Re: Hard wired air compressors

2010-03-18 Thread Ron Greenman
But it's sooo hard, and I have to see episode 7 of 2 1/2 men for the sixth time, and the dog has to pee, and On Thu, Mar 18, 2010 at 2:05 PM, George Church wrote: > Submit a proposal! > > -Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun

RE: Hard wired air compressors

2010-03-18 Thread Thom McMahon
Just so we're clear, I am NOT advocating plug in compressors or quick coupled air lines it's just a reality that they meet the code as it currently stands. I'd welcome clarity in the code that would say something like. "All electrical circuit's which supply power to any Fire protection device or l

set

2010-03-18 Thread Mark Hasenmyer, PE
___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-re

RE: dry system air leak

2010-03-18 Thread john . powell
I remember years ago we traced several leaks in a large dry system by itroducing froen refrigerating gas and using an electronc gas detector. I dont know if this will work with the modern refrigerant gasses. John Powell NZ -original message- Subject: RE: dry system air leak From: "Fletcher, Ro

RE: Hard wired air compressors

2010-03-18 Thread George Church
Submit a proposal! -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Thursday, March 18, 2010 4:13 PM To: sprinklerforum@firesprinkler.org Subject: Re: Hard wired air compressors I'd like to

Re: dry system air leak

2010-03-18 Thread Todd Williams
Try nitrous oxide, when everyone starts laughing, you found the leak. (just kidding) Wintergreen extract is one product. Then just follow your nose. At 04:27 PM 3/18/2010, you wrote: >There was a thread a while back (I think) that discussed a way of >finding leaks in dry systems using a colored

an interesting story

2010-03-18 Thread Todd Williams
Be interesting to see what the final analysis is on this one... http://www.charlestonbusiness.com/news/33372-kiawah-island-golf-clubhouse-lsquo-a-total-loss-rsquo-after-wednesday-rsquo-s-fire Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com

RE: dry system air leak

2010-03-18 Thread Fletcher, Ron
Thanks Chris, I'll check it out. Sounds like we will have to fill it with antifreeze solution plus dye. We were hoping there was way to test using a gas or air instead of liquid. Fletch -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@fire

Re: dry system air leak

2010-03-18 Thread Ben Young
Here's the thread: http://www.mail-archive.com/sprinklerforum@firesprinkler.org/msg19989.html Benjamin Young Sprinkler Designer Rowe Sprinkler Systems, Inc. b...@rowesprinkler.com On Thu, Mar 18, 2010 at 4:27 PM, Fletcher, Ron wrote: > There was a thread a while back (I think) that discussed a

RE: dry system air leak

2010-03-18 Thread Chris Cahill
Google tracing dyes - there are regular and florescent, liquids, powders tablets. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: chr...@sentryfiremn.com Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW

dry system air leak

2010-03-18 Thread Fletcher, Ron
There was a thread a while back (I think) that discussed a way of finding leaks in dry systems using a colored gas or something like that. I didn't save the thread because we live in Phoenix and don't have dry systems except in freezers. My mistake. We are working on a freezer system repair, have f

RE: exterior spacing of Pilot heads

2010-03-18 Thread Fletcher, Ron
Have you checked out the Viking C-1 release? I think it can be spaced more than 8 ft apart. Probably pricey but maybe worth a look. Ron Fletcher Aero Automatic Phoenix, AZ . -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.o

Re: Hard wired air compressors

2010-03-18 Thread Ron Greenman
I'd like to see a requirement in 13D that you need to prove the recovery rate for the well will either be the system demand (plus the already required 5 gpm extra) or that there is sufficient storage to compensate for the full duration. On Thu, Mar 18, 2010 at 12:52 PM, George Church wrote: > Yes

Re: Hard wired air compressors

2010-03-18 Thread Ron Greenman
Over 1/8 HP. On Thu, Mar 18, 2010 at 12:27 PM, David de Vries wrote: > Every winter in this land of the midwest, I see at least one dry pipe system > that has tripped because someone disconnected the air supply.  The most > common problem is a "permanent" air compressor installation powered thr

