Re: Fire Dept.

2009-11-11 Thread steve
inklerforum> > > > > For Technical Assistance, send an email to: supp...@firesprinkler.org > > > > To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org > > (Put the word unsubscribe in the subject field) >

Re: Fire Dept.

2009-11-11 Thread Jay Jay Blocker
rinklerforum > > > > For Technical Assistance, send an email to: supp...@firesprinkler.org > > > > To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org > > (Put the word unsubscribe in the subject field) > _

Re: Flex Head Friction loss

2009-11-11 Thread Ron Greenman
I guess it's just gonna be what all the AHJs consider listed and/or approved. If'n I were the an AHJ I'd I'd accept either. If'n there were an FM interest I suspect they'd want FM approved stuff only, and to there criteria. If'n I were gonna performance design this thing I bet I could set up some e

RE: Flex Head Friction loss

2009-11-11 Thread Daniel Wilder
I respectfully disagree with this. The FM standards dictate that number or turns and minimum radii (based on length) be maintained in order to have their tested friction loss be accurate, same for UL. Whether or not the turns are maintained after turnover on future work is another matter and wher

Re: Flex Head Friction loss

2009-11-11 Thread ParsleyConsulting
George, I looked at some of the data from FlexHead this afternoon, and what occurred to me was that if the devices were installed and maintained the minimum radius on the bends that met the FM limitations rather than those for UL, that a reasonably good case could be made to suggest the FM equ

RE: Flex Head Friction loss

2009-11-11 Thread George Church
Since when did FM stop being a recognized national testing laboratory? We've used FM criteria often in projects, and their ESFR obstruction criteria is far more illustrative than NFPA's. So if we have a job FM does not insure, and we want to use a device that is not UL listed but IS FM-Approved,

Re: Flex Head Friction loss

2009-11-11 Thread rahe . loftin
Dennis, If this is not an FM job, then they have no dog in the fight and you cannot use them to reduce your equivalent lengths. Since there is no FM inspection and no FM insurance, you will have to use the UL equivalent lengths and submit the shop drawings and calculations to the local AHJ with th

Re: Riser Check Valve Info ?

2009-11-11 Thread Forest Wilson
Now you can check the UL listing, and see if it was listed. The 1996 edition of NFPA 13 (4-15.2.5) required an automatic drip in areas subject to freezing. American Star Valve Corporation ncorporated by Brian Crider, American Star Valve Corporation is located at 6181 E Lake Rd # 186 Palm Ha

RE: Riser Check Valve Info ?

2009-11-11 Thread Thom McMahon
Dave: You might want to check the Face to Face of those valves and look for a valve with the same dim. The FDC check is only about $125, and depending on the riser check you use you'll spend double or triple that. It may still be less than all the labor and lost time looking for parts. Thom McMaho

RE: Riser Check Valve Info ?

2009-11-11 Thread George Church
No UL/FM marks, year of mfr cast in body as reqd on listed valves, etc? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Wednesday, November 11, 2009 4:43 PM To: sprinklerforum@firesp

RE: standpipe for attic?

2009-11-11 Thread Thom McMahon
Thanks Paul I've missed that one! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On

RE: Riser Check Valve Info ?

2009-11-11 Thread Craig.Prahl
American Star Valve Corporation Incorporated by Brian Crider, American Star Valve Corporation is located at 36181 E Lake Rd # 186 Palm Harbor, FL 34685. American Star Valve Corporation was incorporated on Tuesday, October 04, 1994 in the State of FL and is currently not active. Brian Crider rep

Riser Check Valve Info ?

2009-11-11 Thread Dave Phelan
Greetings all, I ran across an installation (poor) yesterday and could use some assistance identifying two check valves on it. The system is wet piped and is circa 1994. The 3" riser check (definitely not an alarm check) is a red cylinder with a taping for the main drain and a plate 'American

Re: standpipe for attic?

