Travis you are correct in your mental image of the room. We have three 
locations that have come into question. One does only have one communicating 
wall but the others have multiple. It’s my impression as well that without the 
full height walls, we have to add coverage.

Get Outlook for iOS<https://aka.ms/o0ukef>

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]>
Sent: Monday, April 29, 2019 6:36 PM
To: [email protected]
Cc: 'Cecil Bilbo'; 'Pete Schwab'
Subject: RE: NFPA 13 8.15.23 Spaces above ceilings 2016ed

I’m not sure I get your total picture, but I’ll try.

First, we start with sprinklers in all spaces.  Then we can ask if we can omit 
in places.  The section you quote is only applicable if it is open on one side, 
like figure A.15.23.3.  If your IT room is the space in question and you have 
it open to rooms around it, then your don’t meet the criteria of open on only 
one side.  Based on very limited idea of what you have on your project, I tend 
to think sprinklers would be required above the areas adjacent to the IT room.  
But I am envisioning the IT room as an island surrounded by rooms on all sides, 
or at least more than one side.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum <[email protected]> On Behalf 
Of JD Gamble
Sent: Monday, April 29, 2019 5:31 PM
To: [email protected]
Cc: 'Cecil Bilbo' <[email protected]>; Pete Schwab 
<[email protected]>
Subject: NFPA 13 8.15.23 Spaces above ceilings 2016ed

Can anyone explain how this section would NOT apply to the following situation.

IT Room, open to deck, walls do not go full height.  Rooms around the IT room 
are non/limited combustible above with hardlids below.  Currently no sprinklers 
installed above the ceilings where spaces communicate with the IT rooms open 
walls. (we are in the argument about it, State isn’t much help).

Have I applied this section in error requiring sprinklers above the hardlids 
because the walls are not full height based on 8.15.23?

JD Gamble