Re: smoke detectors save lives

2010-03-18 Thread Reza Esmaeili
George I would appreciate if you be so kind to send me a copy also. Thanks, Reza rezaesmaeili...@yahoo.com From: George Church To: sprinklerforum@firesprinkler.org Sent: Thu, March 18, 2010 2:39:47 PM Subject: smoke detectors save lives Who wanted a clipping o

RE: Hard wired air compressors

2010-03-18 Thread George Church
Yes, I love those calls at 10AM, please come immediately, we had an emergency at 3 AM. Without breaker protection/lock-in as a requirement for a hard-wired air compr, I can't think the plug-in is any worse. I agree with Ron's intent concept, for with small hand tools, a lot of sprinkler protection

exterior spacing of Pilot heads

2010-03-18 Thread Greg McGahan
Official from NFPA is that exterior means by definition "exterior" and that 8'-0" is the only option (for those who followed this previous thread). Thanks for the feedback Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 __

RE: Hard wired air compressors

2010-03-18 Thread David de Vries
I have also encountered, more than once, the central station or security guard on duty calling the building engineer at home in the middle of the night, saying "we got a low air supervisory on the alarm panel" and the building engineer replies, "OK, I will call the sprinkler contractor in the mo

Re: Hard wired air compressors

2010-03-18 Thread David de Vries
Every winter in this land of the midwest, I see at least one dry pipe system that has tripped because someone disconnected the air supply.  The most common problem is a "permanent" air compressor installation powered through an ordinary toggle switch and someone flipped the switch thinking it op

RE: Hard wired air compressors

2010-03-18 Thread Thom McMahon
I think of it this way: A nitrogen tank is not hard wired, and the shut off valve handle is not tampered. If not for the Low air pressure monitor, who would ever know if the nitrogen bottle was "Online" or "Offline" since the valve handles are non-indicating? Allowed by 13, yet no more reliable t

RE: Hard wired air compressors

2010-03-18 Thread Art Tiroly
A disconnect and breaker will also disable the power to the A/C unless locked in "ON" position. Low air alarm will provide the backup if not too late. Art -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg

RE: Hard wired air compressors

2010-03-18 Thread Thom McMahon
I would say if your system is equipped with a low air monitored trouble, neither the Quick coupling in the air line nor the plug would constitute an impairment, since if you have air loss to the point the LAP switch operates you'll know it, before the system trips. Thom McMahon, SET Firetech, I

RE: Hard wired air compressors

2010-03-18 Thread lamarvaughn
No,it is not an impairment by any definition because the system will still function as intended (assuming that it isn't tripped & frozen because someone unplugged it and forgot about it). Hard wiring may keep these "accidents" from happening. Greg McGahan wrote: > Ok to follow up with

Re: Hard wired air compressors

2010-03-18 Thread Ron Greenman
Weel, back to what I just found in 70 then if it were disconnected when you look at it it is an impairment. When you plug it back in and verify it operates properly it is not. On Thu, Mar 18, 2010 at 11:49 AM, Ron Greenman wrote: > As I look through the electric code an argument could be made tha

Re: Hard wired air compressors

2010-03-18 Thread Ron Greenman
As I look through the electric code an argument could be made that a plug is not what would define portable or permanent. In fact an argument could be made that even a quick-disconnect air line in addition to the plug could still be considered permanent and that the term "permanent" has more to do

RE: Hard wired air compressors

2010-03-18 Thread Greg McGahan
Ok to follow up with the 3rd round, then is it an impairment per NFPA #25? Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler

RE: Hard wired air compressors

2010-03-18 Thread Bobby Gillett
We have a manuf. facility that we inspect., (system by others) They have small dry system that has a portable air compressor, the maintenance crew installed a quick disconnect in the piping after installation. They take the air compressor and use it, even though instructed not to, with signs by man

