Carpet Store

2019-04-29 Thread Tony Silva
Has anyone designed a sprinkler system for a carpet store (such as End of the Roll) assuming no high piled storage? If so, what was the occupancy or design criteria? Thanks, Tony ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http:

Re: NFPA 13 8.15.23 Spaces above ceilings 2016ed

2019-04-29 Thread JD Gamble
Travis you are correct in your mental image of the room. We have three locations that have come into question. One does only have one communicating wall but the others have multiple. It’s my impression as well that without the full height walls, we have to add coverage. Get Outlook for iOS

RE: NFPA 13 8.15.23 Spaces above ceilings 2016ed

2019-04-29 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I'm not sure I get your total picture, but I'll try. First, we start with sprinklers in all spaces. Then we can ask if we can omit in places. The section you quote is only applicable if it is open on one side, like figure A.15.23.3. If your IT room is the space in question and you have it op

NFPA 13 8.15.23 Spaces above ceilings 2016ed

2019-04-29 Thread JD Gamble
Can anyone explain how this section would NOT apply to the following situation. IT Room, open to deck, walls do not go full height. Rooms around the IT room are non/limited combustible above with hardlids below. Currently no sprinklers installed above the ceilings where spaces communicate with

Re: Backflow Forward Flow Test Forms

2019-04-29 Thread Bruce Verhei
pdf, and sample page with several page instructions. Best. https://www.doh.wa.gov/Portals/1/Documents/4200/FldTstReport.pdf & https://www.doh.wa.gov/Portals/1/Documents/4200/FldTstRpt-Instructions.pdf Best. > On Apr 29, 2019, at 15:01, Bruce Verhei wrote: > > MS Word version. PDF available

Re: Backflow Forward Flow Test Forms

2019-04-29 Thread Bruce Verhei
MS Word version. PDF available from same site. Best. Bruce Verhei https://www.doh.wa.gov/Portals/1/Documents/4200/FldTstReport.docx > On Apr 29, 2019, at 09:26, wrote: > > Does anyone have a Standard form for this test? > > Jerry Van Kolken > Millennium Fire Protection Corp. > 2950 San Lu

Backflow Forward Flow Test Forms

2019-04-29 Thread jvankolken
Does anyone have a Standard form for this test? Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730 ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http: