Re: 3/4" Copper Pipe in Light Hazard Occupancy

2011-10-21 Thread Thomas Watt
George, If you are not familiar with Xpress copper fittings, let me tell you, they are great!!! We did a church a couple of years ago using this method. One leak!!! No fire, flux, solder, etc= No Hot-work permits. Sizes: 1/2"- 4" They would be great for a retro-fit. The press-fit tool and ja

RE: 3/4" Copper Pipe in Light Hazard Occupancy

2011-10-20 Thread Ed . Tambini
NFPA 13 (2010) 22.4.1.2 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Thursday, October 20, 2011 9:49 AM To: sprinklerforum@firesprinkler.org Subject: 3/4" Copper Pipe in

Re: 3/4" Copper Pipe in Light Hazard Occupancy

2011-10-20 Thread Travis Mack, SET
22.4.1.2 Pipe sizes shall be no less than 1 in. (25 mm) nominal for ferrous piping and 3⁄4 in. (20 mm) nominal for copper tubing or nonmetallic piping listed for fire sprinkler service. 2010 EDITION On 10/20/2011 9:49 AM, George Medina Jr wrote: Forum, I surveyed a high rise in Los Angeles for

3/4" Copper Pipe in Light Hazard Occupancy

2011-10-20 Thread George Medina Jr
Forum, I surveyed a high rise in Los Angeles for a tenant improvement and the entire system was done in Copper. I noticed the drops and end of lines were in 3/4" copper. Is that allowed in NFPA-13? The system is not more than 25 years old. If it is allowed, can somebody point me to the code se