Thank you to all who replied. This is good information. I still have some
questions of those who responded. I am going to involved in a conference
call this afternoon with the Building official and Plumbing Inspector for
this Municipality in Vermont to discuss this subject and try to work out
lets not exclude getting clarification on the smaller BFP in the
middle/end of the wet pipe system supplying the supplemental
antifreeze system.
Roland
On Apr 2, 2010, at 5:07 AM, G. Tim Stone wrote:
Thank you to all who replied. This is good information. I still have
some
questions of
Rolland,
The city AHJ has only referenced the connection to the municipal water main
connection as it enters the building. I do not believe that it would affect
the connection or installation of the BFP on an Anti-freeze loop on a
sprinkler system. Seems to me that would create a logistics
And provision for forward flow testing of the smaller backflow
Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless Phone
- Reply message -
From: Roland Huggins rhugg...@firesprinkler.org
Date: Fri, Apr 2, 2010 10:35 AM
Subject: Connecting to Public Water Supply
To:
Who else has a listing?
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Subject: RE: WINDOW SPRINKLERS
You know there are window sprinklers other than Tyco's.
Greg McGahan
By fed. And most state laws, the water purveyor is responsible for the water
quality up until the backflow device. The backflow device represents the
Owners responsibility to protect the water purveyors supply from anything
the Owner does with his water.
Making Beer or other uses like fire
The NRC Canada's IRC has an interesting article on the use of SSP QR heads to
protect tempered glass windows, but I don't believe ICC has adopted any of
these yet.
http://www.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n12.html
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
I am forwarding the email below from a local Insurance Agent.
G. Tim Stone
Chairman: Northern New England Chapter of AFSA
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT.
Since when did AHJ's or legislatures for that matter worry about
insignificant practical matters like insurance? lol
Roland
On Apr 2, 2010, at 8:31 AM, G. Tim Stone wrote:
I am forwarding the email below from a local Insurance Agent.
G. Tim Stone
Chairman: Northern New England Chapter
Forumites,
NFPA 20 - 2007 par. 5.7.6.2 ( = 2010 par. 4.7.7.2) says:
Pressure relief valves and pressure regulating devices in the fire
pump installation shall not be used as a means to meet the
requirements of 5.7.6.1. (= 2010 par. 4.7.7.1)
I ask this question because it seems to be not
Is there a maximum pile volume for rubber tires stored on side in
portable racks 25 ft. high? Roof height is 35 ft.
Ron Fletcher
Aero Automatic
Phoenix, AZ
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
One concern I have is for dry pipe and preaction systems. The in-rush to
fill the system will have a short term high velocity flow that will pick up
any debris in the fire line and move it into the riser. Should that be added
to the flushing proceedure or is it a special case that that does not
Don't forget;
2006 IBC Preface-Introduction
Internationally, code officials recognize the need for a modern, up-to-date
building code addressing the design and installation of building systems
through requirements emphasizing performance.
104.11 Alternative materials, design and methods of
Let's say you used option #3 and opened the valve all the way and the
velocity was only 5 FPS.
Why would that velocity ever be more than 5 FPS? Even in the case of a dry
pipe valve or pre action?
You could break the main off at the riser and you'd still only have 5 FPS
velocity.
Alternate: You
I believe another reason was fear of main relief valve sticking OPEN as
flows increase, so the water that should go to 10 open heads is out in the
parking lot.
We address by using Clarke diesels w/PLD, 170 pSI output from churn to
demand. About as good as it gets at base of riser. Sometimes your
Who else manufactures Window Sprinklers? Also, I am calculating the window
sprinklers the same way as Tyco is recommending for there 'Window Sprinklers'
to calculate, I could not find in NFPA-13 how to calculate sprinklers for
Window protection (any suggestions?) I am using Tyco FRB 2.8K heads.
In Ch 6, ESFR protection is allowed for aerosols stored in racks but I
do not see where it states what type of racks this is allowed with. IE:
Single, double, or multi row racks.
When in-racks are required along with the ESFR sprinklers they have
specific examples of all 3 types of racks. I take
Or engineering. I forget who started this, presumably G. Tim. But all
this who's work is whose stuff has a lot to do with politics. So in
Washington I put a 6 double check in a vault in the yard for the
sprinkler system (and I'm guessing a 3 for the water supply is also
OK for me to do by the
Reliable Model FM for one. They are not listed to make the glass 1 hour rated,
but they are listed for exposure protection.
Greg McGahan
Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
-Original Message-
From:
tony, first off why a 3000 sq ft remote area ? second - utilizing res
spkrs will not let you reduce an area to be calculated wherein 13
requires; largest room, corridor heads etc.
Tom Poisal, CET
Fire Sprink Ink
On 3/31/10, Ed Kramer k...@frii.com wrote: