RE: 3000 sqft rule

2020-03-05 Thread Lévis Blanchet via Sprinklerforum
Good Morning Everyone, What is your interpretation of art. 15.3.2.2 ( NFPA-13 2013) regarding scissor stairs? Are sprinklers required at each floor on both side of the landing or heads at the top & bottom only. Thank you. Lévis Blanchet Technical Sales Representative Fire Suppression Divisi

RE: 3000 sqft rule

2020-03-04 Thread Larry Keeping via Sprinklerforum
Greenman via Sprinklerforum Sent: March 4, 2020 3:30 PM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: 3000 sqft rule Does anyone know what edition of 13 the 3000 sqft rule was introduced? Ron Greenman rongreen...@gmail.com<mailto:rongreen...@gmail.com> 253.576.970

Re: 3000 sqft rule

2020-03-04 Thread cw bamford via Sprinklerforum
I found this 1996 edition 5-2.3.1.2. (b).unsprinklered combustible concealed spaces .3000 sq ft Chuck Bamford On Wed, Mar 4, 2020 at 12:30 PM Ron Greenman via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Does anyone know what edition of 13 the 3000 sqft

Re: 3000 sqft rule

2020-03-04 Thread 321 via Sprinklerforum
Ron, I think it was the 2010 edition. John W. Farabee 561-707-5150 On Wednesday, March 4, 2020, 03:30:36 PM EST, Ron Greenman via Sprinklerforum wrote: Does anyone know what edition of 13 the 3000 sqft rule was introduced? Ron Greenman rongreen...@gmail.com 253.576.9700 The

3000 sqft rule

2020-03-04 Thread Ron Greenman via Sprinklerforum
Does anyone know what edition of 13 the 3000 sqft rule was introduced? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942