Thanks to a wonderful sprinkler contractor and mentor who retired some
years ago I have his copy of the 1969 edition of NFPA 13.
In that document there is a reference to the _*1*__*965 edition of NFPA
23*__*1*_, in appendix "A", and identifies that it applied to:
"...storage, 2
I recently did a system upgrade of an OH pipe schedule system with 130
SF/head..
Good water supply and a low storage height made it work easily.
Back then only hazardous liquids were designed to extra hazard pipe schedule
and K8 - 90 SF/head.
Art Tiroly
ATCO Fire Protection/Tiroly
24400
All - I have a unique situation, unique to me anyway. Pipe schedule storage
occupancy installed per the 1969 edition of NFPA 13. It looks to me that NFPA
231 didn't come out until 1972, meaning storage would have fallen under what I
assume was one of the extra hazard curves in NFPA 13 in 1969
Reference TFP490, page 7 of 10, specifically graph A. There is a minimum
slant distance, or distance from the peak, which can be tricky.
Skyler Bilbo
On Wed, Jan 16, 2019 at 1:51 PM J H wrote:
> Does anyone have any input on this?
>
> -- Forwarded message -
> From: J H
> Dat
Question for the group. Do sprinklers protecting a 3 story atrium glass need to
be outside in atrium space or inside occupied space? What is the spacing of
heads. Thanks
Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
Check out Reliable’s design guide. I think Figure 3, 11, and 12 address your
question.
Nick Maneen, SET
c 704.791.7789
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of J H
Sent: Wednesday, January 16, 2019 2:51 PM
To: sprinklerforum@lists.fires
Does anyone have any input on this?
-- Forwarded message -
From: J H
Date: Tue, Jan 15, 2019 at 1:53 PM
Subject: Res Sprinklers on both side of sloped ceiling ridge?
To:
Hello,
Can you put one sprinkler near the ridge line of an interior sloped ceiling
for 13D residential sprin