2009-11-11 Thread Todd Williams
Empty attic. Some ductwork and maybe an air handler or two. The core is 3 floors and the wings are two. Peaked roof with wood joist on wood beams. Separation is plaster on lathe on wood joist or sheetrock on wood joist. At 03:39 PM 11/11/2009, you wrote: >OK. Attic that's just an unusable empt

RE: standpipe for attic?

2009-11-11 Thread Steve Leyton
/fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Ant

Re: standpipe for attic?

2009-11-11 Thread Ron Greenman
OK. Attic that's just an unusable empty space? Attic for storage? Attic with mechanical equipment? Empty attic with the same joist plane as an adjacent occupied space? Mechanical pent? Empty, unusable attic seems to be similar to an interstitial space to my way of thinking. If it's partially occupi

RE: standpipe for attic?

2009-11-11 Thread Paul Pinigis
Per section 1509.2 of the 2006 IBC, a penthouse or rooftop enclosure can be up to 1/3 of the area of the roof. Over that and it is a floor. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...

RE: standpipe for attic?

2009-11-11 Thread Thom McMahon
Same sort of question could be asked of a "Mechanical penthouse" How big does it have to be before it's a floor, and not just a box set on the roof? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Origin

Re: Flex Head Friction loss

2009-11-11 Thread Todd Williams
I always use the larger number because doing that I never had a conflict problem. If the job is designed for FM using the FM criteria, the AHJ could come back and reject the design because the friction loss doesn't match what he is looking at (UL). At 01:34 PM 11/11/2009, you wrote: >We are d

RE: Flex Head Friction loss

2009-11-11 Thread Brown, Mike
If your calcs are going to be tight use the FM approved equivalent lengths but remember the FM approved ones cost more. Mike Brown Project Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph. 336.886.7027 Ext. 140 Fax: 336.886.7024 WWW.SUNLANDFIRE.COM -Original Message-

Re: Flex Head Friction loss

2009-11-11 Thread Travis Mack
Look at the minimum radius. It is 3" for UL and 7" for FM. I assume that is why the different equivalent lengths. That may help you decide what you are going to use. Travis > We are doing a job using flex heads. They show different equivalency loss > for FM and UL listings. 9.6 ft versus 27 ft.

RE: standpipe for attic?

2009-11-11 Thread Bill Brooks
Normally an attic is not considered a story, but it could be. If it is not a story and if there is no stair access to the space, there may not be a need to provide a standpipe connection for this area. However, IBC Section 1209.3 does provide for access to concealed spaces such as attics. My ass

Flex Head Friction loss

2009-11-11 Thread Dennis Browning
We are doing a job using flex heads. They show different equivalency loss for FM and UL listings. 9.6 ft versus 27 ft. respectfullt. What should I use? This is not a mandated FM project and I am designing to 2002 13 light/ordinary hazzard. I would rather use the 9.6 factor. At what point would

RE: Fire Dept.

2009-11-11 Thread Steve Leyton
> > > > For Technical Assistance, send an email to: supp...@firesprinkler.org > > > > To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org > > (Put the word unsubscribe in the subject field) > ___ > Sprink

RE: standpipe for attic?

2009-11-11 Thread Steve Leyton
Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (

Re: standpipe for attic?

2009-11-11 Thread Todd Williams
I don't typically provide standpipes for attics, but the attic space is usually 1 level up from the occupied space. What is the proper separation between an attic and occupied spaces? There are walls with some doors. At 12:18 PM 11/11/2009, you wrote: >Do you typically supply standpipe coverage

RE: Porte' Cochere

2009-11-11 Thread Thom McMahon
Further if you look at A8.15.7.2 you'll see that the porte-cochere do not normally require sprinkler where there is no occupancy above. I believe that you stated that there is an occupied space above, so I would say sprinklers are required. By the statement in the last line of A8.15.7.2 "However a

Re: Porte' Cochere

2009-11-11 Thread Ron Greenman
I declare it a tunnel and the drive an Eisenhower Freeway. Proceed appropriately. Oh wait. It's Veteran's Day, not April Fool's. Remember that veterans have given anywhere from two years to all of their lives in service to all of us. Think about that the next time you feel you don't have a few minu

RE: Fire Dept.