RE: Hard wired air compressors

2010-03-18 Thread Reed Roisum
The source is to be available at all times. This isn't necessarily talking about being movable or not. If it is able to be unplugged then it would not be available at that time that someone unplugs it. It wouldn't hurt to have some additional verbiage to clarify the intent here. I actually t

RE: Hard wired air compressors

2010-03-18 Thread Bobby Gillett
It can still be unplugged and out of service, that’s what we're told. If we use a portable style we have it hard wired. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com -Original M

RE: Hard wired air compressors

2010-03-18 Thread Greg McGahan
Ok, what about the argument that it is hard piped and even though it is plugged in you can't pick it up and remove it? Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

Re: Hard wired air compressors

2010-03-18 Thread Ron Greenman
Yes to discussed before and I agree with your interpretation. On Thu, Mar 18, 2010 at 11:16 AM, Greg McGahan wrote: > This is a friendly discussion and not a conflict. However, please see > the interpretation below. > > > > 13-7.2.6.2.1 states, the air supply shall be from a source available at >

Hard wired air compressors

2010-03-18 Thread Greg McGahan
This is a friendly discussion and not a conflict. However, please see the interpretation below. 13-7.2.6.2.1 states, the air supply shall be from a source available at all times. A plug-in air compressor is portable and would not meet the 'all times' criteria. Hence, my interpretation that th

RE: smoke detectors save lives

2010-03-18 Thread Maag, Barry
A copy of that would be greatly appreciated. bm...@siouxfalls.org Barry Maag Fire Inspector Sioux Falls Fire Rescue 605-367-8054 bm...@siouxfalls.org -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geor

Re: smoke detectors save lives

2010-03-18 Thread Charles Thurston
Hello George, I would like a copy coastalf...@sc.rr.com If you would Please. Thanks Thursday, March 18, 2010, 7:09:47 AM, you wrote: > Who wanted a clipping of homebuilders fighting smoke detectors a month or so > ago? Ran across one, sent it to some forumites last eve > glc > __

RE: smoke detectors save lives

2010-03-18 Thread David Blackwell
I did please email me a copy at blac...@llr.sc.gov David W. S. Blackwell, II, PE, CFI-I, CFPE Engineering Office of State Fire Marshal 141 Monticello Trail Columbia, SC 29203 Phone: 803.896.9833 Fax: 803.896.9806 Email:

Re: smoke detectors save lives

2010-03-18 Thread Dennis J Briggs Jr.
George would you be so kind to send me a copy also. Thanks, Dennis Briggs, Jr. C.E.T. -Original Message- From: Matt Grise [mailto:m...@afpsprink.com] Sent: Thursday, March 18, 2010 08:57 AM To: 'sprinklerforum@firesprinkler.org' Subject: RE: smoke detectors save lives Can you send to me

RE: smoke detectors save lives

2010-03-18 Thread Smith, David L.(FAC)
I'll take a copy George. Thanks for offering! Excellence is not a skill, its an attitude! Ralph Marston   David L. Smith Fire Protection Maintenance City of Lakeland Public Works / Facilities 228 S. Massachusetts Ave. Lakeland, Fl. 33801 Office: 863-834-2380 Fax:  863-499-2384 Cell: 863-559-0903

RE: smoke detectors save lives

2010-03-18 Thread Matt Grise
Can you send to me also? m...@afpsprink.com Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprink

RE: smoke detectors save lives

2010-03-18 Thread Fox Duane T. (FireMarshal)
George, Can you send a copy to duane@state.de.us Thanks Duane Fox, Jr DE State Fire Marshal's Office -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Thursday, March 18, 2010 7:10

RE: smoke detectors save lives

2010-03-18 Thread John Drucker
Please john.druc...@verizon.net -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Thursday, March 18, 2010 7:10 AM To: sprinklerforum@firesprinkler.org Subject: smoke detectors save lives

smoke detectors save lives

2010-03-18 Thread George Church
Who wanted a clipping of homebuilders fighting smoke detectors a month or so ago? Ran across one, sent it to some forumites last eve glc ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/list