Some commentary states that the FDC is not intended to be a substitute for the 
normal water supply (GPM) but a supplementary source used to boost pressure.  
With that being the intent, the smaller size makes more sense.

With the test header, you are testing the actual flow (gpm) characteristics of 
the pump.

The FDC and Test Header is an apples to oranges comparison.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Thursday, April 09, 2009 8:54 AM
To: [email protected]
Subject: RE: 100ft from FDC to hydrant?

NFPA #13 gives the same amount of attention to the placement of the FDC as it 
does it's adequacy to handle the flow required for the hazard, none. If the 
location is critical then shouldn't the connection size and number of inlets be 
critical?

A 3000 gpm pump requires a 10" test header with 12 2.5" outlets but only one 4" 
FDC with 2 2.5" inlets. How is that going to work?

We hear about sprinkler saves all the time. Ever hear of a save because the 
water supply into the building was impaired and the arriving fire dept. used 
the FDC as the secondary supply?

Just my 2 cents.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Thursday, April 09, 2009 2:18 AM
To: [email protected]
Subject: RE: 100ft from FDC to hydrant?

While we are speaking of codes take another look at 2006 IBC 508.5.1

"Where a portion of the facility or building hereafter constructed or moved 
into or within the jurisdiction is more than 400 feet (122 m) from a hydrant on 
a fire apparatus access road, as measured by an approved route around the 
exterior of the facility or building, on-site fire hydrants and mains shall be 
provided where required by the fire code official."

What if the hydrant is 401 feet away ?. The fire code official cites
508.5.1
with the following directive; "provide a hydrant 100 Feet from the FDC".
The
fire code official relies on; "fire hydrants and mains shall be provided WHERE 
REQUIRED BY THE FIRE CODE OFFICIAL". The fire code official is clearly within 
the scope of the code section. Oh intent you say, the intent of
508.5.1 is to minimize the hose stretch required of the fire department.
It
goes without saying that a 100 ft hydrant stretch is less work then a 400 ft 
stretch. 

John Drucker
Fire Protection Subcode Official
New Jersey

PS, Hi David. Quick question. Based on Vancouver 508.5.8 what if a property 
owner installs a fire sprinkler system voluntarily. I will assume that as we do 
in NJ it must then be provided with an FDC where 20 or more sprinklers are 
installed since the system albeit voluntary must still be installed in 
accordance with the standard. Does that make the FDC required and thus require 
the installation of a hydrant within 150 feet as well ?

Thanks
John


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Smith, David
(VFD)
Sent: Thursday, April 09, 2009 12:43 AM
To: [email protected]
Subject: RE: 100ft from FDC to hydrant?

I would always recommend asking for the reference when you receive comments and 
aren't sure where they are coming from. You'll want to make sure that you know 
what they are referencing and even that they have the ability to enforce it. 
 
For instance, portions of Chapter 5 of the 2006 IFC pertaining to fire 
department access weren't adopted at the state level and isn't enforceable in 
WA unless the local jurisdictions adopt it through local ordinance or have 
their own requirement. Other agencies may modify the model code with something 
more specific or restrictive. Our reference here in Vancouver would be:
 
Vancouver Municipal Code 16.04.160, Amendment to IFC Section 508
508.5.8 Fire Department connections. A fire hydrant shall be located within 150 
feet of all required and approved fire department connections.
 
Regards,
 
David M. Smith, Deputy Fire Marshal
Vancouver Fire Department, Fire Marshal's Office 7110 NE 63rd Street Vancouver, 
WA 98661 360-487-7240 Phone/Fax

 
________________________________

From: [email protected] on behalf of John Drucker
Sent: Wed 4/8/2009 3:46 PM
To: [email protected]
Subject: RE: 100ft from FDC to hydrant?



Members, Perhaps this will help;

2006 IFC Section 508 Fire Protection Water Supplies

508.5.1 Where required.

Where a portion of the facility or building hereafter constructed or moved into 
or within the jurisdiction is more than 400 feet (122 m) from a hydrant on a 
fire apparatus access road, as measured by an approved route around the 
exterior of the facility or building, on-site fire hydrants and mains shall be 
provided where required by the fire code official.

Exceptions:
1.      For Group R-3 and Group U occupancies, the distance requirement
shall be 600 feet (183 m).
2.      For buildings equipped throughout with an approved automatic
sprinkler system installed in accordance with Section   903.3.1.1
(NFPA-13)
or 903.3.1.2, (NFPA-13R) the distance requirement shall be 600 feet (183 m).

Don't forget about 2006 IFC Appendix B and C if adopted in your jurisdiction.

Sincerely

John Drucker
Fire Protection Subcode Official


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to