2009-11-11 Thread Thom McMahon
J. Being in Colorado I see two major paths, 1) Most Fire dept. that have three stations also have their own (Fire Marshal or Certified Plan reviewer as required by the CO Div. of Fire Safety) if this is the case I'd have the Inspector review the facility and in conjunction with the contracting offi

Re: standpipe for attic?

2009-11-11 Thread Ron Greenman
Do you typically supply standpipe coverage to an attic? Is the occupied space properly separated from attic space? On Wed, Nov 11, 2009 at 9:11 AM, Todd Williams wrote: > I am working on a building where part of the 3rd floor is occupied > (center core) and the rest (wings and area over core) is

standpipe for attic?

2009-11-11 Thread Todd Williams
I am working on a building where part of the 3rd floor is occupied (center core) and the rest (wings and area over core) is unoccupied attic. The building is fully sprinklered, including the attic. Does the standpipe coverage have to reach the remote part of the attic spaces or just the occupie

RE: Fire Dept.

2009-11-11 Thread lamarvaughn
gt; http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: supp...@firesprinkler.org > > > > To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org > > (Put the word unsubscribe in the

Re: Porte' Cochere

2009-11-11 Thread Todd Williams
Porte Cochere translates to "coach gate" or "coach door"; it's not that odd. At 10:38 AM 11/11/2009, you wrote: >proceed with great caution. UNDER the building is not the same as a >canopy attached to the building regardless of what odd French names we >apply. From the context of the title and

Re: Porte' Cochere

2009-11-11 Thread Roland Huggins
proceed with great caution. UNDER the building is not the same as a canopy attached to the building regardless of what odd French names we apply. From the context of the title and all other information, it would be a challenge to say 8.15.7 applies to anything that does not stick out beyo

RE: Unsubscribe

2009-11-11 Thread Steve Leyton
be in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 4596 (2009) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __ Information from ESET NOD32 Antivirus, version of virus signature data

RE: Fire Dept.

2009-11-11 Thread Steve Leyton
r Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 4

Unsubscribe

2009-11-11 Thread Chris Gaut
Chris Gaut ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesp

RE: Fire Dept.

2009-11-11 Thread George Church
It's not IF, it's WHEN If what your planned course of action is makes you sick to your stomach, then you need to change it and make sure the problem is identified to the parties that CAN rectify it. If they don't, its no longer on you. But if it burned, and someone died, could you live with saying

RE: Fire Dept.

2009-11-11 Thread Craig.Prahl
So just because it's the fire department you're supposed to ignore a system that is grossly under-designed and doesn't meet code? Perfect. What a tribute to the industry when the fire department burns down but the news media reports the building was fully sprinklered and the system failed.

RE: Fire Dept.

2009-11-11 Thread John Drucker
The answer lies within NFPA-25. Emphasis in CAPS. 2008 NFPA-25-1.1.2 "The types of systems addressed by this standard include, but are not limited to, sprinkler, standpipe and hose, fixed water spray, and foam water. Included are the water supplies that are part of these systems, such as private f

Re: Fire Dept.

2009-11-11 Thread lamarvaughn
This sounds like one you may be wise to let someone else sort out.Not knowing all the particulars of this area,I would have to ask "Why are they looking for a ligitimate inspection of a system that they KNOW isn't code compliant"?Also,not just one station but multiples.This tells me this is not

Re: Fire Dept.

2009-11-11 Thread Norm and Lucie Arendt
Interesting as I ran across a similar piping arrangement but in a commercial building. Digging back through the code and building records I found out that some 20 plus years ago this type of system was permitted. Fortunately the owner in this case is remodeling and has to bring it up to curre

Re: Fire Dept.

2009-11-11 Thread Todd Williams
In spite of who it is, it would be wrong to just sweep this under the rug. Does the jurisdiction have something written in the Code stating that a system must be installed per standard, even if not required? If so, you could challenge the system based on that. Either way, you should document yo