as they did seat belts, as they did emission controls. However, we're all better off because we have them. At 08:12 AM 4/9/2009, George Church wrote: >Well, I know where I'll be on April 22. Hope any of you in PA will join us. >Sure, plumbe

RE: PA IRC Hearings-your support is needed

2009-04-09 Thread Kevin King
The voice of reason has spoken. Amen! -Original Message- From: George Church Sent: Thursday, April 09, 2009 6:12 AM To: sprinklerforum@firesprinkler.org Cc: 'Tim Knisely' Subject: PA IRC Hearings-your support is needed Well, I know where I'll be on April 22. Hope any of you in PA will j

PA IRC Hearings-your support is needed

2009-04-09 Thread George Church
Well, I know where I'll be on April 22. Hope any of you in PA will join us. Sure, plumbers will do a lot of this work. Sure, we'll get some since we actually DO SFDs on the rare occasions they present themselves in our market. Bt I'm doing this because for 35 years I've protected warehouses where p

RE: 100ft from FDC to hydrant?

2009-04-09 Thread John Drucker
While we are speaking of codes take another look at 2006 IBC 508.5.1 "Where a portion of the facility or building hereafter constructed or moved into or within the jurisdiction is more than 400 feet (122 m) from a hydrant on a fire apparatus access road, as measured by an approved route around the