Seems to me there is a grooved transition piece available.
On Wed, Jun 30, 2010 at 5:25 PM, wrote:
> I have cut sch 80 pvc
> On process piping.
> Manufacture says no on fire cpvc
> I have some old cutgrovers 4" smallest.
> I feel you pain on the 24hr I have long legal doc telling them if they
Hi everyone.
I recently was made to look very bad by a local AHJ because I told my client
that small hose stations were required for his high-piled combustible
storage facility (50,000 square feet plus of class IV commodities stored up
to 20 feet high). The client complained to the AHJ about h
And if baled too wet that mold can produce heat and eventually combustion. I
don't know if this influences the protection scheme or not, but you could
theoretically have a fire begin at the bottom of the stack (if it can get
enough oxygen) and be quite large before producing enough heat to acti
There won't be any wrapping, the hay needs to breathe. Otherwise it will
become moldy. I spent several teenage summers "bucking" hay from the fields
and stacking it in the barns.
I would classify it as OH Group 2.
As for the storage standard, from my experience it is standard practice to
stack the
I have cut sch 80 pvc
On process piping.
Manufacture says no on fire cpvc
I have some old cutgrovers 4" smallest.
I feel you pain on the 24hr I have long legal doc telling them if they want to
turn it on I warned you!
Sent from my BlackBerry® smartphone with Nextel Direct Connect
-Original M
Has anyone ever tried to cut groove cpvc?
The reason I ask is it might save on that 'last' joint and cut-in times
(which nobody in these parts it seems but me follows, but I'm venting).
Does anyone out there have a cut groover?
TD
Go Red Sox!
___
Spri
Look at stable protection. Also, somewhere I seem to recall that you have to
treat it like Group A Plastic.
Sent from my iPhone
On Jun 30, 2010, at 6:03 PM, Ed Cyr wrote:
> Forumites,
> Can someone give me guidance to the storage standard for protection of this
> commodity?
> Client would lik
Matt,
Solid piles, size unknown. storage will most likely take up most of 40K
except for required ailses.
bldg height 22' at the peak.
Unaware of any wrapping, will inquire.
Will have more info tomorrow.
Thx
Ed
On Wed, Jun 30, 2010 at 3:05 PM, Matt Grise wrote:
> Will it be a solid pile or an
Will it be a solid pile or an open array? (I am picturing a barn with a solid
block of hay bales at one end)
Will the bales be wrapped in mesh or plastic wrap? How tall is the building
deck? Round bales or square?
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in K
Forumites,
Can someone give me guidance to the storage standard for protection of this
commodity?
Client would like to store to 20' of hay bales. Pile size undetermined.
Prefab metal structure, 40K sqft.
Any input would be appreciated.
Ed Cyr
Alpha Fire Sprinkler Corp.
San Luis Obispo, CA
___
Can you please forward a copy of the article regarding the use of pitot tube
and diffusers, that was in the AWWA Journal, thanking you all in anticipation.
Regards, from down under,
John Luxford
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkle
For a less expensive option there are also desiccant dryers available. They
don't get the air quite as dry, and they require more attention, but the price
difference is substantial.
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO
913.888.0647 ph
913.888
Also keep in mind that, at least with the Tyco K-17 ESFRs, the upright
version cannot protect uncartoned unexpanded plastics, while the pendent
can.
Benjamin Young
On Wed, Jun 30, 2010 at 12:31 PM, Richard Carr <
richa...@associatedsprinkler.com> wrote:
> According to the Viking data sheet on
Look at General Air Products of Exton PA. They make a "Dry Air Pac". Works
well, we have installed several in critical locations where we do not want
any moisture in dry or pre-action systems. None better.
John O'Connor
National Fire Sprinklers, Inc.
Nashville TN
-Original Message-
F
Most air dryers are designed to work best at cooler ambient and compressed air
temperatures (office temperatures are ideal). If that is not available,
pre-cooling the compressed air is advisable. If dryer is mounted outside or in
hot area you might get longer life out of the dryer by using one t
I have a dry system that is undergoing some retro to fix multiple problems.
The customer has requested an air dryer be installed on the systems air supply
bfore the air maintenance device. Can any one provide any feed back on air
dryers that you might have experience with. All info is appreci
According to the Viking data sheet on the ESFR, it appears to me to be
less restrictive on obstructions, and it says mixing ups and pends is
acceptable to the manufacturer ( with AHJ approval)
Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
richa...@associatedsp
Dewayne,
You're absolutely correct. From the new FM 8-9, 2010 edition:
2.3.3.6.4 Do not mix sprinklers having different orientations (i.e.,
pendent and upright) on the same ceiling-level sprinkler system within
the same protected area unless indicated otherwise by this data sheet.
If you look
I would be careful mixing pnd and up. I think I read in the new 8-9 FM
storage standard that you could not mix the two.
Don't remember seeing this in 13 (10ed) but it could be there.
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
-Original Message-
From: sprinklerforum-bou
Perhaps semantics but I believe FM has done away with the term ESFR. Mfg's are
rewriting their cut sheets to the effect. You are correct on pendant is much
better than upright in some cases even when the upright is putting more water
out.
Chris Cahill, PE
Fire Protection Engineer
Note the e
The upright ESFR is less of a problem with obstructions, you may pay a
little more but can help a lot with obstruction issues and you can mix
pendents and uprights.
Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
richa...@associatedsprinkler.com
-Original
Check out FM's new DS 2-0 which includes some interesting changes regarding
ESFR's based on recent testing. As I recall, the downward momentum of the
water out of pendent ESFR's was demonstrated to be superior in getting through
the fire plume, hence listings for ESFR pendents going forward dif
>From a functionality standpoint, I have seen FM tests suggesting the pendant
>heads working significantly better than uprights.
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO
913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com
Opinion only but no benefit other than the space that I have seen
Sent on the TELUS Mobility network with BlackBerry
-Original Message-
From: "Brian Harris"
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Wed, 30 Jun 2010 10:39:24
To:
Reply-To: sprinklerforum@firesprinkler.org
S
Check out the obstructions allowed with upright ESFR's
Mike
> From: br...@firstdefensefire.com
> To: sprinklerforum@firesprinkler.org
> Subject: ESFR Heads
> Date: Wed, 30 Jun 2010 10:39:24 -0400
>
> I know a couple years ago they only made ESFR heads in the pendent position,
> now that the
I know a couple years ago they only made ESFR heads in the pendent position,
now that they make them in uprights as well is there a benefit one way or
another these days with still sticking to the pendent only method? I know
you get a couple extra inches of space allowed from deck to deflector but